How Do I Transform 110V To 130V

06/25/2011 7:20 PM

Hey all,

I have a 130v dc motor and I'm trying to hook it up to a 110/120v ac wall outlet. I'm aware that I will need a rectifier and from what I understand I will lose about 10% power from the rectifier. So I am trying to figure out how to bring the wattage back up from 108 to 130. I need this to be an inexpensive fix and I'm no electronics expert, but I'm willing to take the time and effort to make this work.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
3
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#1

Re: how do i transform 110v to 130v

06/25/2011 7:43 PM

Your problem will be stepping down from about 160VDC (because that's what you get by full wave rectifying 115VAC and feeding the result to a capacitor) down to 130VDC. For this small voltage margin and that low power, it's not worth to apply DC/DC step down conversion, I would feed it through a resistor, or if you need more stable speed and starting torque, through a few diodes in series. Each silicon diode voltage drop is about 0.6V-0.7V. For small duty cycle the motor will also survive 160V just fine, you will just have about 20% higher speed. Another cheap solution is to use a 115V to about 15V ac transformer, add it's output at oposite phase to 115V, and then rectify. You will get the right Voltage. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply Good Answer (Score 3)
Member

Join Date: Jun 2011
Posts: 6
#3
In reply to #1

Re: how do i transform 110v to 130v

06/25/2011 8:46 PM

Thank you very much! That's a huge help.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#6
In reply to #1

Re: how do i transform 110v to 130v

06/26/2011 11:48 AM

Is that right - that you get 160VDC by full wave rectifying 1-phase 115VAC and feeding the result to a capacitor? Perhaps I'm missing something, but I'd have thought the DC voltage would be about the same as the RMS AC volts, 115. Without a capacitor that would be RMS DC volts. With a capacitor output would be smoother, but I'd expect 115 volts. I don't see how it could give a steady output = input peak volts, 115*√2. Please explain if I'm wrong.

Cheers........Codey

__________________
Give masochists a fair crack of the whip
Register to Reply
2
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#10
In reply to #6

Re: how do i transform 110v to 130v

06/27/2011 6:00 AM

My friends sorry I have to insist on this. Rectifying and charging a big enough capacitor will give you higher DC voltage than AC RMS by about 1.41... times minus some diode drops, neither lower nor the same, because capacitor will be charged up to AC peak. If you don't use a capacitor then yes, RMS voltage remains about the same. It's basic fact, and I think not difficult to understand both theoretically and practically. And I hate to preach, but when not fully understanding concepts, please avoid advising others. Anyway no big deal. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Dec 2007
Location: California
Posts: 2363
Good Answers: 63
#11
In reply to #10

Re: how do i transform 110v to 130v

06/27/2011 11:26 AM

hmmm interesting 1.41 the difference between peak and rms.

Register to Reply
Guru

Join Date: Jul 2005
Location: Stoke-on-Trent, UK
Posts: 4496
Good Answers: 137
#16
In reply to #10

Re: how do i transform 110v to 130v

06/28/2011 9:17 AM

Well, judging by other posts, there seems to be some doubt about it. Not that I'm suggesting it's a matter of opinion, it can of course be settled by measurement. Thinking about it some more, I can see that with a capacitor the DC voltage will approach peak AC volts if the DC load has very high impedance, as the capacitor can charge to that level, but otherwise the capacitor will partly discharge during part of the cycle, giving lower average voltage.

And please don't lecture me about not fully understanding concepts etc! If I'm confident I have an answer to something, I might state it as a fact, hopefully diplomatically when appropriate. If I'm not sure, or making a comment, or asking a question, I try to put it in terms suitable for that. I thought it was pretty clear which category my #6 was in.

