Exhaust Blower Sizing for Small Fume Hood

08/12/2011 10:57 AM

Hi All,

I am trying to size an exhaust blower for a fume hood in a lab. The fume hood is for periodically cleaning 2" x 6" SS panels periodically with toluene, acetone, and IPA.

I have estimated that the maximum content of solvent in the air stream is less than 0.01% (100ppm).

I have estimated that, for a 100 ft/min ave face velocity at the 1.5ft x 2ft opening, I need a 300 ACFM flow rate. Temp is 72ºF.

The hood has a 6" flange opening for round duct.

The duct is 6" round galvanized at 25ft total length. There will be two 90º, 4-piece elbows (no vanes) with R/D ratio of 1.5.

The duct will go straight up, through a wall, then straight up and out the roof.

I have used an on-line calculator that gave me 0.426inH2O pressure drop and 0.145inH2O velocity pressure.

I have contacted a few vendors and am getting motor sizes ranging from 1/12 to 1/4 HP.

1). Is the velocity pressure the same as static pressure? (Thats what the vendors are calculating.)

2). I am estimating that a 1/8 or 1/6 HP motor will work. Does that sound reasonable?

Thanks everyone!

Mike

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#1

Re: Exhaust Blower Sizing for Small Fume Hood

08/12/2011 11:38 AM

I would size the motor slightly larger than any of the calculations suggest.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#3
In reply to #1

Re: Exhaust Blower Sizing for Small Fume Hood

08/12/2011 11:41 PM

I would size the motor slightly larger than any of the calculations suggest.

OK, so I'm going to buy three blowers? One calc was 1/4 HP, the second was 1/12 HP. Mine was 1/8 HP.

The calculations that I made were for the high-end flowrate, so in the calculations, the motor is already oversized (as if I didn't know to allow for that).

What I really want someone to check, is if my calculations make sense. If you don't know how (or care to) go through them, don't bother replying.

I'm sorry to be so abrupt, but I took time to include enough detail for someone who knows something about this stuff to answer my question.

How many questions are posted here that have almost no detail?

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#11
In reply to #3

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 6:54 AM

I'm sorry I bothered replying. I just posted what I would do. Since you're dealing with toxic, cancer causing solvents, I wouldn't do any calculations. I would get the largest fan that fit that particular hood, and be done with it.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#12
In reply to #11

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 5:38 PM

Sometime, something that seems so apparent to you may not be to someone else.

I am planning on a rooftop unit, not something that is attached to the hood. Ostensibly, we could get a blower that would be complete overkill.

Should we get a 20HP unit?

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru
Hobbies - Fishing - New Member

Join Date: Jun 2008
Location: Raleigh, NC USA
Posts: 13529
Good Answers: 468
#14
In reply to #12

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 11:16 PM

No worries dude. I don't know a whole lot about anything. I'm just a wrong answer waiting for a bad question. All is well.

I would go for the 1/3 HP unit.

__________________
Those who would give up essential Liberty, to purchase a little temporary Safety, deserve neither Liberty nor Safety. Ben Franklin
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#17
In reply to #14

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 11:38 PM

I'm sorry for my abrupt manner. I appreciate most of your posts and your take on the current US admin.

Why the 1/3 HP unit? I think 1/3 HP would be overkill.

Did you check out the calculation page on the site I provided in my OP?

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#2

Re: Exhaust Blower Sizing for Small Fume Hood

08/12/2011 11:20 PM

Be careful to not work above the Lower Explosion Level. I assume that you bring the solvents also under the hood. If the bottle breaks, you'll have a different scenario, also with spills. Chose the fan carefully - use a metal one with good ground and static discharge lead and brushless. Consider working in hotte (box with frontal sliding door)

A hood will suck too much omnidirectional. The products you use work addictive but are cancer evoking. The velocity and concentration tell me nothing unless you describe the exhaust system. The concentration will be function of work procedure, spill control, application dose and room temperature. And where your nose is.

The company I worked for lost 80% of their lab technicians to cancer.

__________________
Plenty of room here
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#4
In reply to #2

Re: Exhaust Blower Sizing for Small Fume Hood

08/12/2011 11:48 PM

I wrote: I have estimated that the maximum content of solvent in the air stream is less than 0.01% (100ppm).

