Voltage Drop Formula

07/30/2011 4:05 AM

What is the formula for calculating the Voltage Drop in a LV Switchgear Panel?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: Voltage Drop Formula

07/30/2011 5:03 AM

In the PANEL? Usually VD is only an issue in the conductors when the length is long. There is very little VD in a switchgear busbar system that is properly designed and maintained.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Participant

Join Date: Jul 2011
Posts: 4
#2
In reply to #1

Re: Voltage Drop Formula

07/31/2011 2:51 AM

yes, that will be very low, but one of my client is asking for that, so can u just tel me how to calculate that? is thr any formula for that?

Register to Reply
Associate

Join Date: Dec 2008
Location: Kuwait
Posts: 27
#3

Re: Voltage Drop Formula

07/31/2011 6:17 AM

The Standard VD formula applies. Even though your customer is asking for the VD in a LV panel. The formula stays the same. Calculate the length of the busbars in your LV panel. Apply the VD formula and you will see very negligible VD. Good Luck!

__________________
Mark Abell
Register to Reply Score 1 for Good Answer
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#4

Re: Voltage Drop Formula

07/31/2011 10:25 PM

Your client must be in ownership or management, which would explain this weird question.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Associate

Join Date: Dec 2008
Location: Kuwait
Posts: 27
#5

Re: Voltage Drop Formula

08/01/2011 12:08 AM

Tornado's (#4) response is valid. A little research and you'll have the basic VD formula. Remember, the formula is for VD period! Whether you are applying it to an LV Switchgear panel or a legitimate length of a Conductor wire. You are getting closer to the answer...(lol).

__________________
Mark Abell
Register to Reply
Participant

Join Date: Jul 2011
Posts: 4
#6

Re: Voltage Drop Formula

08/01/2011 2:25 AM

VD = √3 X V X I X L X COS Ǿ, this is the formula know?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7

Re: Voltage Drop Formula

08/01/2011 3:59 AM

Once again, British Standard 7671 gives all.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Jul 2006
Location: Eastern Kansas USA
Posts: 1503
Good Answers: 128
#8

Re: Voltage Drop Formula

08/02/2011 7:04 PM

Tinoj,

I suspect the question you have asked is not the question you need answered. In a panelboard, the busbars and conductors all have a precise resistance, based on their dimensions and the resistivity of the metals (typically copper or aluminum). The voltage drop on these components is then fairly easily calculated by the application of Ohm's law, E=IR. This formula works for nearly all parts you are interested in.

However, I believe the question that is of greatest concern is whether your panelboard has too high a voltage drop due to components that have poor connections. If you know the predicted voltage drop of all the components, and compare it against the actual voltage drop, this might suggest that one or more connection(s) are bad, but it might also suggest that your original calculation was bad. Typically bad connections have too high a resistance and therefore cause localized heating. It is this heating which is your problem. Uncorrected, it can lead to equipment failure and fires. The most reliable way to detect this is with an infrared camera in the hands of a skilled operator.

Measuring voltage drops requires you to be "hands-on" with a panelboard that is open. Doing an infrared scan may require the covers to be off, but doesn't involve putting any leads or probes directly into the works.

Hope this helps--JMM

Register to Reply
Participant

Join Date: Jul 2011
Posts: 4
#9
In reply to #8

Re: Voltage Drop Formula

08/03/2011 3:06 AM

Thank you Mr. Jmuller,

this explanation is good. It helps me a lot. Once more thank you so much.

Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#10

Re: Voltage Drop Formula

08/03/2011 3:24 AM

Unless there are loose, corroded, or otherwise bad connections within the panel, the voltage drop there will be insignificant. I suspect that the real question is how much voltage drop there is in the wiring from the panel to the loads it serves. This latter is a common issue, which depends on the wiring size and length, and whether single or 3-phase.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

jmueller (1); JRaef (1); MasterEmaybe (2); PWSlack (1); Tinoj (3); Tornado (2)