Codey

__________________
Give masochists a fair crack of the whip
Register to Reply
Active Contributor

Join Date: Mar 2011
Posts: 17
#12
In reply to #6

Re: how do i transform 110v to 130v

06/27/2011 11:41 AM

I agree with you code master.It appears simplemind got confused between single phase rectification and three phase rectification.The out put raw DC voltage from a single phase bridge rectifier is approximately 90% input ac voltage where as it is 140% in case of three phase bridge rectification.As such if the input is 120 V single phase out put may be around 115 Volts DC after smoothening with capactor.If this is not sufficiant to run 130 V DC motor,booster transformer may be used to boost the incoming to approximately 145 V ac and then rectified to get desired Dc voltage

Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#13
In reply to #12

Re: how do i transform 110v to 130v

06/27/2011 12:01 PM

http://en.wikipedia.org/wiki/Rectifier#Rectifier_output_smoothing

The voltage drop across the diodes is much more significant at these low voltages.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Jul 2006
Location: CA (Central Arkansas, USA)
Posts: 599
Good Answers: 10
#14
In reply to #1

Re: how do i transform 110v to 130v

06/27/2011 1:21 PM

Or wire a small transformer as a bucking transformer before rectifying. -- JHF

__________________
If it's too good to be true, it probably isn't
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#15
In reply to #1

Re: how do i transform 110v to 130v

06/28/2011 4:03 AM

GA

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Member

Join Date: Jun 2011
Posts: 6
#18
In reply to #1

Re: how do i transform 110v to 130v

06/28/2011 11:24 AM

The engine I'm trying to power is- http://www.surpluscenter.com/item.asp?item=5-1744&catname=electric and I was looking at this full wave rectifier- http://www.skycraftsurplus.com/siliconebridgerectifier-35amp600v.aspx I'm relay lost when it comes to the capacitor. I found this -http://www.alliedelec.com/search/productdetail.aspx?SKU=5860471 which is 300vac and- http://www.alliedelec.com/search/productdetail.aspx?SKU=8620554 which is 300vdc. I'm kinda confused as to where I need to place the capacitor. One person was saying that its not good to hook a rectifier up directly to the outlet without a capacitor first. Do I need to have a capacitor before and after the rectifier or will one prior be enough. Also I'm planing on using http://www.skycraftsurplus.com/potentiometer100krotary24mm.aspx to adjust the speed of the motor. Where would be the best place for me to place the potentiometer? ac side? dc side? before or after the capacitor? Again I can't stress enough how much I appreciate your help.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#19
In reply to #18

Re: how do i transform 110v to 130v

06/28/2011 11:44 AM

OK so its a brushles PM motor, it MUST have DC.....

Its only 0.05 amp, but will probably surge a bit at switch on.

A simple Pulse Width modulator can be made from schematics available on the web, to allow the DC to be cut down to an average of 130VDC.....Even a good linerar regulator may be able to supply the 130VDC , with a suitable, even the starting current as well.....

It should be quite an easy job........

PS. There may be more "modern" methods to supply 130VDC at a steady 1 or 2 amps that I am unaware of, so you should listen to the other CR4 guys, they may well have better ideas than I do!!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#24
In reply to #18

Re: how do i transform 110v to 130v

06/29/2011 5:04 AM

The last three components you have identified may be suitable for "parts" of a complete design to achieve what you're aiming for. However they are totally unsuitable for the roles I think you are envisioning for them.

I strongly suggest you consider buying an off the shelf 130VDC PSU like the one I suggested in post #9

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru

Join Date: Oct 2008
Location: Deepest Darkest Rutherford Oz
Posts: 951
Good Answers: 145
#2

Re: how do i transform 110v to 130v

06/25/2011 8:12 PM

Like I said in your other thread,

You need to tell us how much current the motor will draw on start up and running. This hall has a bearing on how you spec the components you need.

You will need a transformer to isolate the rectifier from the mains.

The supply authorities are really not keen on rectifiers directly on the mains.

Depending if you use a full wave or a bridge rectiier circuit you'll get around what you want.

__________________
There are two reasons for a man to do a thing, One that sounds good, and the real one...
Register to Reply
Member

Join Date: Jun 2011
Posts: 6
#4
In reply to #2

Re: how do i transform 110v to 130v

06/25/2011 9:12 PM

The draw on start is'nt listed, but the draw running is .5 Amps and its a fixed magnet if that helps. Your saying i still need a transformer before the rectifier? If so what parts do you recomend to get this thing running nicely (for cheap)?

Register to Reply
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#5

Re: how do i transform 110v to 130v

06/26/2011 1:04 AM

You can put a standard 110/18 Volts transformer in buck mode on wall outlet, net output you will get is 115-18= 92 Volts, rectifying it with capacitor on output can give you about 1.41x92=130 Volts,make sure transformer is adequate to the motor full load current.

Register to Reply
Power-User

Join Date: Sep 2006
Location: Houston Texas
Posts: 282
Good Answers: 16
#7

Re: How Do I Transform 110V To 130V

06/26/2011 10:25 PM

Make it easy on yourself and just purchase a dedicated DC motor controller. We specify the PWM drive from KB Electronics

http://www.kbelectronics.com/data_sheets/kbws.pdf

__________________
Specializing in Dynamic Weighing Systems for Powder and Bulk Solids Handling
Register to Reply
Guru

Join Date: Oct 2006
Location: Surrey BC Canada
Posts: 1571
Good Answers: 42
#8

Re: How Do I Transform 110V To 130V

06/27/2011 12:19 AM

If you full wave rectify and feed that directly to your motor, without additional capacitors, the average DC voltage is "Line volts" x (2√2) /∏ = 99 volts Now subtract a couple volts for your diodes.

The problem of trying to peek ride with a filter capacitor is that the capacitor value changes with load. The diodes also have to be sized to take higher peek currents, which is not a big deal with the small motor you have.

Working backwards you will need a single phase AC supply of about 150vac.

A small 30 or 40 volt transformer can be connected in boost configuration to provide this, or even better use a step up isolation transformer.

Now if you use a dimmer switch ahead of your bridge rectifier you can have a poor mans speed regulator!

Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2005
Location: Hemel Hempstead, UK
Posts: 5826
Good Answers: 322
#9

Re: How Do I Transform 110V To 130V

06/27/2011 5:06 AM

Output Voltages

5.1V/15A, 12V/8A 24V/4A;

36V/3A, 48V/2A, 72V/1.5A or

130V/0.75A are standard.

Consult factory for other output

voltages.

__________________
If you spend all your time looking for people and things to complain about: trust me, you will find plenty to complain about.
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#17

Re: How Do I Transform 110V To 130V

06/28/2011 10:31 AM

Turning the AC into DC, smoothing it a little with a few caps is a good move, then you could use a DC motor speed controller to bring the voltage down to the value required.....

I am assuming (maybe wrongly) that this is a brushed DC motor and not a brush-less.

It could be a universal motor (no need then to convert to DC by the way if true, also called a series wound motor, not usual for pumps I believe, but often for fans), which will probably work just fine on AC.

Actually, a normal, no electronics, DC shunt motor (saying that will stir up the fanatics I am sure on CR4!!), will also run on AC. Any motor will work on AC provided the fields and the brushes swap polarity at one and the same time.....just like AC does.

Only a Permanent Magnet Motor or most brush-less will definitely NOT work on AC.

Till the motor type is definitely known, I cannot be any more helpful, sorry.

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Jun 2011
Posts: 135
Good Answers: 7
#20

Re: How Do I Transform 110V To 130V

06/28/2011 2:17 PM

What you need to understand is that the AC voltage you are using is 120V RMS, not peak. The 120V (root mean square) voltage coming from your outlet can do about the same amount of work (power), as a DC source of 120V. Using the RMS value makes the math easy when computing AC power. P=I*E just like when you are calculating power for DC circuits.

Because the AC voltage varies over time, it starts at 0V, then climbs to 169V (the peak),then drops to 0V again. Then it drops further to -169V (the negative peak), before climbing back up to 0V and the whole process begins again. Power mains repeat this cycle at either 50 or 60 cycles per second (Hertz). The frequency used depends on the part of the world you are in. In this example the RMS voltage is 120V, the peak voltage is 169V, and the peak to peak voltage is 339V. All three of these values are correct at the same time because they are measuring different aspects of the waveform.

To convert the RMS voltage to peak voltage multiply by 1.414.

To convert from peak voltage to RMS multiply by .707.

When using a diode to convert the AC voltage to DC, the diode allows the current to flow only while the voltage is positive. Over time the voltage increases all the way up to the peak voltage. All the time that the voltage is increasing, current flows, and the voltage goes up. Then the source voltage drops down to 0V and then to -169V, then back to 0V, to start the cycle over again. However, when the source voltage drops below that first peak, the diode is reverse biased and will not allow any current to flow, so the peak is the voltage that is stored in the capacitor.