Maybe I included too much detail in my post. You must have missed the above statement. Do you know ANY FLAMMABLE SOLVENT that has an LFL below 0.1%, let alone 0.01% (which I padded by more than an order of magnitude?)?

The company I worked for lost 80% of their lab technicians to cancer.

That's a wild, unsubstantiated statement. Do you have evidence to support this? I'll bet it wasn't due to any standard solvents.

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#5
In reply to #4

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 12:16 AM

I burried them all, one by one. This company started in the 70's and stopped in the 90's. APPLIED SOLVENTS WERE TOLUENE, XYLENE AND ALCOHOLS - all on a LAB Scale. And the lab had for those days good exhaust systems.

Free to air. The production plant was the worst: we used 70.000 liters toluene per month and this was flashed of the furnaces for about 8 years in a row.

Yhe first job I did there was designing a solvent recovery system with active carbon cylinders, that recovered to 92% of the solvents to reuse again and again.

My brother was a lucky one - he just lost the capability to smell.

I worked in a different division and my exposure was significantly less. I quit after 4 years.

It all depends how much toluene you will use and how accurate your vent works.

More: through what opening(s) size in sqFt or parts of Square Meters you attract the air to build up your exhaust stream.

Again: calculate to avoid disaster by accident.

When you smell it, it sucks already.

Why not a bigger fan system, say 1/2 HP with speed control?

At least you can play with openings, adapt the noise and work safe.

__________________
Plenty of room here
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#6
In reply to #5

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 12:48 AM

I agree that toluene is the most toxic solvent that we work with, but when you are talking less than 50 mL a day usage at most, and half of that gets thrown away with the paper towels into the enclosed flammable can, you really have very little solvent to get rid of.

More: through what opening(s) size in sqFt or parts of Square Meters you attract the air to build up your exhaust stream.

The hood opening is 24" wide by 18" high, as I already said. Did you really read my first post?

I burried them all, one by one. This company started in the 70's and stopped in the 90's. APPLIED SOLVENTS WERE TOLUENE, XYLENE AND ALCOHOLS - all on a LAB Scale. And the lab had for those days good exhaust systems.

Sounds like some lawyers made a lot of money. I'm sorry, but I don't believe they died of solvent-induced cancer. IF THIS REALLY HAPPENED, IT WAS CAUSED BY SOME OTHER REALLY NASTY COMPOUNDS - SOLVENTS THAT WE ARE TALKING ABOUT ARE NOT BAD ENOUGH TO CAUSE WHAT YOU ARE DESCRIBING.

Where did this take place, anyway? General area is OK.

I'm sorry about your friends, but your scenario doesn't make chemical/biological sense.

I need help with engineering and math, not chemical/greenie paranoia.

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#10
In reply to #5

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 5:12 AM

Hi Mike,

I did not and still do not see the opening dimensions.

English is not my native tongue, but as far as your explanation: I see a pipe upwards, somewhere through a ceiling with a hood - like an upside down funnel sitting at the bottom of the pipe. And probably with a table or bench underneath where you wash and dry your metal pieces.

If this is the case, your theory of CFM's is not relevant for the table area, but starts to make sense at the entrance of the hood (funnel).

Maybe here we went wrong. The hood will also collect air from all sides and not only the area straight under the hood.

I have no idea about the temperature difference bottom- top of your hood with pipe, to calculate the chimney effect. No-one talks about this here too. But this effect could completely compensate or overcompensate your friction.

You would be surprised of how much air you can evacuate as "leak" through this pipe, unless you put a vane in it. I have not enough parameters to calculate your fan, where in the first place the displacement counts and not the HP- rating.

I have been only trying to help and in a last attempt describe what the most safe working area can be: I'd make a box with in the front a glass sliding window that has counter weights and can be positioned at the chosen height. You can look through the glass to work and expose only your hands and arms. In this scenario your opening is a real one, considered the box is pretty hermetically sealed.

The sliding window can also be closed down, what keeps your room air in the room when not used.

This as far as your technical part.

----------------------------------------------------------------------------------------

As Toluene and Xylene concerns, read the CAS and Safety regulations. I buried them all means I am not a grave digger but I have been visiting them and it was not a nice view a while later I went to their funerals.

There is reason why companies move to easy legislation countries. Ethics in Europe are different from the US. Doctors and Lawyers cannot advertise or get barred or banned by Law. Workers have insurance and free medical care and are insured for industrial risks with a threshold. When they die, they get paid by insurance.

