can anybody help me to find cable sizing. if there is any L.T cable or H.T cable then can we know by any calculation or formula that what is it,s size in "mm".
Thank,s and Regard,s.
Ikram Shehzad
Re: how to know cable sizing
07/28/2011 4:38 PM
07/28/2011 5:37 PM
Check that last one closely. The first 4 are the easy part. The last one is where you earn your money.
07/29/2011 5:03 AM
Hire a qualified Electrical Engineer, who will use the local equivalent of British Standard 7671.
07/29/2011 10:43 AM
To calculate the cable size it is necessary to know the followings-
Input data-
Voltage Kv
Total Kw
Load Power Factor
Cable resistance and reactance
Demand Factor
Load Factor
Ambient Temparature
Number of Cables in Paralel
Laying of Cable(Air/ Under Ground)
Short Circuit withstand time
Output-
Max current=
Derating Factor=
Voltage drop=
Area of cable=Ish*sqrt(T_short)/derating factor/number of parallel cable
Location: off the beaten track, not quite whoop whoop nor humptydoo
08/02/2011 1:45 AM
AS/NZS 3008 is in mm
Everything works out in the end, just not neccessarily how you want