Two 500 KVA generators (one as stand by) should do it!
Right now to be sensible:
Are there any heavy loads to be started?
How critical are the loads
Power factor of the load
There's others factors I can't / don't want to think of at the moment, (I've had a few beers). You know the details of the loading we don't. If the load is critical it needs a standby generator. Heavy starting loads require a generator of X% over the base load, depending on the starting characteristics of the load. Power factor is reflected by a higher running current KVAr as to actual theoretical current KW resulting in a higher O/P required at the generator.
A 100KW generator will not supply a 100KW load.
Talk to the generator manufacturers.
__________________
The reports of my death are greatly exaggerated.
Sir There is a load of two heavy Motors of sullary pumps 55KW each and four three phase motors of 7 KW each with 10 in nos hollogon lights of 1000 Watts.
Well, (2 x 55kW) + (4 x 7kW) + 1kW is >100kW. Are the big pumps both running at the same time? If so, then the 100kW load figure is too low and a larger generator will be needed.
What about diesel-driven pumps, as an alternative?