MGE UPS 60KVA Galaxy 5000

07/26/2011 3:49 AM

I have a UPS (MGE Galaxy 5000, 60kva). A month back, its PFC board, charger fuse and AC Normal fuses got blown after some mains power transients....and of course showing the respective alarms. I ordered for spares and have fixed them now. However, two of the AC Normal Fuses blow again while am trying to start up the unit i.e. immediately I close static by-pass breaker (Q4S). When I follow the circuit, the only thing between the Normal AC input fuse & the input breakers (Q1/Q4S) is the input filter board. Kindly assist me to troubleshoot the cause of this fault (blowing the ac normal input fuses)??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: MGE UPS 60KVA Galaxy 5000

07/26/2011 9:56 AM

What are the ohms readings downstream of the fuses?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Member

Join Date: Dec 2009
Posts: 6
#2
In reply to #1

Re: MGE UPS 60KVA Galaxy 5000

07/27/2011 2:52 AM

CURRENT IS 125AMPS

VOLTAGE IS 690V

AC IR IS 200KA

CLASS IS AR

NOT ABLE TO FIND THE OHMS AT THE MOMEMENT SIR. PLEASE ADVISE ON THE WAY FORWARD SINCE MY SYSTEMS ARE DOWN

THANX

Register to Reply
Participant

Join Date: Jan 2013
Posts: 1
#3

Re: MGE UPS 60KVA Galaxy 5000

01/04/2013 4:56 AM

The last time I had exactly the same scenario on my MGE Galaxy 5000 60kva....I found that one of "thyristors - for the yellow/middle phase" located behind the "normal AC main power supply board - CSNEN board" had failed. Immediately I replaced that with the "opened" input fuses....UPS worked perfect.