overload setting on big motor,s

07/28/2011 4:30 PM

Dear all,

can you tell me that if a motor is 200 k.w and it,s rated current is 386 amp,s on delta. so please tell me that if we want to set the over load at 360 amp,s. we cannot installed overload at power because that,s too high current for overload. then we set overload on C.T ratio. and C.T,s ratio are 300/5. so please tell me that what is calculation for this. These C.T,s are installed on power cable,s.

Thank,s and Regard,s.

__________________
Ikram Shehzad
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: overload setting on big motor,s

07/28/2011 4:44 PM

A better choice of CT would be 500/5. If the overload sensor is applied to the CT secondary, then to match the motor FLA of 386, it should be set at 386 × 5/500 = 3.86 A.

[Editorial note: plurals such as "motors" do not ordinarily take either a comma (,) or an apostrophe (').]

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#2

Re: overload setting on big motor,s

07/28/2011 4:46 PM

You should probably get some local help who knows something about electricity.

It worries me that you are asking these types of questions on a forum where no one knows that your information is valid and you don't know the qualifications of the person careless enough to give a novice advice.

Seek professional help, or you could end up permanently dead. Or worse yet, you could kill somebody else.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: overload setting on big motor,s

07/28/2011 11:57 PM

Normally OL relay is sized according to phase current (386/1.732) which is approximately about 180A(check). CT should be 200/5.

__________________
pnaban
Register to Reply Score 1 for Off Topic
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4

Re: overload setting on big motor,s

07/29/2011 5:03 AM

Hire a qualified Electrical Engineer, who will use the local equivalent of British Standard 7671.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply