Micro-Farad Calculation

07/01/2011 11:15 AM

As will become obvious, I am not an electrician. I am attempting to determine the micro-farad value necessary for power factor correction. I have the following data available: KV, KVAR, V, PF, KW, AMP. Can I use this data to calculate the µF value? If so, can someone assist me with that formula?

Thank you

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Micro-farad calculation

07/01/2011 11:18 AM

It would be better to give that data to someone who can, then, rather than struggle with it one's self.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#2

Re: Micro-Farad Calculation

07/01/2011 11:36 AM

Corrected KVA x 10^9
C = ----------------------------
2 pi x f x e^2


Where;
C = required capacitance in microfarads
f = frequency of applied voltage
e = applied voltage

You could use Tau instead of 2Pi, but that would only hasten Pi's death.

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#3

Re: Micro-Farad Calculation

07/01/2011 1:14 PM

I'm not sure why you're looking for the value in μF, when most of the power factor caps I've seen are rated & sold by kVAR. Take a look at the following site which gives a LOAD of assorted on-line calculators for electrical applications. The first page (check out all 8 pages - lots of good stuff!) gives 2 different ones to calculate kVAR of caps needed based on your existing and desired power factor. Beware of trying to correct to a PF of 1.0 - Not a good idea. Better to correct to 0.95 or so.

http://www.electricsmarts.com/container.aspx?tab=tools&distid=19542&showresults=1&limit=&ph=calculators&aw=&anw=&ew=&page=1

Here's a site that gives a good practical explanation of PF correction and does example calculations:

http://home.earthlink.net/~jimlux/hv/pfc.htm

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply Score 1 for Good Answer
Active Contributor

Join Date: Jun 2011
Posts: 19
Good Answers: 1
#4
In reply to #3

Re: Micro-Farad Calculation

07/01/2011 8:36 PM
Register to Reply
Guru

Join Date: Feb 2006
Posts: 1758
Good Answers: 6
#5
In reply to #3

Re: Micro-Farad Calculation

07/02/2011 5:01 PM

And it is professional job, cannot be a fixed values connected permanently until ensured that does not reach unity and beyond. Damage to Powerlines or equipment may occur.

Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#7
In reply to #3

Re: Micro-Farad Calculation

07/05/2011 11:00 AM

I have never heard of anyone warning off of unity for power factor. Why would you not want that?

Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#8
In reply to #7

Re: Micro-Farad Calculation

07/05/2011 2:26 PM

If you try to correct to get 1.0 PF, changes in load can drive the system "past" unity to capacitive power factor. Then you run the distinct likelihood of getting into a resonant condition. The resulting overvoltages are well-documented to be destructive for electrical equipment.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#9
In reply to #8

Re: Micro-Farad Calculation

07/05/2011 3:14 PM

I see what you are saying. I shoot for the best I can, but I have a very stable load running 24/7 on an UPS which manages a 1.00 for the provider. On the supply side of the UPS we average about .96 pf.

We monitor for destructive harmonics regularly to prevent such unfortunate occurrences.

Register to Reply
Guru

Join Date: Feb 2010
Posts: 1013
Good Answers: 36
#6

Re: Micro-Farad Calculation

07/03/2011 7:21 PM

If V is the phase voltage and call it U in a 3 phase supply, f is the frequency.

And required KVAR = Q

And Cd = Capacitor Value for each phase In Delta connection

And Cs = Capacitor Value for each phase to Neutral in Star connection

Then Cd = [(Q*1000) / (2*∏*f*U²*√3)]*10^6

And Cs = 3*Cd

Register to Reply Score 1 for Good Answer
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

cuba_pete (3); dennis461 (1); Haajee (1); LAA_Lucke (1); PeterT (2); PWSlack (1)