Hello,
ASME B31.1 - 122.1.2 Steam Piping
(A.3) For steam piping between the first stop valve and the second valve, when one is required by para. 122.1.7
Q1) What is one mentioned above?
Q2) At CCPP Plant Configuration GTx2-HRSGx2-STx1
- What is Design Pressure Criteria from superheater outlet to turbine throttle valve?
- What is Design Pressure Criteria for the lowest pressure at Safety valve on the superheater?
- What is the lowest setting pressure of Boiler Drum Relief Valve?
Thanks
Pathfinder Tags: ASME B31.1 Steam Piping
Good Answers: 34
Re: ASME B31.1 Steam Piping
06/30/2011 10:22 AM
Not sure, but maybe you are looking for this ( From ASME B.31.1 par 100.1.2 and Fig´s):
Piping between the terminal points and the valve or
valves required by para. 122.1 shall be provided with
Data Reports, inspection, and stamping as required by
Section I of the ASME Boiler and Pressure Vessel Code.
All welding and brazing of this piping shall be performed
by manufacturers or contractors authorized to
use the appropriate symbol shown in Figs. PG-105.1
through PG-105.3 of Section I of the ASME Boiler and
Pressure Vessel Code. The installation of boiler external
piping by mechanical means may be performed by an
organization not holding a Code symbol stamp. However,
the holder of a valid S, A, or PP Certificate of
Authorization shall be responsible for the documentation
and hydrostatic test, regardless of the method of
assembly. The quality control system requirements of
shall apply. These requirements are shown in Appendix J
of this Code.
06/30/2011 10:36 PM
The "one" refers to the second stop valve, if it is required, which depends on circumstances and the Code being followed.