20 Amps Through 14 Gauge Romex Wire.

07/22/2011 11:02 PM

is it safe to draw a 20 amp. current through 14 gauge romex?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#1

Re: 20 amps through 14 gauge romex wire.

07/22/2011 11:45 PM

That information can be found on the Internet, like here. And, being your asking a question like this, it seems like your already over your skill limitations. You can cause fires and possibly kill someone by lack of knowledge and skills. A home's electrical wiring is not the proper place to do a smoke test on a wire's carrying capabilities.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#4
In reply to #1

Re: 20 amps through 14 gauge romex wire.

07/23/2011 12:24 AM

i appreciate your imput, but i was hoping for an answer, not a sermon.

Register to Reply Score 2 for Off Topic
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#9
In reply to #4

Re: 20 amps through 14 gauge romex wire.

07/23/2011 10:19 AM

Sorry, but a sermon is what you deserve. I'm just hoping that the sermons you get here don't turn into a eulogy for you and your family. Replacing a 15 ampere circuit breaker with a 20 ampere breaker is a recipe for disaster.

Depending on the wiring conditions 17 amperes is the nominal maximum safe rating for new 14 gauge wire. (Don't get your hopes up at the word "nominal", any change from the code rating lowers the safe operating current.) Your home was wired by somebody that just barely met wiring code for a 15 ampere breaker.

I know that it's hot today and that you'd love to add an air conditioner to your home. I'm sorry that you cannot just plug the air conditioner you bought into the existing wiring in your house. DO NOT ALTER THE WIRING OF YOUR HOME.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#31
In reply to #9

Re: 20 amps through 14 gauge romex wire.

07/24/2011 4:36 AM

the thing is that i've never had this problem until recently. i was hoping that someone would blame it on the push-in plugs on the back of my outlets. i've seen 12 gauge wire pop out of these things. talk about a fire hazzard!. how do they get this junk certified? thesr's not even an option to hook them up with the screws. hell, they don't even have screws on them. don't these type of things have to be approve by the underwriter's labratory?

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#36
In reply to #31

Re: 20 amps through 14 gauge romex wire.

07/24/2011 8:21 AM

There was a time that knife edge only outlets were legal in the US. I don't believe they're legal now. I'm not going to guess or slight who or what group insisted that these outlets should be legal. Your house wiring was apparently assembled during this era. Despite my earlier "holier than though" attitude about doing your own house wiring, I do recommend that you replace all of these knife edge outlets with screw terminal outlets. Don't forget the normal safety protocol of turning OFF the power at the breaker before removing the cover plate and test before you touch.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#38
In reply to #31

Re: 20 amps through 14 gauge romex wire.

07/24/2011 9:47 AM

Buy a handful of outlets, with screws they're cheap.

you could temp a solution, buy some #12, add a 20 amp breaker hook up a temporary outlet until the electrician can get to you

it won't be legal, but it will be safe...

if the ac has a regular end on it, 15amp circuit. there could be exceptions

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#47
In reply to #9

Re: 20 amps through 14 gauge romex wire.

07/25/2011 10:50 AM

2011 NEC still rates

AWG 14 at 15 Amps

AWG 12 at 20 Amps

AWG 10 at 30 Amps

Not alot has changes thrugh the years.

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Participant

Join Date: Dec 2012
Posts: 3
#52
In reply to #9

Re: 20 amps through 14 gauge romex wire.

12/29/2012 5:54 PM

a good rule of thumb is that a 100 watt bulb pulls .84 amps or use i =e divided by r which is ohms law----if it kicks the ---wire too small --heat on small wire transfers back to breaker and it kicks out ---bigger wire is the answer.

Register to Reply Score 1 for Off Topic
Power-User
New Zealand - Member - Kiwi

Join Date: Oct 2007
Location: Christchurch, New Zealand
Posts: 328
Good Answers: 29
#13
In reply to #4

Re: 20 amps through 14 gauge romex wire.

07/23/2011 6:13 PM

"i appreciate your imput, but i was hoping for an answer, not a sermon."

If you don't want the sermon, stay out of the church.

__________________
paulusgnome
Register to Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#26
In reply to #13

Re: 20 amps through 14 gauge romex wire.

07/24/2011 3:56 AM

i'm old enough to remember when engineering did'nt seem like a liberal art. these days everyone wants to give me personally advise from, how i should raise kids. to telling me to stop smoking. if i need preaching to, i'll go to church , and if i'm concerned about my heath,i 'll see my doctor. otherwise, i'll stick with common sense.

Register to Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#32
In reply to #4

Re: 20 amps through 14 gauge romex wire.

07/24/2011 5:37 AM

you want an answer.. here it is!

Get a certified electrician in to solve your problem, you will sleep better knowing that your house is safe, your insurance company will pay up if there is fire and your family is safe.

It wasn't a sermon you got is was sound advice.....

People here in CR4 will advise you, but I to am of the opinion you are in WAY over your head.. therefore any advice will not only confuse you, but not be fully understood as you don't have the right skills & education to carry out the advice.

Please remember you came here asking the question, it doesn't mean you are going like the reply, especially if it doesn't fit in with your way of thinking or the reply you were hoping for!

Be smart, be safe!

__________________
The square root of nothing is what you make it!
Register to Reply
Participant

Join Date: Dec 2012
Posts: 3
#54
In reply to #4

Re: 20 amps through 14 gauge romex wire.

12/29/2012 5:58 PM

get larger wire --probably # 10

Register to Reply Score 1 for Off Topic
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: 20 amps through 14 gauge romex wire.

07/22/2011 11:50 PM

How many inches long is the wire?

Register to Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#3
In reply to #2

Re: 20 amps through 14 gauge romex wire.

07/23/2011 12:03 AM

it's about 40' long and has 8 outlets

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#10
In reply to #2

Re: 20 amps through 14 gauge romex wire.

07/23/2011 2:34 PM

I was going to ask the same question, but I didn't want to get the OP hopes up

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5

Re: 20 amps through 14 gauge romex wire.

07/23/2011 2:01 AM

In the U.S. NEC (National Electrical Code), I think it is Article 310 that gives wire ampacities under various conditions (number of wires in conduit/cable; location, such as in free air or buried; ambient temperature; type of insulation; etc.) Although the theoretical ampacity may be higher than 15A, I think there is a footnote that limits the overcurrent protection to 15A for general wiring.

This is off the top of my head, so be sure to consult all relevant tables and notes.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#6
In reply to #5

Re: 20 amps through 14 gauge romex wire.

07/23/2011 3:24 AM

thanks for the info. i'm only running a 10,000 btu ac, a 250 watt bulb and a computer on this circuit. i was kicking the 15 amp breaker when i turned on the ac. i bought a new 15 amp breaker and it still kicks off. all the outlets are type where the wires push into the back. do you think i should change the outlets? i moved the line over to a 20 amp breaker, but i'm not sleeping very well.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#7
In reply to #6

Re: 20 amps through 14 gauge romex wire.

07/23/2011 4:19 AM

Do you have a wattage or amperage rating for the A/C unit? (This is the largest load on the described circuit.) It is a motor, and its starting current is the likely cause of tripping the breaker. If possible, it should probably have its own dedicated circuit (which might even be required, but I'm not sure.) If you have a clip-around ammeter, you can check what the total circuit draws when all items are running.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#15
In reply to #7

Re: 20 amps through 14 gauge romex wire.

07/23/2011 10:45 PM

no, the wattage is listed on the inside of the unit. it's an efficent md.

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#17
In reply to #15

Re: 20 amps through 14 gauge romex wire.

07/23/2011 10:47 PM

Oh I'd just love to hear what the wattage claims. Oh, please do tell us.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
2
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#11
In reply to #6

Re: 20 amps through 14 gauge romex wire.

