07/01/2011 11:15 AM
As will become obvious, I am not an electrician. I am attempting to determine the micro-farad value necessary for power factor correction. I have the following data available: KV, KVAR, V, PF, KW, AMP. Can I use this data to calculate the µF value? If so, can someone assist me with that formula?
Thank you
Re: Micro-farad calculation
07/01/2011 11:18 AM
It would be better to give that data to someone who can, then, rather than struggle with it one's self.
Good Answers: 44
Re: Micro-Farad Calculation
07/01/2011 11:36 AM
Corrected KVA x 10^9
C = ----------------------------
2 pi x f x e^2
Where;
C = required capacitance in microfarads
f = frequency of applied voltage
e = applied voltage
You could use Tau instead of 2Pi, but that would only hasten Pi's death.
Good Answers: 131
07/01/2011 1:14 PM
I'm not sure why you're looking for the value in μF, when most of the power factor caps I've seen are rated & sold by kVAR. Take a look at the following site which gives a LOAD of assorted on-line calculators for electrical applications. The first page (check out all 8 pages - lots of good stuff!) gives 2 different ones to calculate kVAR of caps needed based on your existing and desired power factor. Beware of trying to correct to a PF of 1.0 - Not a good idea. Better to correct to 0.95 or so.
http://www.electricsmarts.com/container.aspx?tab=tools&distid=19542&showresults=1&limit=&ph=calculators&aw=&anw=&ew=&page=1
Here's a site that gives a good practical explanation of PF correction and does example calculations:
http://home.earthlink.net/~jimlux/hv/pfc.htm
07/01/2011 8:36 PM
07/02/2011 5:01 PM
And it is professional job, cannot be a fixed values connected permanently until ensured that does not reach unity and beyond. Damage to Powerlines or equipment may occur.
Good Answers: 44
07/05/2011 11:00 AM
I have never heard of anyone warning off of unity for power factor. Why would you not want that?
Good Answers: 131
07/05/2011 2:26 PM
If you try to correct to get 1.0 PF, changes in load can drive the system "past" unity to capacitive power factor. Then you run the distinct likelihood of getting into a resonant condition. The resulting overvoltages are well-documented to be destructive for electrical equipment.
Good Answers: 44
07/05/2011 3:14 PM
I see what you are saying. I shoot for the best I can, but I have a very stable load running 24/7 on an UPS which manages a 1.00 for the provider. On the supply side of the UPS we average about .96 pf.
We monitor for destructive harmonics regularly to prevent such unfortunate occurrences.
07/03/2011 7:21 PM
If V is the phase voltage and call it U in a 3 phase supply, f is the frequency.
And required KVAR = Q
And Cd = Capacitor Value for each phase In Delta connection
And Cs = Capacitor Value for each phase to Neutral in Star connection
Then Cd = [(Q*1000) / (2*∏*f*U²*√3)]*10^6
And Cs = 3*Cd