Cigarette companies are not sued by addicts. Doctors have ethics and work to heal the patients in the first place and not to fill their pockets. I am still bothered about impressions at seminars with (confraters) doctors of the US and Europe and the experiences I had during exchanging thoughts.

I try to give a honest impression, fueled by experience. I am not a Greenboy and in all the cases I am hired now by employers to adopt safety in their businesses. You underestimate the "Benzene" group, just like 40 years ago our bosses told us toluene did no harm. Men were put in process tanks to clean these with toluene on Saturdays, to remove the rests of Zinc oxide coatings. They had to talk or sing during the job and had a harness on. When their talk made no sense like drunks, they got hoisted out and put in the fresh air. A few years later, the link started to become clear. I am 60 and only 3 were older. Some would now be close to 40. Name and numbers I spare you. The country is the flagged one - The ending was a little more civilized for the victims than in Bhopal. For exact details PM me.

__________________
Plenty of room here
Register to Reply Off Topic (Score 3)
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#13
In reply to #10

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 5:55 PM

I have estimated that, for a 100 ft/min ave face velocity at the 1.5ft x 2ft opening, I need a 300 ACFM flow rate. Temp is 72ºF.

There it is. It's not a funnel, but a box with a duct flange on the top. The hands go through the 1.5ft x 2ft opening to do the work with the solvents. Air is sucked in through the open to carry the solvents, up and through the blower on the roof.

I take your point on the benzene/toluene/xylene compounds. Keep in mind however, that breathing 1000ppm day in and day out is a lot different from 5 - 10 ppm for 10min every couple of hours. Note that the odor detection for toluene is 0.17ppm - if you can smell it, you are not necessarily breathing over-limit vapor.

I hope makes things clearer.

Mike

P.S. Your English is very good!

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply Off Topic (Score 5)
Guru
United States - Member - New Member

Join Date: Mar 2010
Location: In the pool because it is too hot.
Posts: 3054
Good Answers: 141
#16
In reply to #13

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 11:18 PM

I think the chimney effect will be working. Whatever fan will improve it. Take care

__________________
Plenty of room here
Register to Reply Off Topic (Score 5)
2
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#7

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 2:55 AM

So far all comments are on the topic you have not requested. I will try to answer your two questions.

1) Is the velocity pressure the same as static pressure?

No, the velocity pressure is negligible compared to static pressure. So for calculations of power requirement it can be neglected, unless velocity is abnormally high. Value of velocity pressure is (density x velocity)**2/ 2g. Static pressure can be measured directly at blower discharge with the help of pressure gauge or manometer. Sum of static pressure and velocity pressure is called total pressure.

2) You can calculate power requirement, its very simple. But I'm giving in SI units, you have to convert suitably.

Gas Power (kW) = Flow Rate (cu.m/s) x Pressure rise (kPa)

Motor kW = (Gas power/ Bower Efficiency) x 1.2

Assuming blower efficiency as 0.6, motor power is two times the gas power. Take the next standard size motor. Static pressure rise is sufficient for calculation.

Register to Reply Good Answer (Score 2)
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#8
In reply to #7

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 3:10 AM

Hi pritam,

It's late here, and I'm about for bed. I took in enough of your post to appreciate your answer. I will take a look tomorrow and reply with how it helped!

Thanks, and GA!

Mike

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#9
In reply to #7

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 3:26 AM

A small correction in my comment #7.

Value of velocity pressure is (density x velocity**2)/ 2g ( please note the correction).

Register to Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#15

Re: Exhaust Blower Sizing for Small Fume Hood

08/13/2011 11:17 PM

Check with your standards for fume cabinets. The last time i had anything to do with them was in 1992 and the Australian standard had changed so that there could not be any discharge to atmosphere. This also applied to cyto toxic cabinets. The rationale is that innocent people in the neighbourhood should not be able under any circumstance to be subjected to your waste product.

The cabinet has to have inbuilt filtration with the onus being placed on the operator to check the efficacy of same.

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply Score 1 for Good Answer
Commentator

Join Date: Nov 2009
Posts: 78
Good Answers: 9
#18

Re: Exhaust Blower Sizing for Small Fume Hood

08/14/2011 11:11 PM

Dear friend

I have calculated using your figures v=300 acfm (= 8.5 m3/min) and TDH = 0.57 inch water (= 142.3 Pa). Assuming 60% efficiency.

Power = (8.5/60) x 142.3/0.6 = 33.6 W or 0.045 HP

My result is very close to the vendor figure of 1/12 HP. Therefore, to answer your question, your figure of 1/8 is very-very reasonable.

Hope the above helps.

P.s. Have you included the entrance and exit loss in your pressure drop calculation?

Register to Reply Score 1 for Good Answer
Commentator

Join Date: Aug 2011
Location: India
Posts: 59
Good Answers: 11
#20
In reply to #18

Re: Exhaust Blower Sizing for Small Fume Hood

08/15/2011 8:16 AM

Your calculation is based on figures of OP and formula given by pritam at #7. Formula is right but figures of OP is un-believable. See:

100 ft/min ave face velocity at the 1.5ft x 2ft opening, I need a 300 ACFM flow rate. I have used an on-line calculator that gave me 0.426 inH2O pressure drop and 0.145 inH2O velocity pressure.

100 ft/min velocity is too small for blowers and fans, based on which he has back calculated flow rate requirement. Velocity should be somewhere 30 to 60 ft/s. Pressure rise taken is also too small. It is based on pressure drop calculation, and not at static pressure requirement at discharge which shall be around 4 inH2O. So, OP has to check once again the requirement. I strongly agree with#7, that velocity pressure is negligible compared to static pressure.

__________________
When there is smoke, there must be fire.
Register to Reply Score 1 for Good Answer
Guru

Join Date: Aug 2010
Posts: 687
Good Answers: 21
#19

Re: Exhaust Blower Sizing for Small Fume Hood

08/15/2011 6:53 AM

I won't go through the design stages for building a discharge fan system for a lab booth here. Much to complicated for a short paragraph or two.

There is one manual that I kind of use for the bible to the standards required here in the states by OSHA. It is the ACGIH Industrial Ventilation, A manual of Recommended Practice For Design. A copy of which you should obtain and read before committing to building a booth of any kind.

Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#21
In reply to #19

Re: Exhaust Blower Sizing for Small Fume Hood

08/15/2011 3:45 PM

Everyone, thank you for the replies. Maybe this will clear some things up. This is how I have it pictured:

The box itself is an off-the-shelf unit. We are not building it ourselves.

If this clears things up for anyone, please feel free to comment.

My main reason for posting here is to double-check vendor info. One of them came up with a 1/4HP blower. Another came up with 1/12HP for the blower. Seems like a pretty wide spread.

I used Pritam's calculation and got 1/20HP. I will likely go with the 1/12HP model we were quoted.

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Commentator

Join Date: Nov 2009
Posts: 78
Good Answers: 9
#22
In reply to #21

Re: Exhaust Blower Sizing for Small Fume Hood

08/15/2011 9:45 PM

Have you consider elevation in your pressure drop calculation? the fan needs also to overcome the force due to gravity.

If I assume that the height of the stack is 10 m and adding to the pressure drop given earlier, the HP required will be 0.08 HP which is very close to 1/12HP quoted by the vendor.

Register to Reply
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#23
In reply to #21

Re: Exhaust Blower Sizing for Small Fume Hood

08/15/2011 11:49 PM

GA to prdp2344 for pointing out important issues pertaining to calculations.

"100 ft/min velocity is too small" and "It is based on pressure drop calculation"

Mikerho, please check these issues. Decide static pressure and velocity at discharge, refer some standard. Pressure rise and velocity both selected by you are extremly on lower side.

Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#24
In reply to #23

Re: Exhaust Blower Sizing for Small Fume Hood

08/16/2011 12:22 AM

Hi pritam,

Thanks for the concern. This is from WIKI; this excerpt is derived from Occupational Safety and Health Administration (OSHA) standards:

Maintenance

Fume hood maintenance can involve daily, periodic, and annual inspections.

