Relay Anomaly

07/05/2011 2:20 AM

recently the 11 kv conductor snapped but i was astronised to know that the earth fault relay didnot operate. the earth fault relay is very healthy and on other times(100 out of 100) it operates normally... the settings(time and overcurrent) are quit good.........

can anybody please suggest me the poosible reasons...................

thnkx in advance................

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: relay anomaly

07/05/2011 2:28 AM

When the 11kv conductor snapped, which part (energized/deenergized) was still connected to the earth fault relay? I suspect this would be really important.

I too might be astonished by this, but astronised? Did you actually see stars?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Active Contributor

Join Date: Apr 2011
Location: india
Posts: 21
#5
In reply to #1

Re: relay anomaly

07/07/2011 11:21 AM

thankx a lot 4 ur pecious comment......

brother it was actually energised (sending) part wic was in connection with the ground......

so according 2 the logic the relay must had to trip as the fault persist for nearly an hour ..............

can u suggest me some possible reasons 4 this please....

thankz sir..........

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6
In reply to #5

Re: relay anomaly

07/08/2011 7:05 PM

Read the above responses again, your answer is there.

The AMOUNT of earth fault current flow that occurred was insufficient to trigger the relay. It isn't likely to be any more complicated than that. Just because the cable was touching the ground does not automatically mean massive amounts of current will flow. Could have been high resistance, the ground may have been dry, all manner of issues that prevented the current from flowing in significant amounts.

That's why live conductors lying on the ground should never be touched. YOU might be the catalyst that facilitates current flow, but by the time the relay trips, you are a charred cinder.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: relay anomaly

07/05/2011 3:51 AM

The snapped conduct mustn't have made a good a good connection to earth. Most OH lines have a high earth fault tolerance otherwise they would trip every time it rains.

I've seen a 11KV line snap and the conductor was lay on dry ground quite happily setting fire to the grass, the supply didn't trip un till it was done manually.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: relay anomaly

07/05/2011 3:55 AM

The reason is that, when the conductor broke, no earth fault was created.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Posts: 989
Good Answers: 14
#4

Re: Relay Anomaly

07/06/2011 8:47 PM

Probably the earth fault relay was waiting for a currious squirrel to come by to see what that line was laying on the ground...

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

129CBRider (1); JRaef (1); mir imran altaf (1); PWSlack (1); TonyS (1); Tornado (1)