Neutral Shift in Star Side

07/11/2011 3:44 AM

pls any one help this concept... i want to knw about the unbalance in star side of a delta/star transformer.... i learnt from book tat the neutral shifts when unbalance occurs... i want to knw clearly... pls explain me... what is meant by neutral shift...??? if un balance occurs in star side what will happen..???

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: neutral shift in star side

07/11/2011 3:48 AM

Unbalance is simply the expression of single phase loads on a three-phase supply. If the circuit protection devices are correctly set, then nothing noticeable will happen.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3
In reply to #1

Re: neutral shift in star side

07/11/2011 11:27 PM

What will be the difference it makes due to unbalanced loads in earthed neutral and unearthed neutral systems?.

__________________
pnaban
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: neutral shift in star side

07/11/2011 5:41 AM

f d neutral aint bonded 2 erth thN a voltage shift cn occur f Ull wrt n nonsense TXT, Ull gt a nonsense ans

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Active Contributor

Join Date: Sep 2009
Location: A.P., India
Posts: 20
#4

Re: Neutral Shift in Star Side

07/16/2011 4:50 AM

Mr. Hamid,
unbalance is caused by the load. Neutral point in a Star Winding is the reference point where the voltage is zero or balanced from 3-phases. To eliminate the problem of Neutral shift (or Floating Neutral Condition), arching grounds due to any problems/faults in the system, the Neutral Grounding is adopted in electrical systems.
Just draw yourself a simple diagram for a Star wound source feeding a 3ph load - both for an Earthed & Unearthed star points of source. Do this for both balanced & unbalanced loads separately. In all the above, no change in circuit values. Calculate currents drawn by the different loads in earthed system, apply same current in unearthed system and calculate back the voltage drops across the each limb of source winding /load. You will find the difference yourself.
If your system's star point is not earthed, to keep the system in balanced condition, during any imbalances in the loads or during any fault, the neutral will get shifted.
sitaram.

__________________
-- sitaram