KW-KVA-KVAR-PF

07/16/2011 12:03 AM

hi....There are many manufactures in the market who promise to improve power factor and reduce your electricity bill. I m dealing with an intelligent saver, that is nothing but the combination of capacitors. It helps to improve the power factor, KVA and KVAR. How come it does not have any effect on KW.

It is plug and install device which can fix at any outlet socket, means across the circuit.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#1

Re: KW-KVA-KVAR-PF

07/16/2011 12:16 AM

How does it work, and why?

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Power-User
Popular Science - Weaponology - New Member

Join Date: Jun 2011
Location: Berkeley, CA USA
Posts: 128
Good Answers: 4
#8
In reply to #1

Re: KW-KVA-KVAR-PF

07/17/2011 1:13 AM

How does it work

The system has a current sensor and compares the angle of the current signal to the voltage signal to determine the KVA. Then they select the closest cap to cancel the PF of the load and place it in parallel with the load.

They cancel the reactive portion of the load. A pure inductor would have a +90° phase angle and a pure capacitor would have a -90° phase angle. That is the direction of the angle. The magnitude of the vector is determined by the size of the capacitor.

why?

This will only work with inductive loads, Don't bother with this type of device on your computer or electronic load as those look captive to the power system.

__________________
Working to end the use of carbon for energy
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#9
In reply to #8

Re: KW-KVA-KVAR-PF

07/17/2011 2:57 AM

Theoretically speaking, it would be possible to have excessive leading (capacitive) power factor that would benefit from power factor correction inductors. This is not particularly common, as far as I know.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User
Popular Science - Weaponology - New Member

Join Date: Jun 2011
Location: Berkeley, CA USA
Posts: 128
Good Answers: 4
#13
In reply to #9

Re: KW-KVA-KVAR-PF

07/17/2011 8:14 PM

Theoretically you are correct. Electronic loads use diodes to charge capacitors which is why they look some what like a captive load. These devices mostly cause 3rd harmonic distortion. So an inductor will not fix that. Now almost all new devices use what is called Power Factor Correction (PFC) that makes them look more like a resistive load on the power system.

__________________
Working to end the use of carbon for energy
Register to Reply
Guru

Join Date: Apr 2007
Location: Hyderabad, India
Posts: 596
Good Answers: 12
#2

Re: KW-KVA-KVAR-PF

07/16/2011 1:04 AM

APCPDCL changed KWH billing to KVAH billing since April 2011; hence it will be wise to maintain optimum PF instead of high PF;

__________________
Subramanyam
Register to Reply Score 1 for Good Answer
7
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: KW-KVA-KVAR-PF

07/16/2011 3:59 AM

kW is the power you actually need. You cannot reduce it can you ? What the power saver is doing is to reduce the unnecessary part of the load which is causing the cables to overheat, and, maybe, make the meter show more consumption (if you are being billed per kVA). The kVAR of the capacitors will oppose and maybe cancel the inductive kVAR inherent to the motor.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 7)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#6
In reply to #3

Re: KW-KVA-KVAR-PF

07/17/2011 12:33 AM

The best answer and also the best description I've ever seen.. May I use it please?

__________________
The square root of nothing is what you make it!
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #6

Re: KW-KVA-KVAR-PF

07/17/2011 1:09 AM

Thank you. Of course you are free to use it...i do believe i got this one from another thread long ago on CR4

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Commentator

Join Date: Jul 2008
Posts: 56
Good Answers: 1
#4

Re: KW-KVA-KVAR-PF

07/16/2011 2:05 PM

Thanks to every one...I hit the books and my doubt is clear...let me put this in this way...when combination of capacitors connected across the circuit it will affect PF,KVA,KVAR but not KW because (consider 1 figure) this is power triangle shows some active power(KW) consumption which is fixed irrespective of PF, KVA and KVAR.

now (Consider figure 2) in this figure due to capacitors combination PF will improves which further reduce KVA and KVAR for the same active power(KW). Amplitude of both KVA and KVAR reduce as pf reduce.

correct me if I am wrong.

Register to Reply
Guru
Australia - Member - New Member Engineering Fields - Mechanical Engineering - New Member

Join Date: Sep 2006
Location: NSW Australia
Posts: 1101
Good Answers: 23
#5
In reply to #4

Re: KW-KVA-KVAR-PF

07/16/2011 10:50 PM

The only possible saving of true power with PF correction is the reduced heating of supply cables which is the resistive part of the equation. This could be a problem if you had a PF of 0.5, but at 0.9 PF any further improvement becomes very expensive.

__________________
Dont get on to the roundabout if you dont know how to get off
Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#10

Re: KW-KVA-KVAR-PF

07/17/2011 6:57 AM

Most of the plug-in devices of this type are consumer frauds. Capacitors can be used to correct power factor and you will benefit by paying a lower penalty for a high power factor (usually levied on higher power 3 phase loads - never on residential - yet you describe a residential plug in unit).

You will not benefit by lower KW hours. The power company rewards those with a PF of unity with zero penalty because it reduces losses caused by the added lag/lead currents making wires hotter - they bear those losses - a reward you for alleviating them.

There are numerous people selling these fraud units, since they cost little to make = very profitable - all they need are fools to buy them. They are often sold by people on commission who try to cheat their friends for a fee - now you know.

__________________
Per Ardua Ad Astra
Register to Reply
Guru
United States - Member - Born, raised halfway 'round .....

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1269
Good Answers: 27
#11

Re: KW-KVA-KVAR-PF

07/17/2011 9:28 AM

For a regular residential consumer, installing power factor correcting device is not going to decrease their power consumption and lower their billing since the installed residential watt meters are designed to measure only the real power (in kw-hr) used. In this respect, in order for the utility companies not to be on the losing end due to reflected kvars on their power lines, they are strategically installing PF correcting devices on their poles.

In contrast, industries running big motors, it is mandatory or required to have their PF corrected else will be penalized and billed accordingly.

__________________
vsar
Register to Reply
Associate

Join Date: Jun 2008
Location: South Carolina, USA
Posts: 46
Good Answers: 2
#12

Re: KW-KVA-KVAR-PF

07/17/2011 3:52 PM

I agree with the comments made!

There are a lot of deceptive (Junk) devices that create mistrust for new emerging technologies that have proven to perform. However, most of the points made are valid for single-phase applications only. Because the homeowner often "Feels" the hurt of high utilities; while industry just factors this in as a production cost! Fraudulent companies prey on this need by homeowners to reduce utility costs…

However, IF you utilize 3-phase motors, and your process does not require full-speed operation to perform, reducing the motor cycles will dramatically reduce energy consumption and costs. VFD technology is nothing new, but an accurate method of optimizing these VFDs has always been lacking. New Smart Controller technologies that decrease, align, clean, and balance the power signal, actually reduce and improve kW, kVAR, kVA, and PF.

This is nothing more than "Cruise Control" technology for motors; allowing you to save on "Fuel" (Electricity) by taking advantage of these new "Demand-Response" technologies…

__________________
Knowledge Gained is in Direct Proportion to Equipment Ruined... or, K(+) = E(-)
Register to Reply
Register to Reply 13 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

aurizon (1); brich (1); garth (1); harjeetsinghengg (1); kramarat (1); kvsridhar (2); kvsubramanyam (1); regsoft (2); Tornado (1); vsar (1); Who Wants 2 Know??? (1)

Previous in Forum: Generation or Transmission   Next in Forum: If Nitrozen Filled In Power Transformer For More Than 6 Months During Stroge

Advertisement