Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Construction Engineering - New Member India - Member - New Member Engineering Fields - Nanoengineering - New Member Safety - Hazmat - New Member

Join Date: Mar 2006
Location: Chennai, India
Posts: 312
Good Answers: 3

Concrete Honeycombing

07/27/2011 10:48 AM

I observed honeycombing in concrete, formed due to improper consolidation of concrete. This could have happened due to inadequate supervision during construction. To break and redo whole concreting is too expensive.

Kindly suggest cheaper solutions (other than reconstructing).

__________________
nvmani
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#1

Re: Honeycombing

07/27/2011 10:59 AM

Take your pick. I'd tear it all out and re-do it.

Troubleshooting Surface Imperfections

CR4 Admin: Removed broken links

Register to Reply
Guru
United States - Member - Member Engineering Fields - Electrical Engineering - Electrical Construction

Join Date: Apr 2010
Location: Mid Western USA - The Corn Belt
Posts: 1439
Good Answers: 58
#2

Re: Honeycombing

07/27/2011 10:59 AM

Based on your lack of details, we have no way of knowing if this is a backyard patio, a truck dock ramp, an aircraft runway, a warehouse slab, an eight lane highway, or a pedestrian walkway.

More details please.

__________________
The first 5 days after a weekend are always the hardest................................
Register to Reply
Power-User
Engineering Fields - Electrical Engineering - New Member Engineering Fields - Power Engineering - New Member Technical Fields - Technical Writing - New Member Engineering Fields - Construction Engineering - New Member India - Member - New Member Engineering Fields - Nanoengineering - New Member Safety - Hazmat - New Member

Join Date: Mar 2006
Location: Chennai, India
Posts: 312
Good Answers: 3
#5
In reply to #2

Re: Honeycombing

07/28/2011 6:37 AM

The construction pertains to RCC roof slab,constructed over 1st floor of my residence,for approximately 1000 sq.ft.area.Thanks.

__________________
nvmani
Register to Reply
Power-User

Join Date: Feb 2010
Posts: 268
#7
In reply to #5

Re: Honeycombing

07/28/2011 5:05 PM

Did the contractor not have any insurance for this kind of scenario

__________________
guds777
Register to Reply
3
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#3

Re: Honeycombing

07/27/2011 12:35 PM

Yuppers is the answer......it resulted from poor vibration of the concrete during it's placement, or too tight a bar bundle etc.

Either jet it out or chip away, then fill with an epoxy modified cementious repair compound matching or exceeding the design strength parameters of the base concrete.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply Good Answer (Score 3)
Commentator

Join Date: Jul 2011
Location: Singapore
Posts: 82
#4

Re: Concrete Honeycombing

07/27/2011 11:17 PM

Assuming that the affected is substantial, you can always perform structural integrity test using Non destructive Test, ie impact echo, pulse radar and etc. Do contact Mr. Sze at www.setsco.com. Hope this help

__________________
Wish you luck on your search.
Register to Reply Score 1 for Good Answer
Guru
Popular Science - Weaponology - New Member Fans of Old Computers - PDP 11 - New Member Technical Fields - Architecture - New Member Hobbies - HAM Radio - New Member

Join Date: Oct 2009
Location: Maine, USA
Posts: 2168
Good Answers: 71
#6

Re: Concrete Honeycombing

07/28/2011 8:05 AM

Sue the builder and have it replaced! I would not want that over my head!

__________________
Tom - "Hoping my ship will come in before the dock rots!"
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Feb 2010
Posts: 268
#8

Re: Concrete Honeycombing

07/28/2011 5:10 PM

Is it just in small portion of the concrete, or is it all over the place.

__________________
guds777
Register to Reply
Guru

Join Date: Jun 2006
Location: Ottawa Canada
Posts: 1975
Good Answers: 117
#9

Re: Concrete Honeycombing

07/28/2011 10:00 PM

It is over head, and therefore you need an engineer licenced to practice in your area to examine it to determine if the structure is solid enough to be safe. This cannot be done by a forum, I would have to look at it in person, and probably take some cores.