  • Daily fume hood inspection
    • The fume hood area is visually inspected for storage of material and other visible blockages.
  • If hood function indicating devices are not a part of the fume hood, a 1-inch (25 mm) by 6-inch (150 mm) piece of soft tissue paper should be placed at the hood opening and observed for appropriate directional flow into the hood.
  • Periodic fume hood function inspection
  • Capture or face velocity is typically measured with a velometer or anemometer. Hoods for most common chemicals must have an average face velocity of 100 feet (30 m) per minute at sash opening of 18 inches (460 mm) or higher. Face velocity readings should not vary by more than 20%. A minimum of six readings shall be used determine average face velocity.
  • Other local exhaust devices shall be smoke tested to determine if the contaminants they are designed to remove are being adequately captured by the hood.
  • Annual maintenance

I really have done my "homework". So you see, my flow rate is adequate, and, since the calculations indicated a 1/20HP motor, and, since I am upscaling it to 1/12HP, I believe that everything is well in hand.

I appreciate your feedback!

Mike

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
2
Guru
Engineering Fields - Mechanical Engineering - New Member India - Member - New Member

Join Date: Aug 2008
Location: City of destiny, INDIA
Posts: 775
Good Answers: 67
#25
In reply to #24

Re: Exhaust Blower Sizing for Small Fume Hood

08/16/2011 3:56 AM

average face velocity of 100 feet (30 m) per minute at sash opening

Mikerho, I also rechecked, the velocity is perfectly in order for this application. So the flow depends only on sash opening size. So now instead of pondering over motor size, get a blower or exahust fan along with motor to suit flow rate. If you get with a speed regulator, it will be better.

Register to Reply Good Answer (Score 2)
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#27
In reply to #24

Re: Exhaust Blower Sizing for Small Fume Hood

08/17/2011 7:32 AM
__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#26
In reply to #21

Re: Exhaust Blower Sizing for Small Fume Hood

08/17/2011 7:28 AM

In my experience we slavishly follow the States in regard to our standards. Please check that you haven't been sold a pup.

Our standards call for the exhaust air to be sent back into the room, after going through appropriate filters.

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#28
In reply to #26

Re: Exhaust Blower Sizing for Small Fume Hood

08/17/2011 7:43 PM

Well, we could not put in a hood, and let the guy who has to clean the coupons with the solvents breathe the stuff day after day.

Sorry for the sarcasm, but we will be below fugitive emissions amounts.

However, we do have a Regenerative Thermal Oxidizer (RTO) to incinerate the solvent vapors coming from our coater drying oven. It's possible that we could tie in to the oven exhaust duct. The vapor throughput is on the order of 50 lb/hr - the RTO would EASILY handle what comes from the hood.

It is quite a ways away however and the hood would still need a blower to feed to the plenum between the oven and the RTO.

These regulations really piss me off! If someone uses MEK at home to do degreasing and whatnot, capturing the fugitive vapors is not regulated. In a work/production environment however, everything can be scrutinized with an electron microscope.

It might be worth it to feed the RTO to avoid any remotely possible noncompliance.

Hmmm, I think I'm getting paranoid

Thanks for the response!

Mike

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Register to Reply
Guru

Join Date: Sep 2008
Location: Where the sun sets on OZ
Posts: 1381
Good Answers: 28
#29
In reply to #28

Re: Exhaust Blower Sizing for Small Fume Hood

08/18/2011 7:55 AM

No wurries. I know you checked with OS&H but if our lot are anything to go by!!!!

For example; Our OSH acreditor, lets call him Ryan, is on the national executive. He told me/us on our course that "If i were you blokes i'd make sure i had ( an elcb protected 4 outlet power board ) next to me so that i could see my tools plugged in to it".

I told him that as all buildings under construction are required by law to be protected by an elcb an extra elcb on the line can cause both false positives ( most common ) but worse, also a false negative. The manufacturer was aware of this situation and buried in the instructions was advice to not have their device on an already protected circuit. Also number one item on his instruction sheet was 1. do not use on the end of an extension cord. Plug directly into the wall outlet.

Quite the opposite to his advice in his lecture.

I suggested to him that he may like to bring up my points at the next national gab fest.

Next time i saw him i asked the question. His reply "We are still advising people to use them as they have a stand on them to keep the plugs up out of any water that may be on the ground". WTF????

During his lecture he again made his statement about keeping the device close and mentioned that he had the onerous task of telling a wife that her husband had been electrocuted just last week. I spoke to him afterwards and asked how the bloke was electrocuted. He said the elcb didn't work. I was too polite to hammer home the point that it was his advice that probably killed him.

Is Os&h just another industry providing jobs and not doing much else?

Regards

Jim

__________________
Where's the KaBoom? There should be a KaBoom!
Register to Reply Off Topic (Score 5)
Register to Reply 29 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: