Motor HP for Given CFM

06/30/2011 5:14 AM

Dear All,

I have CFM and Static Pressure in mmwg and I want to calculate the motor HP. Could you tell me How it measures? what's the formula?

Register to Reply
Pathfinder Tags: Motor capacity of req. CFM
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: motor hp for given cfm

06/30/2011 5:36 AM

Pressure rise multiplied by volumetric flowrate divided by efficiency. It will get to the right order-of-magnitude.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Jun 2011
Posts: 2
#2

Re: motor hp for given cfm

06/30/2011 6:34 AM

Use Kruger software for the same.

Register to Reply
Commentator
Popular Science - Weaponology - New Member India - Member - New Member

Join Date: Jul 2008
Location: INDIA - GOLDLAND
Posts: 89
Good Answers: 1
#3

Re: motor hp for given cfm

06/30/2011 6:57 AM

Use following equation to get the BHP.

BHP = {[capacity in cfm X pressure in inches ] \ 6356 }* 0.75

This BHP is at duty point .

Now , Motor hp = 1.15 * BHP.

From motor selection data select next available motor. Also, don`t select the motor on borderline, cause fan is fabricated one and it is an art. So some allowance should be considered.

The fan can be tested by IS method or simply by anemometer method. Current consumption at different damper opening gives you suitability check for the motor you selected.

Register to Reply Score 1 for Good Answer
Guru
India - Member - New Member Engineering Fields - Electromechanical Engineering - New Member

Join Date: Oct 2006
Location: India, 200 Km. North of Delhi.
Posts: 1393
Good Answers: 53
#4

Re: Motor HP for Given CFM

06/30/2011 10:00 AM

Make sure these are intersecting values or pressure and airflow on pressure airflow curve in the normal operating conditions,and are not the maximum pressure and maximum airflow, Otherwise your all calculations may go wrong, and you may end up with much bigger unit than of required.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#5

Re: Motor HP for Given CFM

07/01/2011 1:31 AM

Following formula can be used to calculate motor power:

Air Power (kW) = Pressure rise (Pa) x Flow rate (Cu.m/s)

If pressure is static it is 'static air power' and for total pressure it is 'total air power'.

Break kW = Air Power (kW) x Efficiency

Use 'static efficiency' or 'total efficiency' (~0.75) depending on air power.

Motor kW = 1.15 x Break kW

Motor HP = Motor KW/ 0.75

Register to Reply Score 1 for Good Answer
Register to Reply 5 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

manoj negi (1); pritam (1); PWSlack (1); rakesh_semwal (1); sanjaykangralkar (1)