Capaci of a Generator

07/05/2011 7:09 AM

Please reply asap.

1. we have a load of about 100kw, atleast how many kilowatts generator we can use there.?

2. Can we use this generator 24hrs contineously for a long time.??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Anonymous Poster #1
#1

Re: Capaci of a Generator

07/05/2011 7:44 AM

100kW, and yes. Is that asap enough?

Register to Reply
Participant

Join Date: Jul 2011
Posts: 4
#2
In reply to #1

Re: Capaci of a Generator

07/05/2011 8:56 AM

Sir, our load is 100kw how we can use generator with the capacity of 100kw. i think it must be more than our load.

and what about the countinous running of a generator for long time ( 6 months or more) answer any experienced person please. thanks

Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#3

Re: Capaci of a Generator

07/05/2011 9:08 AM

Bhatti,

Your question is too vague to come up with a viable answer.

Do some research on the internet. You should be able to find what information is required to come up with the correct size.

Try a Google search, here allow me.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#4

Re: Capaci of a Generator

07/05/2011 9:29 AM

Two 500 KVA generators (one as stand by) should do it!

Right now to be sensible:

  • Are there any heavy loads to be started?
  • How critical are the loads
  • Power factor of the load

There's others factors I can't / don't want to think of at the moment, (I've had a few beers). You know the details of the loading we don't. If the load is critical it needs a standby generator. Heavy starting loads require a generator of X% over the base load, depending on the starting characteristics of the load. Power factor is reflected by a higher running current KVAr as to actual theoretical current KW resulting in a higher O/P required at the generator.

A 100KW generator will not supply a 100KW load.

Talk to the generator manufacturers.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Participant

Join Date: Jul 2011
Posts: 4
#5
In reply to #4

Re: Capaci of a Generator

07/05/2011 10:03 AM

Sir There is a load of two heavy Motors of sullary pumps 55KW each and four three phase motors of 7 KW each with 10 in nos hollogon lights of 1000 Watts.

Waiting reply please. Thanks

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Capaci of a Generator

07/05/2011 10:17 AM

Well, (2 x 55kW) + (4 x 7kW) + 1kW is >100kW. Are the big pumps both running at the same time? If so, then the 100kW load figure is too low and a larger generator will be needed.

What about diesel-driven pumps, as an alternative?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #5

Re: Capaci of a Generator

07/05/2011 11:29 PM

You should consider LRC of motors,starting method,whether both starts together etc