Correcting Lead Power Factor

07/19/2011 6:21 AM

Good day to all,

I would like to ask if anyone knows how to correct power factor leading loads?

Regards & Thanks

Versalite

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#1

Re: Correcting Lead Power Factor

07/19/2011 6:50 AM

put an inductor in series with the load .

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Register to Reply
2
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Correcting Lead Power Factor

07/19/2011 8:12 AM

Put an inductor in parallel with the load .

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 2)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Correcting Lead Power Factor

07/19/2011 1:54 PM

Do you have capacitors connected to your system?

Register to Reply
Member
Engineering Fields - Electrical Engineering - New Member

Join Date: May 2011
Posts: 9
#5
In reply to #3

Re: Correcting Lead Power Factor

07/19/2011 10:46 PM

yeah. they are automatic capacitor banks. is it worth to keep the pf at or very near unity? does these automatic capacitor bank have inductors inside them?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6
In reply to #5

Re: Correcting Lead Power Factor

07/20/2011 4:15 AM

If the power factor is leading, then there is too much capacitance in circuit.

Check the operation of the automatic functions against the Operation & Maintenance Manual and contact the manufacturer if a malfunction is suspected. With this unit working correctly, there would then be no need for an inductor in parallel with the load.

Power factor correction units rarely have inductors in them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Sep 2008
Posts: 706
Good Answers: 32
#9
In reply to #5

Re: Correcting Lead Power Factor

07/20/2011 4:32 PM

As PWSlack stated there is too much capacitance in the load if you have a leading PF. If your capacitor banks are operating properly they should only be adding enough capacitance to balance the lagging inductance of your system. Either they are adding too much because perhaps each bank has a certain rating so when your load's PF drops,the bank or banks that cut in to balance the lagging PF are over correcting. I doubt that they would over correct to an excessive amount so you're probably OK. Like the other contributor asked, just how high a leading PF are you getting?

__________________
Spinco
Register to Reply
Member
Engineering Fields - Electrical Engineering - New Member

Join Date: May 2011
Posts: 9
#13
In reply to #9

Re: Correcting Lead Power Factor

07/25/2011 6:22 AM

The power supply circuit consists of server racks (switches) ONLY, which I think induces leading power factor and not lagging power factor as my environment is a Tier3 data center. Therefore, I even suspect that the automatic capacitor bank is not even working or supplying reactive power! Is there anyone who can confirm my suspicion?

If my suspicion is true, how can I improve the power factor in the datacenter? I have learned lagging pf improvement but NEVER learned about leading power factor improvement

Help pls, thanks to those who replied and those going to reply (in advance)

Regards,

Versalite

Register to Reply
2
Guru
Canada - Member - Specialized in power electronics

Join Date: Feb 2008
Location: Montreal, Canada.
Posts: 1372
Good Answers: 80
#4

Re: Correcting Lead Power Factor

07/19/2011 10:33 PM

Depending on the load and the plant characteristics, adding an inductor may lead to dangerous resonance.

An inductor in series would "boost" the voltage at the load while an inductance in parallel would boost the voltage for the whole plant. Either might cause problems at resonance.

Basically, you need to contact a competent engineer to evaluate the specifics of your application and recommend a safe solution.

N.B. If the load is small (<10%) with respect to the plant feeder capacity, you might not need to worry about it since it will simply help the plant's usual lagging power factor.

__________________
Experienced is earned, common sense is taught, both are rare essentials of life.
Register to Reply Good Answer (Score 2)
Guru

Join Date: Sep 2008
Posts: 706
Good Answers: 32
#7

Re: Correcting Lead Power Factor

07/20/2011 1:23 PM

Generally speaking if you have any induction motors that you are operating elsewhere, run some off this circuit since induction motors operate with lagging power factors this will help correct your leading power factor. Leading power factors are unusual since most plants have numerous induction motors operating. Just type of plant are you operating or what is the main part of your load comprised of? Is it mostly lighting or computers or what?

__________________
Spinco
Register to Reply
Member
Engineering Fields - Electrical Engineering - New Member

Join Date: May 2011
Posts: 9
#10
In reply to #7

Re: Correcting Lead Power Factor

07/20/2011 10:27 PM

data center (tier3) with about 200-250 computers. standby generator. office lightings.

basically data center plus office stuff.

anyway, thanks to all the guys for sharing your experience and expertise. really appreciate it!

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 17
#11
In reply to #10

Re: Correcting Lead Power Factor

07/21/2011 5:55 AM

Certainly the Auto power factor correction is not working properly. The capacitors used are of not desirable value. Please get calibrated again according to your load.

A K Billore

Register to Reply
Member
Engineering Fields - Electrical Engineering - New Member

Join Date: May 2011
Posts: 9
#14
In reply to #11

Re: Correcting Lead Power Factor

07/25/2011 11:25 PM

Hi A K Billore,

I suspect that the pf correction design is flawed as it is more suited for industries with induction motors running, which supplying VARs to correct the pf.

However, in my environment, the circuit provides power for mostly servers (data center) and computers, which I believe their switching behaviour causes leading pf. Thus, how can I improve this leading pf in my datacenter?

Regards,

Versalite

Register to Reply
Active Contributor

Join Date: Jun 2011
Posts: 17
#15
In reply to #14

Re: Correcting Lead Power Factor

07/26/2011 12:08 AM

Hi Versalite,

Certainly the auto P.F. Correction is not suiting to your datacentre load.In P.F. correction system there is no reactive component, only cpacitors are added or redused accordind to requirement.Also P.F.near to unity is never desirable. Hence it is advisible to check the P.F. without correction system. After that correction VAR may be calculated if at all required. Existing system of correction may also be verified by manipulation of different arrays by competent person.

A K Billore

Register to Reply Score 1 for Good Answer
Member
Engineering Fields - Electrical Engineering - New Member

Join Date: May 2011
Posts: 9
#16
In reply to #15

Re: Correcting Lead Power Factor

07/26/2011 2:51 AM

Hi A K Billore,

Yes I agree with you that checking of the p.f. (not from the pf correction device) is needed.

However, lets assume that I've checked the pf without the correction system, and the p.f is leading in nature, how can I correct it successfully?

Thank you for your help thus far!

Regards,

Versalite

Register to Reply Score 1 for Off Topic
Active Contributor

Join Date: Jun 2011
Posts: 17
#17
In reply to #16

Re: Correcting Lead Power Factor

07/27/2011 4:44 AM

Hi Versalite,

This is very interesting idea assuming PF leading without pf correction system with load of 200 computers,lighting etc.But allredy it is known that adding a reactive component will be a dangerous proposition. Hence if at all there is actual leading pf without correction device, its account will have to be taken and reasons sought by trial and error .

A K Billore

Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#8

Re: Correcting Lead Power Factor

07/20/2011 3:34 PM

You have a leading PF. Check with the utility if you are being penalized for this. It is likely that you are not. Utilities like free KVARS. If not, Determine what the PF is. If its just a little leading its not a problem. Do what PW is saying. The unit should correct this problem.

Register to Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#12

Re: Correcting Lead Power Factor

07/21/2011 8:42 AM

Generally leading power factor is caused due to over compensation of inductive loads. It is higly reccomended that for selection of correct sizes of capacitor banks a thorough study of electrical load characteristic is required by deployment of proper electrical instruments, collecing and analysing the data. Power factor improvement upto 0.98 lagging is most suitable. The more the number of stage facility in PFC( Power Factor Controller) relay contain, fine control of power factor is possible provided, adequate protection is adopted for frequent ON/OFF of capacitor banks.

Leading power factor is also very harmful to various electrical equipments like transformers,generators etc., even it may damage the electrical equipments for prolong use. Therefore, please study your electrical power distribution networks, actual requirement of capacitor bank ratings, number of stage contol requires, may fix up power factor improvement upto 0.98 lagging to avoid this type of undesirable situations.

Manindra

__________________
Manindra
Register to Reply
Register to Reply 17 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

A K BILLORE (3); bravo88 (1); manindra (1); marcot (1); PWSlack (2); Spinco (2); Versalite (5); wareagle (2)

Previous in Forum: ABB RELL 511 Vers 2.5   Next in Forum: rmu

Advertisement