Installation of Inverter Instead of Star Delta Operation

07/15/2011 12:57 AM

Dear experts. A centrifugal fan connected to 22kw induction motor with motor rpm 1450 and fan rpm is reduced to750 with pulleys. Now an inverter has to be installed to control the motor rpm between 1000\ 750 rpm. of the motor.

My question the existing pulleys are to be replaced or they will serve the purpose. The fan rpm required is 750

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Installation of Inverter instead of Star Delta Operation

07/15/2011 1:26 AM

At least one of the pulleys must be replaced, because the drive ratio will be different.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#2
In reply to #1

Re: Installation of Inverter instead of Star Delta Operation

07/15/2011 1:50 AM

Thanks for the prompt reply you will recommend to replace the fan pulley?

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: Installation of Inverter instead of Star Delta Operation

07/15/2011 2:08 AM

It might depend on the sizes of the existing pulleys. If the motor pulley is now small in relation to suitable belt bending radius, I would opt for increasing it rather than reducing the fan pulley. This will also reduce overhung bearing loads.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Jun 2011
Location: india/gujrat/Bhuj/atps
Posts: 30
#4

Re: Installation of Inverter instead of Star Delta Operation

07/15/2011 2:30 AM

i m not expert but u should change pully of fan side & fit same pully as 22kw motor side pully. In short u should maintan both pully of same OD.

__________________
Curiosity made genius
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: Installation of Inverter instead of Star Delta Operation

07/15/2011 3:09 AM

What if motor rpm of 1000 is to match fan rpm of 750, and motor rpm of 750 is to match fan rpm of ~560?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#6
In reply to #4

Re: Installation of Inverter instead of Star Delta Operation

07/15/2011 3:36 AM

some one out of cr4 forum is advising not to replace the existing pulley of motor and fan.any comments thanks

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: Installation of Inverter instead of Star Delta Operation

07/15/2011 3:53 AM

Is this advice on another thread about the same topic?

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#12
In reply to #7

Re: Installation of Inverter instead of Star Delta Operation

07/16/2011 12:40 AM

no got this information on phone

Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#8

Re: Installation of Inverter instead of Star Delta Operation

07/15/2011 5:42 AM

Why not control the motor speed between 1450 and say 1000 rpm? No need to change the pulleys then.

__________________
The reports of my death are greatly exaggerated.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Feb 2010
Posts: 164
#13
In reply to #8

Re: Installation of Inverter instead of Star Delta Operation

07/16/2011 12:44 AM

in case we maintain the speed of motor between 1450 and 1000 rpm and retain the same pulleys as suggested by you than what will be the rpm of fan

Register to Reply
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#9

Re: Installation of Inverter Instead of Star Delta Operation

07/15/2011 9:30 AM

It's simple, and yet not.

If you want to run at 1000RPM and the pulleys are right now changing the 1450RPM motor to 750RPM, then if you do not change the pulleys, you will only be able to attain 1000RPM by over speeding the motor with the VFD. When you over speed a motor, you are operating in a constant power mode because you can no longer increase the voltage with the frequency. So in effect, your torque is dropping when you are above base motor speed. That's the simple part.

But on a centrifugal fan, flow increases with speed and load on the motor increases at the CUBE of the flow. So to go from 750 to 1000RPM, an increase of 133%, you are increasing the load on the motor by 1.333 or 237%! So if the motor was originally sized to be 22kW for the expected load at 750RPM, increasing the speed to just 1000PM will require 52kW. So now you have a higher load and a motor that is still the same size. Chances are good that your motor was a little over sized, but that much? I doubt it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Anonymous Poster #1
#10

Re: Installation of Inverter Instead of Star Delta Operation

07/15/2011 10:30 AM

Some one alerady asked

The fan rpm required is 750

But you want the motor RPM between 1000 to 750 RPM? ie you want a VFD drive and that means the fan RPM will also change (Repat from the previous query not answered yet)

One interesting part (I am not sure that I am right though) is that the motor power is a bit derated at lower frequencies (VFDs are supposed to be constant torque fellows so power will go down with the speed. The 22KW motor at 1000 RPM will not give the same power. But the fan (still at 750 RPM as earlier) will demand the same.

Question - if your motor speed is 750-1000 RPM why didn't you go for a 6 pole (Synch speed 1000 RPM) with a VFD to bring it down upto 750?

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#11
In reply to #10

Re: Installation of Inverter Instead of Star Delta Operation

07/16/2011 12:37 AM

thanks for the guideline but the client wants to retain the existing siemens motor 22kw, 1450 rpm.client intrest is to go for vfd to control the rpm of the motor say from 1450 to 850 and wants the fan rpm to be 750-800.please dont mind my question in case it has simple solution.

