Synchronous Motor Load

08/01/2011 7:16 AM

A synchronous motor connected to AC system is running with over
excitation in order to supply reactive power to the line ( as a
synchronous condenser) While supplying reactive power to the line
whether the synchronous motor will take active power from the line if it is on load or no load. While supplying reactive power to the line whether it can be loaded?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Synchronous Motor Load

08/01/2011 9:50 AM

Yes, yes... More clarity and detail in the question will get more clarity and detail in the answer...

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Anonymous Poster #1
#2

Re: Synchronous Motor Load

08/01/2011 12:14 PM

Homework?

Answer is given by RC (correct) now explain why

Register to Reply
Participant

Join Date: Jul 2011
Posts: 1
#3

Re: Synchronous Motor Load

08/02/2011 12:50 AM

Hi

For operating syn motor as a syn condenser, the necessary condition is to make the motor over excited under no load. At this condition s only we can expect the motor to operate as a capacitor, delivering reactive power for the system, the amount of reactive power supplied depends on the amount of excitation given to the motor. We can obtain both leading and lagging reactive power.

So the syn motor must be with no load for making it syn condenser.

Register to Reply
Participant

Join Date: Aug 2011
Posts: 3
#4
In reply to #3

Re: Synchronous Motor Load

08/02/2011 1:04 AM

The question is while operating synchronous motor as synchronous condenser at no load to supply reactive power to the line, whether the motor will take active power to rotate the rotor either from the line or from the DC source

Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5

Re: Synchronous Motor Load

08/02/2011 1:24 AM

A good paper (perhaps too advanced?), the pdf shown first on the google search result page.

Here

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
2
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#6

Re: Synchronous Motor Load

08/02/2011 1:53 AM

The necessary excitation of a sync motor depends on the mechanical load. If a free-running sync motor runs with over excitation it will deliver reactive power. If you increase the mechanical load, the load angle of the rotor will grow and this will eliminate the excess excitation. If you want the keep the capacitive power factor you have to increase the excitation again. Of course the saturation of the iron is a hard limit.

Hungarian railways used to use electric locos with synchronous phase converter and the schedule contained not only the stops and the times but the expected power factor too. The driver was responsible to deliver it. Due to the necessary excitation depended on the actual load of the loco there was a special control system named "Watt-relay" which maintained the power factor set by the driver.

The large round meter on the dashboard is the cosine phi meter.

__________________
Aged man is not old man...
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Mar 2010
Location: BHOPAL, INDIA
Posts: 201
Good Answers: 20
#7

Re: Synchronous Motor Load

08/02/2011 11:34 AM

Yes, motor will draw active power from the line to supply its own electrical and mechanical losses. If the excitation is taken from the exciter mounted from the same shaft, then excitation power will also be taken from the line. This is irrespective of load condition of the motor (at a load or no load).

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#8

Re: Synchronous Motor Load

08/03/2011 12:04 PM

As Qqberci said, it can be done but only to the limits of saturation of the rotor iron. So as your load increases, more and more of that capacity gets consumed in exciting the rotor field for the load, leaving less head room for over excitation as a synchronous condenser.

I have seen this done in two facilities (foundries) with the need for large air compressors because the peak loading on an air compressor can be predictably determined and the extra capacity can be built-in to allow them to function as synchronous condensers for the rest of the plant.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: May 2007
Location: Budapest, Hungary, HA5YAR
Posts: 617
Good Answers: 14
#9
In reply to #8

Re: Synchronous Motor Load

08/03/2011 12:08 PM

I'm starving for a GA... :-)))

__________________
Aged man is not old man...
Register to Reply Off Topic (Score 5)
Power-User
Engineering Fields - Petroleum Engineering - Rig Electrician United States - Member - the Oil Patch Engineering Fields - Power Engineering - Drives & Gen's Engineering Fields - Instrumentation Engineering - Drive Control Popular Science - Cosmology -

Join Date: Jan 2010
Location: Houston off/on-shore @ Oil Patch
Posts: 223
Good Answers: 2
#10
In reply to #9

Re: Synchronous Motor Load

08/04/2011 2:49 PM

anybody with a cartoon avatar and a post with a cho-cho (does that sound like a Hungarian accent?) train deserves a GA

__________________
Why do they make manhole covers round? so they won't fall in [before asking "Who is John Galt?"]
Register to Reply Off Topic (Score 5)
Register to Reply 10 comments