UPS Neutral and Utility Neutral

06/29/2011 11:27 PM

Can you tie ups neutral and utility neutral together? I have one digital input module..Some points will be on ups and some on utility. Will there be any issue if I tie both neutral together?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: UPS Neutral and Utility Neutral

06/30/2011 6:38 AM

What sort of input?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#2

Re: UPS Neutral and Utility Neutral

06/30/2011 8:42 AM

Yes.

There will be a problem of circulating currents.

Better not tie 2 neutrals.

Some times, for better safety, ultra isolation transformers are provided on the load side, so that 2 neutrals are not joined.

__________________
Exploring the Science of Electricity
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 67
Good Answers: 2
#3

Re: UPS Neutral and Utility Neutral

07/01/2011 1:10 AM

Since both neutral will be in any case grounded, these will be shorted through ground. There is no harm to short them and ground them.

Register to Reply
Guru
Popular Science - Weaponology - New Member Safety - ESD - New Member Hobbies - Fishing - New Member

Join Date: Sep 2006
Location: Near Frankfurt am Main, Germany. 50.390866N, 8.884827E
Posts: 17996
Good Answers: 200
#6
In reply to #3

Re: UPS Neutral and Utility Neutral

07/01/2011 7:34 AM

Yes there is, if they are both grounded NOW, another connection will give a "ground loop". Not recommended.

Depending upon how the UPS is designed, something might burn of they are not both on the same ground, for instance, if they were never designed to be connected together.

You need a UPS designer here for some detailed facts.

My advice till then is not to do anything at all in that area......a properly designed UPS will have ground and neutral linked in some PROPER way. If its a Chinese ripoff, all bets are off.......

If so, wear galoshes and rubber gloves when using anything on the UPS (buy a bigger keyboard!)

__________________
"What others say about you reveals more about them, than it does you." Anon.
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#7
In reply to #3

Re: UPS Neutral and Utility Neutral

07/01/2011 7:46 AM

What about the interference by DC leakage currents while joining the 2 neutralS?

Earth common via earth is not a problem. Joining Earth conductor to earth electrodes some times might be a problem, so isolated earths are required.

There should be a spacing of 3 times the depth of earth electrodes between the 2 earth electrodes, so , you get 2 distinct effective earth electrodes.

This code of practice is assumed that you follow.

__________________
Exploring the Science of Electricity
Register to Reply
Participant

Join Date: Jun 2011
Posts: 1
#4

Re: UPS Neutral and Utility Neutral

07/01/2011 1:48 AM

For the utility supply the ground an neutral are tied together at the supply entry to the premises, with a separate ground wire from there. With the power network in the premises the ground is tied at various points, inadvertantly creating poor connections with some impedances. This in turn creates small potential differences which can be witnessed when neutral and ground is tied together further along the power distribution network. These connection impedances resonates also with certain frequencies so that some power spikes are amplified significantly - more seriously so between ground and neutral. In order to eliminate these ground-neutral residual and noise voltages a UPS is not enough. (If the ground-neutral voltage problems cannot be rectified, particularly for older installations,) an isolation transformer is used where the secondary neutral is also used as the ground - with a proper earth pin as ground. On this isolated side the residual voltage between ground and neutral is now eliminated (usually this voltage is bad news for electronics) and one can connect UPS neutral to isolated power neutral. Remember, the UPS cleans up noise from the power between live and neutral, not between any of live or neutral and ground.

Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2006
Location: Placerville, CA (38° 45N, 120° 47'W)
Posts: 6215
Good Answers: 248
#8
In reply to #4

Re: UPS Neutral and Utility Neutral

07/01/2011 1:44 PM

GA for a first post!

Welcome to CR4!

__________________
Teaching is a great experience, but there is no better teacher than experience.
Register to Reply
Active Contributor

Join Date: Sep 2010
Location: Hyderabad
Posts: 11
Good Answers: 1
#5

Re: UPS Neutral and Utility Neutral

07/01/2011 2:08 AM

1)Is it on line UPS or Off line UPS ?

2)If it is Off line UPS you can tie ups neutral and utility neutral together.No problem.

3)If it is on line UPS, not advisable to tie UPS neutral and utility neutral together,If tie together Voltage fluctuation may come.

__________________
"Everything you can imagine is real." -- Pablo Picasso
Register to Reply
Register to Reply 8 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Andy Germany (1); Ayyavaru (1); dkwarner (1); harry potter (2); Learner42 (1); PWSlack (1); rd van Zyl (1)

Previous in Forum: Insulation Resistance Test For Wye Connected Generator   Next in Forum: Automatic Star - Delta - Star Converter

Advertisement