07/23/2011 3:25 PM

I gave my sermon. Now without having the Data Plate Info and using approx. averages, here some math, anyone feel free to correct me.

3,400btu= approx 1kw, 10000btu/3400btu= 2.94kw of power

2.941kW x 1000watts= 2,941watts, 2,941w/117volts(avg)= 25.14 amps!!

25.14amps does not factor in, in-rush current, which does not matter, because you have exceeded the max.allowance for 14ga.wire, 15amp breaker and I'm sure everybody here would agree, you also exceeded the 20amp breaker.

So, the short story is, you have created a brew for Disaster!! And I,too, would not sleep well at night or any other time with what you are doing, Sorry. DJ

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply Good Answer (Score 2)
2
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#12
In reply to #11

Re: 20 amps through 14 gauge romex wire.

07/23/2011 4:32 PM

I need to add a foot note to my post #11, Those calculations do not include 250w light nor your computer. As, Not So Smart stated, your AC unit should be on a dedicated circuit.And you should not run your computer on the same circuit.

Your AC unit needs a minimum 30amp. breaker and minimum 10/2 wire to be safe and able to sleep at night. DJ

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#27
In reply to #12

Re: 20 amps through 14 gauge romex wire.

07/24/2011 4:09 AM

i agree with you.and have been trying to have a licenced eletiction to come out to do the work. it's been 105 degrees here latelyt i can't get an electrition out here for two weeks. i've been baby sitting my ac unit an my wiring. it get's turned off if i'm in bed or out. it's just a a stop gap measure for now.

Register to Reply
Commentator

Join Date: Jun 2011
Posts: 77
Good Answers: 8
#41
In reply to #12

Re: 20 amps through 14 gauge romex wire.

07/24/2011 5:18 PM

DJ95401, you would be right in the money if it was a heater. However, a relatively new 10,000 BTU window AC unit takes about 1000 to 1200 watts, or about 8 to 10 amps. Throw in the light and the PC and you are about 14 to 16 amps. Keep in mind that does not include the unit start up.

Soooo..... OP: take everything else off this circuit including the light (unscrew it or turn it off), put the PC on different circuit and try running the unit to see if it still trips. If not, you have a work around until a sparky comes over. If it does trip try to find a 20 A circuit you can use until you get it fixed. If all the above fails stick your bare feet in some cold water.

Register to Reply Score 1 for Good Answer
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#42
In reply to #41

Re: 20 amps through 14 gauge romex wire.

07/24/2011 6:12 PM

Hi Jonathan, I don't mind being corrected, that's why I said, feel free to correct me. Those numbers I used were off the top of my head from when I was doing HVAC work some 30 years ago. I still think there's more to this story than what was being told. Like most questions we see here on CR4, a lot of important info. is usually left out of the question. So with out the data plate specs. I hedged on the safe side. Which still doesn't explain why his unit still trips a 20amp breaker if it's only drawing approx. 10amps. If he had supplied the data plate info, my numbers would have probably been different. I just hope the OP realizes, what he is doing or trying to do, is extremely dangerous. Cheers, DJ

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#43
In reply to #42

Re: 20 amps through 14 gauge romex wire.

07/24/2011 6:54 PM

An amp meter with peak starting amperage and voltage would tell the true story. But most people don't have access to these or know how to use them. A hard start kit might be just what the doctor ordered. With light information it's hard to give a definitive answer to a lot of questions.

Register to Reply Score 1 for Good Answer
Guru
Canada - Member - New Member Hobbies - Musician - New Member

Join Date: Dec 2006
Location: Western Canada
Posts: 1863
Good Answers: 39
#48
In reply to #42

Re: 20 amps through 14 gauge romex wire.

