VSD

07/18/2011 7:39 PM

In our plant we have two similar cranes, both use VSD's for the travel and both has 4 motors in parallel.The difference is one use V/Hz (altivar 71)and the other uses sensorless vector.(vacon).My question is, does V/Hz have an advantage over sensorless vector?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
2
Anonymous Poster #1
#1

Re: VSD

07/18/2011 10:05 PM

It is the otherway round. The V/f strategy is the basic one. (also called the scaler control)Then we have two types of vector controls

With sensors (encoders) The encoder based system optimizes by capturing the shaft speed and position feedback from an encoder. and

sensorless - try to optimise performance by mathematically determining the motor characteristics and operating parameters (electrical) and controlling VFD output accordingly

The vector controls are able to tune the output based on the exact motor characteristics which varies a bit (which may infact be significant) due to load and temperature variations. And this is not only to tune up the Voltage but the frequency too.

Register to Reply Good Answer (Score 2)
8
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: VSD

07/19/2011 2:11 AM

Not bad. But here's the way I like to teach it when I give seminars to non-engineers.

With a Scalar drive (V/Hz only), the VFD TELLS the motor what speed to run, but that's it. It has no idea if it is actually running that speed or not, it is making an ASSUMPTION. If something interferes with that, such as the issues raised above, it goes blissfully along with no idea that the motor is not performing as ASSumed. It's like telling your child what to do over the telephone without any clue if they are actually doing it.

A Vector drive on the other hand has some sort of feedback loop that looks at the motor's performance and allows the VFD to tweak it's output in order to maintain the desired effect, be it torque or speed (or both). So the VFD tells the motor what to do, then looks at the motor and if there is an error, makes adjustments to correct for it. So this is like telling your child what to do while you are standing there watching them and when they screw up, you correct them.

The FORM of that feedback loop is the difference between Sensorless and True Vector drives. True Vector drives use an absolute encoder feedback to judge motor performance, which is more accurate. Sensorless Vector drives have no external feedback device, but rely instead on a mathematical model of the motor by observing the current signature as the power is fed to it. Essentially if you can monitor, slice and dice the current waveforms with enough accuracy, you can essentially watch the rotor bars pass through the stator fields because of the effects they have on the way the stator coils react to them. So they use that to watch and keep track of the rotor position in lieu of an encoder (this is a HIGHLY non-technical explanation of a very complex process).

The only problem with Sensorless Vector is that unlike an encoder it is not absolute, which means that when the motor starts off after power is first applied, it does not know where the rotor is for a brief instant. Generally this isn't a problem, but on HOIST applications, it can be. If your hoist is holding a load with brakes and you release the brakes to lift or lower it, the motor torque MUST be there at that instant. In the fraction of a second a Sensorless Vector drive takes to determine and calculate the vector agnle, the load may run away and be impossible to stop again.

By the way, the Altivar 71 IS a Vector drive, it can be Sensorless Vector or True Vector with the addition of an Encoder Input card accessory. maybe someone programmed it to turn off the Sensorless Vector, I don't know, but that would be foolish given that it could be used and should be in that application.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 8)
Power-User

Join Date: Mar 2011
Location: oz
Posts: 252
Good Answers: 10
#3
In reply to #2

Re: VSD

07/19/2011 2:31 AM

This is what we are using, now.Is this because we have multiple motors.

Register to Reply Score 1 for Good Answer
2
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7
In reply to #3

Re: VSD

07/19/2011 12:44 PM

Ahhh, you left out the detail that you had one drive and multiple motors. Yes, in that case you cannot use vector control of any kind, your only choice is Scalar control (V/Hz).

If your other system is one drive for multiple motors and they have it in Vector mode, you are destined for problems. The modeling algorithm cannot adjust for all the variables that exist in the power circuit for anything other than one motor and may go completely bonkers on you one day. I've seen it happen may times. it can be commissioned this way and run for a while, but as soon as ANYTHING changes in the circuit, the VFD loses it.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Good Answer (Score 2)
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#5
In reply to #2

Re: VSD

07/19/2011 7:49 AM

Excellent answer! Some more of my motion control understanding gaps have been filled in. Thanks!

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#6
In reply to #2

Re: VSD

07/19/2011 8:44 AM

It is very well explained JRaef, the most VFD guru. I also would like to refer one previous thread where you also have great input on this topic in a reference link (http://www.eng-tips.com/faqs.cfm?fid=1062) of another forum, Eng-Tips.

http://cr4.globalspec.com/thread/52196

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
2
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#8
In reply to #2

Re: VSD

07/19/2011 1:00 PM

I think we're all agreed re the v/f and open loop vector ideas and explanations.

However, in my applications, closed loop vector drives use incremental encoder feedback, not absolute, when controlling asynchronous Induction Motors. When absolute is used, it's to gain positioning information rather than the motor control aspect.

Absolute feedback is needed when controlling synchronous motors in order to maintain field to pole position. There are, however, various means to still utilise incremental with updates (open or closed loop) to maintain good control.

In a hoist application, it's essential to develop torque before lifting the brake, this can be done sensorless (and commonly is) with the appropriate protection devices in place. It is easier and preferable to start at zero speed using feedback but many customers choose a lower cost solution. (but the question referred to travel drives on multi-motors)

__________________
Something new every day!
Register to Reply Good Answer (Score 2)
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#10
In reply to #2

Re: VSD

07/22/2011 4:33 PM

As my good friend Farrin Williams would SAY, amen and Great Answer not just good.,

__________________
To be or not to be........ok that's a trick question.
Register to Reply
2
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#4

Re: VSD

07/19/2011 5:20 AM

The simple explanations and analogies re v/f and open (or closed) loop vector are already posted.

In your application, the feedback for sensorless vector control is the summed current of all four motors, so if one was stalled or even missing, the drive makes its computations based on the total information regardless. So, if the information is rather meaningless, so is the drives computations and adjustments.

In short, when connecting more than one motor, it makes no sense to use vector mode as the mathematical model is being fed erroneous information. So, for example, if one motor load increases, the drive may up ALL voltages causing problems.

So, I recommend v/f control in this case and this offers the advantage of you setting the relationship (fixed) so you can make more sense of control information if needed.

(Normally, vector mode should be superior in most single motor applications particularly in response to low speed operation and / or significant and faster load changes.)

__________________
Something new every day!
Register to Reply Good Answer (Score 2)
Member

Join Date: Feb 2010
Posts: 9
#9

Re: VSD

07/19/2011 10:39 PM

Hi Eltech

I just wanted to say that with the Altivar 71 if you are using sinus filters due to length of cable runs you should use V/Hz and should not sensorless vector control as distortion of the current waveforms (caused by the filter) will lead to erratic control and the speed may appear to surge, hunt , fluctuate, oscillate once you try and travel above a certain speed (low speeds appear to control ok).

I experienced this problem on a shiploader long travelling system where we had 2 altivar 71 vsd's with sinus filters - 10 motors per vsd and tried to set them up in a master slave relationship then sensorless vector and eventually V/Hz before the speed control would work with the "surging/oscillating effect"

cheers

Matt

Register to Reply Score 1 for Good Answer
Register to Reply 10 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Poster (1); ellisamatt (1); eltech (1); JRaef (2); MalcolmK (2); Mikerho (1); msamad (1); Stedou73ish (1)