There are ways to prop it up....brick arches retrofitted underneath come to mind. I am sure that it is likely cheaper to build arches rather than replacing a whole roof! (This was done for Wells Cathedral....so I know it works!)

And arches could be pretty! But lets face it, if you have the slightest worry about what is over your head, then please do not sleep under it. One small earth tremor and your babies are killed. It is NOT worth it to use substandard building materials over head! Walls, maybe, depends. Floors, absolutely. Roads, yes. But roofs? Well, I would have to examine it pretty closely before I would risk it.

Just an observation.

__________________
If it was easy anybody could do it.
Register to Reply Score 1 for Good Answer
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#10
In reply to #9

Re: Concrete Honeycombing

07/29/2011 11:35 AM

GA for yusef.

If the contractor who built this slab has insurance drag him back to the house and ask him if he's going to fix his mess. Get it in writing if the answer is either way. You can always contact his bonding company and file a written complaint.....threaten to "exercise his bond" as that will force the issue of replacement. If he and the insurance company refuses to replace the slab, then you have legal means at your disposal. If he has no insurance or a bonding company still take him to court, but make sure you have a licensed structural engineer visit the work site, inspect it and document the deficiencies as you're going to need him and that engineering report in a court of law as evidence, otherwise it's a battle of finger pointing between attorneys where nobody wins except the attorneys and nothing is finally resolved in regard to fixing the deficient construction.

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply Score 1 for Good Answer
Guru
Engineering Fields - Civil Engineering - Member

Join Date: Mar 2011
Location: ''but, don't we get PAID to ask questions?...''
Posts: 1661
Good Answers: 17
#11

Re: Concrete Honeycombing

07/29/2011 9:34 PM

Well, just for starters, how long ago was your (structure) built, and are there any (warranties/guaranties/other) still in force?

Did you purchase the (structure) ''as is''?

Is the seller still under any legal obligation to make good on the implied quality of the (structure) sold, or are you now totally ''on the hook" for the final sale?

Is it too late to back-out of the sale due to misrepresentation on the part of the seller?

The walls, particularly if of "shotcrete", may have similar defects...

You get some serious rainfall in your country, so you should cover as much, and as well, as possible to protect it from increased damage due torrential rainfall which could be blamed on you for not covering the (structure) better, sooner, etc...

Depending on the extent of the damage, a total ''remove-and-replace'' could be called for...

__________________
''illigitimi non carborundum...''(i.e.: don't let the fatherless (self-deluding,sabotaging, long-term-memory-impaired, knee-jerking, cheap-shotting, mono-syllabic, self-annointed, shadow-lurking, back-biting, off-topic-inquisitors) grind you down...)
Register to Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#12
In reply to #11

Re: Concrete Honeycombing

08/01/2011 4:19 AM

not vibrating the concrete as it was being installed was the most likely problem.

Register to Reply
Power-User

Join Date: Apr 2011
Location: pittsburgh
Posts: 180
#13
In reply to #12

Re: Concrete Honeycombing

08/01/2011 4:22 AM

sorry capt, i just realized i repeated you.

Register to Reply
Guru
Hobbies - DIY Welding - New Member Hobbies - Target Shooting - New Member Engineering Fields - Civil Engineering - New Member United States - Member - New Member

Join Date: May 2009
Location: Red Hook, New York (Mid-Hudson River Valley)
Posts: 4362
Good Answers: 179
#14

Re: Concrete Honeycombing

08/01/2011 8:40 AM

jlstitt, that's okay..."No Wukkas mate".

I find myself repeating things (and talking to myself as well) around here all the time.....especially when it comes to teenagers and doing chores! ***BILL THE CAT ACCCCKKKKK ACCCCKKKK!***

__________________
"Veni, Vidi, Vici"; hendiatris attributed to Gaius Julius Caesar, 47 B.C.
Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

CaptMoosie (3); guds777 (2); jlstitt (2); KJK/USA (1); lyn (1); MR. Guest (1); noelngke (1); nvmani (1); Tom_Consulting (1); Yusef1 (1)

Previous in Forum: Pipe Sizing for Hydro Station   Next in Forum: Freestanding Concrete Foundation - Shear Angle of Resistance

Advertisement