07/25/2011 1:58 PM

I may be able to shed some light on why this circuit trips out despite the spec suggesting differeently. If the branch circuit wiring is #14 AWG there is more voltage drop associated with the start surge compared to using #12 Ga. This voltage drop causes the inductive load <motor> to pull more current than normal. This will cause the breaker to trip. If it is a thermal breaker sitting in a hot environment < heat wave> it will trip even sooner than rated .

__________________
Elnav
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#56
In reply to #12

Re: 20 amps through 14 gauge romex wire.

01/02/2013 11:18 AM

Actually it should be a 10/3 he needs to have the ground as well.

__________________
To be or not to be........ok that's a trick question.
Register to Reply Score 1 for Off Topic
Participant

Join Date: Mar 2014
Posts: 1
#57
In reply to #56

Re: 20 amps through 14 gauge romex wire.

03/11/2014 9:58 PM

10/2 has 2 wires and a ground, 10/3 has 3 wires and a ground and is used for 3 phase circuits, usually commercial.

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#58
In reply to #57

Re: 20 amps through 14 gauge romex wire.

03/12/2014 1:40 AM

Welcome to CR4 John,

10/3 is also used with residential clothes dryers requiring 240 volt 'single phase' 4 prong plugs and receptacles in the U.S.

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#16
In reply to #11

Re: 20 amps through 14 gauge romex wire.

07/23/2011 10:47 PM

thanks for the info. you convienced me. i was trying to take the easy way out. thanks again

Register to Reply Score 1 for Good Answer
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#22
In reply to #16

Re: 20 amps through 14 gauge romex wire.

07/24/2011 12:27 AM

I'm just glad your still here and able to reply and that's a good thing! Best Wishes, DJ

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply Off Topic (Score 5)
2
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#25
In reply to #11

Re: 20 amps through 14 gauge romex wire.

07/24/2011 1:39 AM

Well: it's a heat pump - not a heater

Might want to rework that

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply Good Answer (Score 2)
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#33
In reply to #11

Re: 20 amps through 14 gauge romex wire.

07/24/2011 5:40 AM

why are you saying "sorry"?

GA!

__________________
The square root of nothing is what you make it!
Register to Reply Off Topic (Score 4)
Guru
Safety - Hazmat - New Member Safety - ESD - New Member Engineering Fields - Transportation Engineering - New Member Popular Science - Evolution - New Member Technical Fields - Procurement - New Member Hobbies - Target Shooting - New Member Popular Science - Cosmology - New Member Engineering Fields - Architectural Engineering - New Member Technical Fields - Marketing/Advertising - New Member Engineering Fields - Food Process Engineering - New Member

Join Date: Dec 2005
Location: Mariposa Ca
Posts: 5800
Good Answers: 114
#19
In reply to #6

Re: 20 amps through 14 gauge romex wire.

07/23/2011 11:34 PM

What does the name plate on the ac unit say?

assuming the stuff I found that indicates a draw of around 10 amp is true

I've run into problems on more than one occasion with wires pushed into the quick connection outlets

most notably a house where the lights in 1/2 [one phase] would dim everytime the refrigerator would run

I always use the screw terminals

Turn off the breaker

rewire every outlet on the circuit in question

find a different place to plug in the light 250w = 2amp & computer = 1.5 amp

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#20
In reply to #19

Re: 20 amps through 14 gauge romex wire.

07/24/2011 12:24 AM

I would like to find a 10,000Btu AC unit that only drew 10amps on 120volts! I despise those quick connects, the only thing they good for, is when your doing piece work the construction trade. DJ

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#23
In reply to #19

Re: 20 amps through 14 gauge romex wire.

07/24/2011 12:27 AM

10 amp? Where did you get 10 amp from. The 10,000 BTU (per hour) has already been calculated to be almost 3kW if 100% efficiency is achieved. This means a 25+ ampere draw with single phase 117 VAC power.

