why we are using Aluminium wire armour for single core cables?
Anonymous Poster #2
Re: Use of Aluminium wire armour for single core cables
08/02/2011 5:55 AM
Dunno. Why don't you tell us.
Good Answers: 170
08/02/2011 6:21 AM
Aluminium is non-magnetic. Hence, there would not be any induced currents in the armour due to the current flowing in the main conductor.
08/02/2011 6:25 AM
ok, but y we are using it in single core cable particularly.
Good Answers: 170
08/02/2011 6:59 AM
Because, in multi-core cables, the resultant or the residual flux available for linking with the armour would be zero. And, in single core cables, there would not be any compensating flux from any neighbouring core and thus there would be appreciable residual flux available for linking with the armour and, if the armour is made of a magnetic material, such a resultant flux would induce voltages in the armour which would cause circulating currents, leading to heating and damage of the armour and the cable.
Anonymous Poster #2
07/01/2024 8:24 AM
Dunno. Why don't you tell us?
Good Answers: 15
Re: Use of Aluminium Wire Armour for Single Core Cables
08/02/2011 7:24 AM
in a single core cable steel or any magnetic material is not used for armor for reason already mentioned in earlier responses.
a good reading is suggested for the differences between aluminum and steel armor in cables in general for all - - -
http://www.anixter.com/AXECOM/AXEDocLib.nsf/(UnID)/14FA0C8C75D8006B80256F24006E59F4/$file/a-2_2.pdf
Good Answers: 44
08/02/2011 11:13 AM
Some of the explanations here are sound, but not entirely accurate. My organization has used steel armored cable for multipair and coaxial systems for nearly 50 years. These systems are both high and low voltage systems (many miles in length) transoceanic cable systems designed by AT&T, Lucent, etc.
08/02/2011 11:20 AM
What about single core, though, like the original poster?
Good Answers: 44
08/02/2011 12:10 PM
Single core as in coaxial? Then, yes. I have several list versions of the cable each utilizing various layers of steel armor. We also have a complex grounding system which includes the armor layer.
Good Answers: 15
08/02/2011 10:59 PM
single core as in single core . . . no more no less . . .
08/03/2011 12:02 PM
For the same reason mentioned above, apart from armour, anything 1C cable passes through like gland plate, metallic conduits etc. should also be of non magnetic material.
Good Answers: 44
08/03/2011 12:08 PM
Not sure where you are going with this...single core cable as in...? Coaxial is a single "core" cable with a shield. I guess that you (and the OP) mean power cable, not signal cable.
Guess I should have picked up on that.
08/03/2011 7:51 PM
Good responses already. You may also want to avoid steel cable trays and cable ties in such an application and preferably arrange the cables in a trefoil.
Good Answers: 15
08/03/2011 11:58 PM
steel trays may be acceptable if the magnetic math does not close around the conductor.