Why Can't we Use Fuse in Current Transformer?

08/08/2011 4:47 AM

why we are using fuse in VT alone...... i want to knw why we are not using fuse in secondary side of CT..???? if any short occurs in the sec side of ct... higher current flow than the normal current.... so there could be a possible tat over current relay can trripp...???

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
6
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: why cant we use fuse in current transfrm.....??

08/08/2011 4:55 AM

The fuse is a device to protect the wiring from overcurrent.

On the secondary side of a current transformer the current is proportional to that flowing in the primary and there is no possible source of overcurrent in the secondary as the primary overcurrent protection devices will operate first.

A current transformer not connected to an indicator device, as would be the case were a fuse to be installed in the secondary, will cause very high voltages to appear in the secondary wiring that may be sufficient to break down insulation.

So a fuse is neither necessary nor desirable in the secondary circuits of a current transformer.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply Good Answer (Score 6)
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#2
In reply to #1

Re: why cant we use fuse in current transfrm.....??

08/08/2011 10:17 AM

Bingo.

This by the way is the same reason why you must use shorting terminal blocks in the CT secondary circuit if you want to keep equipment operating in the even of a meter failure or removal.