Register to Reply
Anonymous Poster #1
#14
In reply to #11

Re: Installation of Inverter Instead of Star Delta Operation

07/16/2011 8:26 AM

On the theoritical front -

The VFDs work on constant V/f ratio (to maintain the designed flux density in the iron)

So the 1450 KW motor 22KW you want to run at 1000 /850/750 RPM. A simple calculation

Vvfd = Voltage to Keep the V/f constant

New Power = VVfd I Cos φ = (VVfd/V).V.I Cos φ = (VVfd/V). Prated freq

Since the VFDs normally keep the current constant. And that is not usually increased either due to the copper constraint.

RPM Equiv Freq Vvfd Pnewfreq Power (Derating to)

1450 50 Hz 415 V 22 KW 100%

1000 34.5 286 15.2 69%

850 29.3 243.3 12.9 59%

750 25.86 214.7 11.4 51%

Usually it wont matter since the fan load would have gone down with RPM and the usual motor would have been sufficient. But now you want to use a normal 22KW/50Hz motor at 34.5Hz and that means its rated power output will be 15KW and not 22KW. If it can withstand that derating then of course the RPM will later go down and derating will be taken care of by the reduced load demand.

Look from this aspect and then only go about with your pully/ any ther drive train modification. The pulley is simple

It will be the new RPM (1000) Vs Fan (750) now instead of the earlier 2:1

Depending upon your belt section (A,B,C..) there will be recommended diameter of the pulley. If both the new pulleys are in the range of the specific belt, then go for it. Any way if well selected in the previous system the smaller belt (motor) would have been in the range so the fan can be changed to the new.

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#17
In reply to #14

Re: Installation of Inverter Instead of Star Delta Operation

07/18/2011 4:46 AM

thanks for the detail solution. will request the client to work on the basis you have suggested.they have now installed inverter which is suitable for 18.5kw motor instead of 22kw motor. .one drawback with the client maintenance department is that they are doing experiment on pulleys.first they changed the fan pulley than they changed the existing 22kw motor pulley and brought down the rpm of the motor to 600rpm and of the fan to 750-850 rpm.but the result that is energy saving is not according to their requirement in terms of kwh . hope you will update me when needed thanks

Register to Reply
Guru
Engineering Fields - Systems Engineering - New Member Hobbies - Model Rocketry - New Member

Join Date: Dec 2006
Location: Long.92E,Lat.26N
Posts: 1336
Good Answers: 14
#15

Re: Installation of Inverter Instead of Star Delta Operation

07/17/2011 1:08 AM

Kids riddle?

You must Change 1 Pulley at least.

Now that you are changing to VFD motor - better to change the new motor's pulley.

If as you say your fan rpm "required is 750" you cannot have any pulley--you need direct coupling.And VFD is a waste- because you need to have 750rpm out of motor.

So help you God.

Register to Reply
Member

Join Date: Jul 2011
Posts: 8
#16
In reply to #15

Re: Installation of Inverter Instead of Star Delta Operation

07/17/2011 9:08 PM

I agree with @MUKULMAHANT.

This is simple really. If you opt to calculate by pulley ratios, then, you can play around with the size of the pulleys. calculate by simple math, and get the ratios, assumingly that the motor rpm wont drop not even 0.5% (if its that critical - but for a fan/blower, should be ok). Most customers nowadays, they will prefer using VFD or Inverter if they need to pre-program them, let say, at certain time the speed run at 1000rpm, and other times remain 'jog' at 750rpm etc.

And to change to pulley into a same size, is a no-no. because, might as well, just use a direct coupling. unless, you are unsure wether one day the customer will come back to you asking to change back to pulley system or not.

Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#18
In reply to #15

Re: Installation of Inverter Instead of Star Delta Operation

07/18/2011 4:54 AM

thanks for the guidance.but the client wants to retain the existing siemens motor of 22kw he is only intrested to install inverter so that it has final effect on his energy consumption(kwh). as replied earlier the maintenance dept is carrying different options i.e changing of pulleys of motor and fan.the manegement wants to keep the motor pulley and if necessary replace the fan pulley.will highly appreciate any further suggestion from your side

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#19

Re: Installation of Inverter Instead of Star Delta Operation

07/18/2011 6:00 PM

What does the centrifugal fan supply that is attached to the motor?

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 164
#20
In reply to #19

Re: Installation of Inverter Instead of Star Delta Operation

07/18/2011 11:53 PM

it supply fresh air to the plant

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#21
In reply to #20

Re: Installation of Inverter Instead of Star Delta Operation

07/19/2011 10:57 AM

I would assume that it is set up as CV to the plant. In that case I would agree with all the previous advise, you will need to change one of the pulleys to maintain proper air flow on the forward curve fan when reducing hertz to the motor.

What may be a better option and less expensive than the VFD would be to (though the owner does not want to change the motor) replace the motor with a premium efficient motor. The are designed to provide energy savings at full amperage draws all based on their power factor curves.

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Register to Reply 21 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (2); JRaef (1); marses (1); MUKULMAHANT (1); salahuddin zia (8); Stedou73ish (2); TonyS (1); Tornado (4); yk (1)