Motor Rating

07/29/2011 1:10 PM

why motors rating not more than 415v+_10%?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: motorvrating

07/29/2011 2:24 PM

Not so; there are motors with higher voltage ratings than that.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#5
In reply to #1

Re: motorvrating

08/01/2011 4:02 AM

And lower, of course.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
Canada - Member - If there is a way to screw someting up, there is someone to do so! Safety - Hazmat - New Member

Join Date: Mar 2007
Location: Iqaluit, NU. Canada
Posts: 1854
Good Answers: 140
#2

Re: motorvrating

07/29/2011 4:12 PM

You must be asking about the 10% voltage tolerance rating? All electrical utilization equipment, or most of it, has a built in tolerance for up to a 10% from optimal voltage rating. Meaning, the motor will work as advertised at up to + or - 10% of name plate voltage.

Anything outside that 10% range, either high or low, the motor is not guaranteed to perform as per design.

__________________
Joe Contractor to Electrical Inspector, "What do you mean you are going to make me follow the code?".
Register to Reply
Commentator
India - Member - Proud to be INDIAN Engineering Fields - Power Engineering - New Member

Join Date: Jul 2011
Location: Bengaluru, India
Posts: 91
#3

Re: motorvrating

07/30/2011 5:31 AM

Because + or - 10% tolerance is NEMA (National Electrical Manufacturers Association) standard for motors.

__________________
you need to go, to get something
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#4
In reply to #3

Re: motorvrating

07/30/2011 10:56 AM

Here is the quote from NEMA MG 1 - 2006

****

10.30 VOLTAGES

a. Universal motors-115 and 230 volts

b. Single-phase motors

1. 60 hertz-115, 200, and 230 volts

2. 50 hertz-110 and 220 volts

c. Polyphase motors

1. 60 hertz-115*, 200, 230, 460, 575, 2300, 4000, 4600, and 6600 volts

2. Three phase, 50 hertz - 220 and 380 volts

NOTE-It is not practical to build motors of all horsepower ratings for all of the standard voltages.

*Applies only to motors rated 15 horsepower and smaller.

12.44 VARIATION FROM RATED VOLTAGE AND RATED FREQUENCY

12.44.1 Running

Alternating-current motors shall operate successfully under running conditions at rated load with a variation in the voltage or the frequency up to the following:

a. Plus or minus 10 percent of rated voltage, with rated frequency for induction motors.

b. Plus or minus 6 percent of rated voltage, with rated frequency for universal motors.

c. Plus or minus 5 percent of rated frequency, with rated voltage.

d. A combined variation in voltage and frequency of 10 percent (sum of absolute values) of the rated values, provided the frequency variation does not exceed plus or minus 5 percent of rated frequency, and the voltage variation of universal motors (except fan motors) does not exceed plus or minus 6 percent of rated voltage.

****

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#6

Re: Motor Rating

08/02/2011 10:39 AM

It depends upon the supply voltage.In India Common LV voltage is 415Volts for 3 phase and hence all 3 phase motors are rated for 415Volts.HT motors are rated for 3.3kv,6.6 and 11 KVin India.However outside India it is 380V In Thailand and Indonesia.Similarly in case of HT it is mostly ^KV, 3 KV and 10KV.In Japan 3phase 220V motors are used as well as 200V 3 phase in some parts.As regards the variation In India we need +-10% as Voltage fluctuation is high.Outside it is mostly +_6%.It is not uncommon to have other voltage varitions specified like 415V+-12.5% or +6% and -10% etc which become special execution.Similarly Frequency variation and combined voltage and frequencies are also there.The performance figures like efficiency and power factor are however declared and hold good at rated voltage.What is implied is the motor can deliver the required torque and within permitted temperature rise when running at extreme voltage or frequency conditios.

__________________
To avoid crticism do nothing,say nothing,be nothing