When power generation and distribution were in their infancy, in the U.S., there were two rival groups. One group led by Edison, wanted to use DC voltage. The other group led by Tesla and Westinghouse wanted to use AC current. Ultimately the AC group won because of the ease of distribution. Because transformers can be used, the voltage can be increased. When the voltage is doubled, the current needed to perform a task is cut in half. For example if you had a 120W resistive load, with 120V RMS, 1 amp of current will flow. For the same 120W load, with 240V RMS only .5A will flow. In actual practice actual distribution systems use many thousands of volts in their distribution circuits and use transformers to step the voltage down just before handing it off to you.

__________________
It gets interesting when you put fuel and oxygen in the same molecule, without allowing them to react, YET!
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#21
In reply to #20

Re: How Do I Transform 110V To 130V

06/28/2011 3:12 PM

Your last paragraph is either showing that you have not fully understood Ohm's law yourself, or that your powers of explanation are not your strong suit. Sorry!!

I see where you are coming from, but there are better ways to explain it than that!!!!

For it to work as you explain, the resistance of the load has to quadruple to make it work at the same power with double the voltage.

Power = I x I x R = 1 x 1 x 120 Ohms = 120 watts

Power = I x V = 1 x 120V = 120 watts

or

Power = I x I x R = 0.5 x 0.5 x 480 Ohms = 120 watts

Power = I x v = 0.5 x 240V = 120 watts

It is not easily apparent to many that it is therefore "same" 120W load as you incorrectly put it......it is actually a "different" 120W load of 4 x the resistance........

You need to make explanations that can be easily understood by all I feel......

Sorry to be picky....and I hope this helps a little.....

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Jun 2011
Posts: 135
Good Answers: 7
#22
In reply to #21

Re: How Do I Transform 110V To 130V

06/28/2011 4:32 PM

I didn't say the resistance was the same... I said the wattage of the load was the same in both cases. The word resistive in the sentence is meant to indicate that the load is passive, and to eliminate reactive and inductive loads. You are correct, the resistance of the load does have to change to keep the power dissapated by the load the same in both instances.

I was trying to show that when transfering the same amount of power(wattage), if the voltage doubles, then the current will half. This lowering of the current means that smaller wires can be used to transfer the same amount of power. This makes the long distance distribution of power feasable.

Sorry if I was confusing.

__________________
It gets interesting when you put fuel and oxygen in the same molecule, without allowing them to react, YET!
Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#23
In reply to #22

Re: How Do I Transform 110V To 130V

06/28/2011 4:44 PM

Your last sentence was:-

Sorry if I was confusing.

I answer that with:-

That's the fun of CR4!!

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Guru

Join Date: Dec 2007
Location: California
Posts: 2363
Good Answers: 63
#25
In reply to #22

Re: How Do I Transform 110V To 130V

06/29/2011 11:34 AM

Actually it seems to be more of an explanation about the rms application and meaning of rms power. It would probably have been helpful to elaborate on where the 0.707 and 1.414 values are derived from and what their meaning is so people can understand why rms is representative of the power delivery. As in explaining the application of the square root of 2 to the area under the half cycle of a sinusoidal AC curve.

Register to Reply
Power-User

Join Date: Jun 2011
Posts: 135
Good Answers: 7
#26
In reply to #25

Re: How Do I Transform 110V To 130V

06/29/2011 12:55 PM

The 1.414 number is the square root of 2, and the .707 is it's inverse. Those numbers work just fine as constants for the conversion of RMS to peak, and the reverse. I thought my post was headed off topic and getting too long already, so I left it out.

__________________
It gets interesting when you put fuel and oxygen in the same molecule, without allowing them to react, YET!
Register to Reply
Register to Reply 26 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (5); brick (3); Circuit Breaker (1); Codemaster (2); Delmar (1); GW (1); Lapin (3); rakesh_semwal (1); ramasmy (1); Randall (3); RCE (2); SimpleMind (2); Tobugrynbak (1)

Previous in Forum: how do i get a 110/120v transfered to 140/150v?   Next in Forum: Current Density

Advertisement