Boiler Water Problem

06/25/2011 12:21 AM

We utilize a 3 ton steam generator at our clay brick making plant. The hardness of water from our well is usually mesured at about 700 to 850 ppm.We process the water through a water softening system that bring the hardness to under 50 ppm. Having done so we do not have resedual buildup or cloging in the tubes, but we are having problem with the fire tubes crossion and leakage of water into the fire tubes. to the point that we have had to blined off two tubes in the past 45 days. I have had th soft water analyzed by a Lab. and the have reported the content as follow without mentioning the % amount. Composition : Halite + thenardite + Burketite + Calcite + Quartz. Please advise what can I add to my water to counter off the effect of the above material.

Thanks Majid

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Boiler water problem

06/25/2011 12:35 AM

Water hardness would tend to result in scale formation on the water side of the tubes. This doesn't seem to be a problem with your softened water. Instead, your problem sounds more like dissolved oxygen in the water, which can cause pitting-type corrosion. There is a chemical treatment for this, but I forget the name. Also you could use a deaerator in the feed water system.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Jun 2011
Posts: 41
Good Answers: 1
#2

Re: Boiler water problem

06/25/2011 8:35 AM

It is not what you can do now, it is "how long has it been working without corrosion protection"

The problems you have may have started a long time ago. They may be general and you have the first two failures. Others will follow.

Suggestions: Find out condition of tubes. You may be able to remove a failed one and see condition. Special ultrasonic thickness detector may be easier if you have that service available.

Using boiler chemicals can help but where corrosion already started it is likely to proceed up to failure. Or you may chemical/acid clean the boiler--with some risk of more failures.

If failures are costly to your production get good advice from some service people who may quote for the job. You pay nothing and learn a lot until you decide.

Register to Reply
Power-User

Join Date: Oct 2009
Location: Central Midwest
Posts: 455
Good Answers: 38
#3

Re: Boiler water problem

06/25/2011 10:21 AM

Majid...

Do you have a deaerator in your system ?

Do you periodically test for dissolved oxygen in your system ?

__________________
We have met the enemy....and he is us. POGO
Register to Reply
2
Guru

Join Date: Aug 2008
Location: England & Ireland
Posts: 1063
Good Answers: 61
#4

Re: Boiler Water Problem

06/25/2011 5:41 PM

Your feedwater must be dosed with sodium sulphite to remove any dissolved oxygen gas in the water, which is a well known cause of corrosion pitting. This is standard practice for boilers and steam generators. Get yourself a sulphite measuring kit and make sure the sulphite level does not fall below 20 ppm. The sulphite is normally supplied with a cobalt catalyst added (small pink specks amonst the white crystals) to speed up the reaction. If for any reason you cannot tolerate sodium sulphite carryover in your steam, there is an alternative: hydrazine. This gets oxidised to nitrogen and water - so no contamination. Suggest you consult a local industrial water treatment company for further advice and test kits.

Repeat: Dissolved oxygen must be removed from your feedwater!

Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Marine Engineering - New Member

Join Date: Aug 2007
Location: Australia
Posts: 1630
Good Answers: 20
#5

Re: Boiler Water Problem

06/26/2011 5:35 AM

You mention that you have had your feed water tested but have you tested the boiler water for dissolved solids, salinity, etc?

Other things that can cause problems with boiler water are:

Scale forming salts

Sludge

Metals and metal oxides

Acid water

Dissolved gases (particularly oxygen)

Excessive alkalinity

Oils

All of these things can have a detrimental effect on your boiler tubing.

Why didn't you take a section of one of the tubes that you had to blind and check how bad the problem of scaling was?

Do you ever clean the the boiler intenally and externally?

__________________
TO BE. or NOT TO BE. That is the question!! The Bard
Register to Reply
Guru

Join Date: May 2009
Location: Wolfe Island, ON
Posts: 1357
Good Answers: 109
#6

Re: Boiler Water Problem

06/26/2011 10:42 PM

Majid

Your feed water needs better analysis. Total hardness as CaCO3 is important but so are many of the other parameters like total alkalinity, pH, conductivity, Total Dissolved Solids, and silica. Check with your boiler manufacturer for blow down rates and TDS tolerances. Just based on the hardness of 850 mg/L, I would guess the conductivity of this water at close to 1900 μS/cm (assuming hardness is the majority of cations present) and possibly much higher. The feed water has excess salts and may make your blow down times very frequent. Is there any way you can improve the feed water? Ion exchange or reverse osmosis may be used to remove much of the TDS present. Salty water (or high TDS water) can prove to be both scale forming and corrosive at the same time. Remember, a boiler converts water to steam and leaves behind the TDS. If you are starting with a high TDS I am guessing you are already starting with limited uses. Your report of Halite (NaCl) suggests that there may be an already high level of Na ion present in the raw water before softening. It really sounds like you need a better quality feed water and that is why I suggest treatment such as deionization or reverse osmosis. Be sure to discuss the problems with your manufacturer. They should know what are the operation limits.

__________________
If they want holy water, tell them to boil the hell out of it.
Register to Reply Score 1 for Good Answer
Register to Reply 6 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

energyconversion (1); kevinm (1); MJCronin (1); MOBI (1); oldwidget (1); Tornado (1)