Cable Schedule

07/10/2011 6:24 AM

What is the main different between sentence (3c×2.5mm2 -1run……. & 3c×2.5mm2 -2run) in the cable schedule please advaise

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#1

Re: Cable Schedule

07/10/2011 8:44 AM

I would expect that "3c×2.5mm2" refers to a multi-conductor cable--that is, one jacket containing 3 insulated wires, each with cross-sectional area of 2.5mm^2.

Thus, I would expect 2 runs to refer to 2 such cables run in the same raceway (that is, conduit, cable tray, ...).

But, there is potential for misunderstanding, so I would ask the person / company that generated the cable schedule. It will be cheaper (and less embarrassing) to ask than to redo the work if it is done wrong.

You could phrase your question something like this--"I think this means you want two cables, but I just want to be sure before we do the work."

Register to Reply
Guru

Join Date: Oct 2010
Posts: 1294
Good Answers: 35
#2
In reply to #1

Re: Cable Schedule

07/10/2011 9:04 AM

I should add that somewhere there should also be a cable specification that tells you much more about the cable to be run--maybe just a manufacturer and type number, but maybe things like a temperature specification, and required materials of the jacket and insulation over the individual conductors.

You need to find that specification and make sure you comply with that as well.

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#3

Re: Cable Schedule

07/11/2011 4:11 AM

3cx 2.5mm2 - 1 run, means, three cores, insulated with proper insulation, with proper voltage grade, conductor size of each core is 2.5mm2 and single run or single length laying. Whereas, 3cx2.5mm2 - 2 run, means,three cores, insulated with proper insulation, with proper voltage grade, conductor size of each core is 2.5mm2 and double run or doble length laying.

Manindra.

__________________
Manindra
Register to Reply
Active Contributor

Join Date: May 2011
Posts: 17
#4
In reply to #3

Re: Cable Schedule

07/11/2011 4:18 AM

can you please clarify what meant by length laying (singel or double run)

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#6
In reply to #4

Re: Cable Schedule

07/11/2011 5:03 AM

Single length laying means, from source( panel) to load only one cable connection. Double length laying means, from source( panel) to load two nos cable in parallel connections. Generally this is done to enhance load carrying capacity and minimise voltage drop.

Manindra.

__________________
Manindra
Register to Reply Score 1 for Good Answer
Associate

Join Date: Jul 2008
Location: India, Kuwait
Posts: 31
#5

Re: Cable Schedule

07/11/2011 4:32 AM

From what I understand, you have to lay two cables with the same specs for the same loop.

Maybe 1 is used as a spare... :)

Register to Reply
Register to Reply 6 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Ahmadnaggar (1); gkishorenair (1); manindra (2); rhkramer (2)

Previous in Forum: Earthing via Resistor For Transformer Neutral   Next in Forum: Cable Thermal Withstand
You might be interested in: Cable Laying Services, Cable Assemblies, Cable Trays

Advertisement