Is Leakage Current Test Necessary for Lighting Fixtures?

07/05/2011 4:25 AM

Hi,

Is leakage current test necessary for Lighting fixtures?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Is leakage current test necessary for Lighting fixtures.?

07/05/2011 4:28 AM

Not if the enclosure is made of non-conductive materials, or the fitting is double-insulated.

There simply won't be any.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Good Answer
Guru

Join Date: Dec 2010
Posts: 1895
Good Answers: 44
#2
In reply to #1

Re: Is leakage current test necessary for Lighting fixtures.?

07/05/2011 1:52 PM

Yeah, what he said.

Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#3
In reply to #2

Re: Is leakage current test necessary for Lighting fixtures.?

07/05/2011 10:33 PM

NO, if you do not care to be shocked, or somebody else shocked. In that case such a test is superfluous. Are you nuts, or plain lazy?!?

Register to Reply
Associate

Join Date: Dec 2009
Location: SOUTH AFRICA near the' Cradle of mankind'
Posts: 41
Good Answers: 3
#4

Re: Is Leakage Current Test Necessary for Lighting Fixtures?

07/06/2011 1:51 AM

Hi there.

International standard IEC 60598-1 Requires that you do either an electric strength test by applying a minimum of 1.5kV a.c. for a minimum of 1 second where a maximum leakage current of 5 mA is permitted.

OR

An Insulation resistance test by applying 500 V d.c.for 1 second. with a minimum resistance of 2 M ohm.

The tests are conducted between the live and neutral terminals linked together and the earth terminal or between the conductors of class II and class III luminaires and metal parts/enclosures.

__________________
The more I practice the luckier I get.(Player)
Register to Reply
Associate

Join Date: Dec 2009
Location: SOUTH AFRICA near the' Cradle of mankind'
Posts: 41
Good Answers: 3
#6
In reply to #4

Re: Is Leakage Current Test Necessary for Lighting Fixtures?

07/06/2011 2:08 AM

Sorry, I did not mention that IEC 60598- specifically relates to light fittings.

__________________
The more I practice the luckier I get.(Player)
Register to Reply
Active Contributor

Join Date: Sep 2009
Posts: 18
#8
In reply to #4

Re: Is Leakage Current Test Necessary for Lighting Fixtures?

07/06/2011 6:33 AM

About the insulation test are you sure that it has to be tested for 1 sec or is it 1 min. for HV and Insulation does it has to be performed between Line & Neutral & Body or just line and neutral.

Register to Reply
Guru

Join Date: Jan 2007
Location: Edinburgh, Bonnie Scotland
Posts: 1335
Good Answers: 23
#5

Re: Is Leakage Current Test Necessary for Lighting Fixtures?

07/06/2011 1:54 AM

In the UK, all portable appliances require to be regularly 'PAT' tested. This involves checking the leakage current. Items fail if there is any. Fixed appliances get tested on fitting, and after modifications, but not on a regular basis.

__________________
Madness is all in the mind
Register to Reply
Power-User
United Kingdom - Member - New Member Engineering Fields - Transportation Engineering - New Member Technical Fields - Marketing/Advertising - New Member Hobbies - Target Shooting - New Member

Join Date: Sep 2007
Location: South coast of England
Posts: 411
Good Answers: 36
#9
In reply to #5

Re: Is Leakage Current Test Necessary for Lighting Fixtures?

07/06/2011 7:07 AM

All equipment has some leakage current however small, the amount permitted depends on the class and use of the equipment.

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Jun 2011
Location: New Zealand
Posts: 75
Good Answers: 5
#7

Re: Is Leakage Current Test Necessary for Lighting Fixtures?

07/06/2011 2:34 AM

The answer is dependent upon your reglatory requirements, however even if it is not specified for your reglatory area, insulation resistance testing is a good thing to do. Before trying to test make sure that the lamps are removed from their fittings and the light switches are turned on. If you have two way or intermediate switches then a test will be required for each of the possible switching positions.

Register to Reply
Register to Reply 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Chankley (1); cristle (1); cuba_pete (1); GM1964 (1); Greg M (2); leveles (1); PWSlack (1); shoebelixir (1)

Previous in Forum: E/F Realy Setting for Office Building Load   Next in Forum: When Do I Need to Change My Solar battery?

Advertisement