Wait a minute, I forgot that there's the fact that the air exchange acting as a heat sink is another energy source in this operation. This relationship is handled by the SEER, EER or COP rating of the air conditioner that needs to be known to convert the BTU to electric watts drawn. So this unit might only require the 10 amperes you cite. The air conditioner in question might not be as efficient as the one you found and draw 14 amperes while running and 19 to start.

It still is a good idea to separate a computer from a large current drawing motor like an air conditioner. It is still a horrible idea to change a 15 ampere breaker to a 20 ampere breaker without upgrading the wires. Now a slow trip 15 ampere breaker might accept the higher but brief starting cycle current. What would quickly settle all concerns is a clamp on ammeter or the air conditioner's electric wattage rating. The quick connection knife edges may be a contributing factor, too.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: in optimism
Posts: 4050
Good Answers: 130
#30
In reply to #23

Re: 20 amps through 14 gauge romex wire.

07/24/2011 4:31 AM

Ah - sorry Red, just got down to your post. Seems I sort of 'plagerised' - but nice to see we got to the same place. Maybe makes us a 'gang'

__________________
There is no sin except stupidity. (Oscar Wilde, Irish dramatist, novelist, & poet (1854 - 1900))
Register to Reply
Guru

Join Date: Dec 2008
Location: nj,usa
Posts: 1252
Good Answers: 33
#8

Re: 20 amps through 14 gauge romex wire.

07/23/2011 4:26 AM

If you're running an AC unit you should be using 12 awg or better. 14 awg is not sufficient for a 20 A breaker. Also a dedicated circuit is recommended for your AC unit and NEVER run AC on the same circuit as your computer.

__________________
CARPE CRUSTULORUM!
Register to Reply Score 1 for Good Answer
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#14

Re: 20 Amps Through 14 Gauge Romex Wire.

07/23/2011 8:08 PM

I'd get a long screw and screw the breaker to it's "ON" position, that way it can't cause nuisance trips. While you're at it you might rewire the house with aluminum wiring.

Register to Reply
Power-User

Join Date: Dec 2007
Posts: 136
Good Answers: 1
#18
In reply to #14

Re: 20 Amps Through 14 Gauge Romex Wire.

07/23/2011 11:16 PM

Do you have a Fire Extinguisher ??? It could start when you are sleeping. wire gets hotter and hotter and by that time you and your loved ones could be all asleep from the nice cool air, and never wake up again.

I would NEVER pull the same amount of amp as listed on the breaker, some times the breakers Don't work either.

Register to Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#28
In reply to #14

Re: 20 Amps Through 14 Gauge Romex Wire.

07/24/2011 4:17 AM

fredski, when did you become a smart ass. i've always liked your answers. short, sweet and to the point.

Register to Reply
Guru

Join Date: Feb 2011
Posts: 7025
Good Answers: 207
#35
In reply to #28

Re: 20 Amps Through 14 Gauge Romex Wire.

07/24/2011 8:17 AM

You can't be serious all the time!

Register to Reply
Guru

Join Date: Jun 2010
Posts: 989
Good Answers: 14
#21

Re: 20 Amps Through 14 Gauge Romex Wire.

07/24/2011 12:26 AM

What on earth is the 250 watt bulb for?

Register to Reply
Guru
United States - Member - Hobbies - Fishing - New Member Hobbies - Target Shooting - New Member Hobbies - RC Aircraft - New Member Engineering Fields - Aerospace Engineering - New Member

Join Date: May 2009
Location: Saint Helens, Oregon
Posts: 2216
Good Answers: 70
#24
In reply to #21

Re: 20 Amps Through 14 Gauge Romex Wire.

07/24/2011 12:31 AM

Should we shed some light on the subject for you?

__________________
Confucius once said, “ Ability will never catch up with the demand for it".
Register to Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#29
In reply to #21

Re: 20 Amps Through 14 Gauge Romex Wire.

07/24/2011 4:22 AM

an out door sodium light.

Register to Reply
Guru
Hobbies - HAM Radio - New Member United Kingdom - Big Ben - New Member Fans of Old Computers - Altair 8800 - New Member Canada - Member - New Member

Join Date: Jun 2006
Location: Toronto
Posts: 3968
Good Answers: 120
#34
In reply to #29

Re: 20 Amps Through 14 Gauge Romex Wire.

07/24/2011 7:01 AM

the unit is rated to move 10,000 BTU per hour. As a heat pump between 105F and 70F, if it has performance rating of 3:1 it will use 3333 BTU worth of electric power and thus the claims of 25-30 amps might be excessive. An electric resistance heater at 10,000 BTU/Hr is going to use 2.93 KWH each hour it runs at 120 VAC = 24.16 Amps.

That plus the 250W light and your computer would make it close to 30 Amps, but it is not a heater....

An air conditioner rated at 3 would use 1/3rd that amount ~8 Amps.

http://en.wikipedia.org/wiki/Coefficient_of_performance

__________________
Per Ardua Ad Astra
Register to Reply
Power-User

Join Date: Dec 2010
Posts: 166
Good Answers: 4
#37

Re: 20 Amps Through 14 Gauge Romex Wire.

07/24/2011 9:40 AM

No.

Register to Reply
3
Guru
Engineering Fields - Electrical Engineering - Analog and Digital Circuit Design Engineering Fields - Electromechanical Engineering - Transformers, Motors & Drives, EM Launchers Engineering Fields - Engineering Physics - Applied Electrical, Optical, and Mechanical

Join Date: Jan 2008
Location: NY
Posts: 1207
Good Answers: 119
#39

Re: 20 Amps Through 14 Gauge Romex Wire.

07/24/2011 12:10 PM

The simple answer is "NO, it is not safe to run 20A through 14 gauge romex".

One typical 10000 BTU A/C available at the big orange box store is rated EER=10.8, 1800W, 15A, so let's use these numbers.

14 gauge wire should only be used with 15A (or lower) circuit breakers. That's 1800 Watts MAX. If you attempt to run this A/C unit, plus a 250 Watt lamp, plus a 150 Watt PC, you can see why the >18A load is tripping the 15A breaker.

Realistically, you don't want to load a 15A circuit more than ~80% of that rating. A conservative 12A maximum load is a little under 1500W. That's not even good enough for this A/C unit alone. I would keep the existing 15A wiring and 15A breaker for the lighting, computer, and other small appliances where the total circuit load never exceeded 1500W.

12 gauge wire should be used with a 20A circuit breaker. That would provide 2400 Watts max or the conservative 80% rating of 1920 Watts. I'd run a dedicated 12 gauge wire and 20A breaker for the A/C unit alone. I'd also use quality electrical outlets and would only wire to the screw terminals. With a dedicated 20A circuit, I'd sleep very comfortably knowing that my wiring was safe.

Disclaimer: I'm not a licensed electrician...

but I have updated my 100+ year old home using 12 gauge wire and 20A breakers for ALL the wall outlets. I did use some of the lighter 14 gauge wire and 15A breakers, but only for dedicated lighting and switch plate circuits where the maximum normal current doesn't exceed 10A.

My personal preference is to NEVER use the push-fit ports on electrical outlets. IMO the small contact area heating at the higher currents is not acceptable, even though UL and NEC may approve this application. In my home, I HAVE used approved push-fit connectors that are included in certain lighting fixtures. My reason for accepting them here is that the lamps are typically fixed loads UNDER 1A.

Be safe and Good Luck!

Register to Reply Good Answer (Score 3)
Commentator

Join Date: Dec 2007
Location: Pekin, IL USA
Posts: 86
Good Answers: 5
#40

Re: 20 Amps Through 14 Gauge Romex Wire.

07/24/2011 1:41 PM

First; move your computer and the light bulb off the circuit. Next figure what the air-conditioner will draw alone. A 10000 BTU air conditioner can draw as much as 5000 watts on start up and require 1500 watts to run. This depends on the seer rating. Divide the BTU/efficiency rating=watts/120v=amps. Over 15? Run a 12GA wire for the air. The answer to your question is a simple one. No.

__________________
A good deed not praised holds behind it a thousand deeds yet undone.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#44

Re: 20 Amps Through 14 Gauge Romex Wire.

07/25/2011 8:29 AM

Not in a zone 0 potentially explosive atmosphere.....

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Score 1 for Off Topic
Power-User

Join Date: Dec 2007
Posts: 136
Good Answers: 1
#45
In reply to #44

Re: 20 Amps Through 14 Gauge Romex Wire.

07/25/2011 10:39 AM

Time to Remove this post, getting too stupid.

Register to Reply
Commentator

Join Date: Dec 2007
Location: Pekin, IL USA
Posts: 86
Good Answers: 5
#50
In reply to #44

Re: 20 Amps Through 14 Gauge Romex Wire.

07/25/2011 4:39 PM

No. In zone 0 you can use 44 gauge wire to conduct 17.4 kv with a power factor of 10 or less. In zone 1 through 10 you can use only Arizona copper wire while in all other zones ROW wire is accepted if it is sized according to the AWG specifications. Metric wire requires metric voltages, ISO watts, and metric amps. Several third world countries are going to the use of Tn wire to carry air-conditioner metric tonnage amps. This is particularly true in the Oriental island of Takawan. America is rushing to join the list of third world countries while the rest of the world stands with bated breath. 535 people in Washington, some trusted, most not, play cribbage and determine the fate of the voltage flowing through auxiliary lines ranging from 32 CWG (China wire gauge) to 85 CWG. Most haul the cold air in refrigirated semitrucks limited to 45 tonne each. Ice road truckers I suspose.

__________________
A good deed not praised holds behind it a thousand deeds yet undone.
Register to Reply Off Topic (Score 4)
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#46

Re: 20 Amps Through 14 Gauge Romex Wire.

07/25/2011 10:39 AM

NO!

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Power-User

Join Date: Dec 2009
Location: Hannover, Germany and Jacksonville, Florida
Posts: 141
Good Answers: 8
#49

Re: 20 Amps Through 14 Gauge Romex Wire.

07/25/2011 2:33 PM

Your a comedian... right?

__________________
Johannes
Register to Reply Off Topic (Score 5)
Participant

Join Date: Jul 2011
Location: Home of the Mile High City
Posts: 3
#51

Re: 20 Amps Through 14 Gauge Romex Wire.

07/27/2011 9:08 PM

I hope you are kidding, if your not, you'd be a fool to try it.

__________________
Take a Deep Breath and.....Jump In!
Register to Reply
Participant

Join Date: Dec 2012
Posts: 3
#53

Re: 20 Amps Through 14 Gauge Romex Wire.

12/29/2012 5:55 PM

NO

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - Ever Changing United States - Member - From the Redwoods to the Valleys Engineering Fields - Control Engineering - Building blocks or writing code - to keep you comfortable

Join Date: Apr 2008
Location: 38th Parallel
Posts: 750
Good Answers: 19
#55

Re: 20 Amps Through 14 Gauge Romex Wire.

01/02/2013 11:12 AM

NO

__________________
To be or not to be........ok that's a trick question.
Register to Reply
Register to Reply 58 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

129CBRider (1); 34point5 (2); aurizon (1); brich (2); conntaxman (2); curtis savoy (3); dj95401 (9); elnav (1); Fredski (3); Garthh (2); Gazu (1); jcmcdonell (1); jlstitt (10); Johannescnc (1); John1123 (1); JonathanG (1); lyn (1); mjb1962853 (1); not so smart (1); Paulusgnome (1); PWSlack (1); Randouli (2); redfred (4); Stedou73ish (4); Tornado (2)