Insulation Resistance Test For Wye Connected Generator

06/29/2011 10:18 PM

Hi all,

I have currently a 4 wire, 6 leads - 3 phase wye connected generator and i am intending to perform insulation resistance test on the generator.

I manage to get the IR test readings for Phase1/2/3 - Ground.

However , for the insulation resistance test between the phases ( i.e Phase 1 - 2 , phase 1 - 3 etc ). I am constantly getting 0 ohmn.

What could be the problem causing this?

Btw, I have already removed the neutral point of the generator

Can any kind souls advise please?

Urgent ! As i am doing th eload test soon !

__________________
There is no limit towards how much one can learn.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#1

Re: Insulation Resistance Test For Wye Connected Generator

06/29/2011 11:34 PM

Ahem. I presume that you get zero ohms with a megger because you were just testing for insulation resistance. If you look at a Wye wiring diagram, you should easily see why you have a low resistance between phases.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Commentator
Engineering Fields - Power Engineering - Power Engineering Passion Engineering Fields - Electrical Engineering - Engineering Passion India - Member - New Member

Join Date: Mar 2011
Location: Noida, (U.P.), India.
Posts: 99
Good Answers: 6
#2
In reply to #1

Re: Insulation Resistance Test For Wye Connected Generator

06/30/2011 3:21 AM

I am agree with redfred,

If you are testing insulation resistance of a star connected generator with the isolated neutral, the insulation tester will never show a reading of 0 Ohm until and unless there is any short-circuit between the phases. I think you have forgot to isolate the neutral.

But if you have isolated the neutral, then remove all connections of all 6 leads and measure insulation resistance between the phases and ground.

Vinu_Answers Sure_Answers

__________________
Sure Answers Always
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: Insulation Resistance Test For Wye Connected Generator

06/30/2011 2:16 PM

"But if you have isolated the neutral, then remove all connections of all 6 leads and measure insulation resistance between the phases and ground"

Our OP has already tested 3 phases to ground and from what I can see got good readings. He does now need to split the star point to test between phases.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#4

Re: Insulation Resistance Test For Wye Connected Generator

06/30/2011 10:44 PM

I assume you have a 3-terminal insulation tester . . . Hi - Lo - Guard.

Also assume that all your 3 phases - with 6 leads are disconnected from ground.

SO, to test between phase A to B, connect A to Hv, . . B to Lo, everything else to Guard and ground it.

Register to Reply
Active Contributor

Join Date: Jun 2009
Posts: 12
#5

Re: Insulation Resistance Test For Wye Connected Generator

07/02/2011 4:14 AM

hi,

greetings from India,

6 leads mean R (r1r2),Y (y1,y2) B (b1,b2)

1. you have tested Ph- Earth and got values( hope those are acceptable as you have not mentioned them (above 20 M ohm))

2. do you have removed N link between r2-y2-b2 ?

if so then you must get good IR between r1 & y1, y1 & b1 and b1 & r1.

if this shows '0' M ohm then there must be inter turn fault (or due to heavy moisture content)

Otherwise check the set for residual voltage by removing excitation.

this must be balanced and equal P-P and P-n wise.

if this test is ok then you may start the set.

Register to Reply
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aditya01 (1); olehwi (1); redfred (1); TonyS (1); Vinu_Answers (1)

Previous in Forum: Brush/Brushless Synchronous Motor?   Next in Forum: UPS Neutral and Utility Neutral

Advertisement