Selection of Starters For Motors

08/13/2011 3:33 AM

I want to know what type of starter is used for 3 ph induction for various hp for eg,,,,, if i am using 10HP motor what type of stsrter csn be uded , wheathere DOL or Star Delta?

If the ratings is higher what type can be used.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: Selection of starters for motors

08/13/2011 3:57 AM

It depends on the supply and if the drive can handle DOL starting. If the supply is weak then S/D doesn't put as much strain on it, the same can be said for the drive, can it handle the high torque of DOL starting?

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#2

Re: Selection of Starters For Motors

08/13/2011 10:15 AM

Different type of starters/starting methods are available. The selection depends on how rigid or weak the supply system is. Common starting methods are:

a. DOL

b. Auto-transformer starter

c. Star Delta starter

d. V/F controlled starter (VFD/VSD)

There selection is based on hand calculations or simulation thru' s/w wherein voltage drop during DOL starting is observed. If the same is within permissible limit, DOL is obvious choice. If not, other starting methods in b, c, d above can be resorted, to reduce starting current and hence voltage drop. Lot of factors goes into selection of b/c/d such as economics, reliability, load characteristics, O&M issues etc.

While selecting b/c, note that, as they are nice in reducing the starting current but consequently also pull down the starting torque of motor (by factor V2). Make sure the selected starting method, gives sufficient torque to the motor to take on the load.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#7
In reply to #2

Re: Selection of Starters For Motors

08/15/2011 4:25 AM

The original poster also needs to take the supply tariff into account when selecting. If the tariff is a peak-demand one, then replacement of DOL starters with more sophisticated ones, beginning with the biggest motors across the facility, could show very quick payback times.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: Selection of Starters For Motors

08/13/2011 12:53 PM

If it were me, S-D is never an acceptable choice, I think they cause more problems than they solve. I would use solid state and if it's under 10HP, you might even look into a VFD because they are now so inexpensive.

But as mentioned, the decision on using DOL or some other sort of Rediced Voltage starting is typically based on an evaluation of the available supply stiffness and/or the mechanical issues. Quite honestly at 10HP it's pretty difficult to justify anything other than DOL, unless perhaps variable speed offers other benefits.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Member

Join Date: May 2011
Posts: 5
#4

Re: Selection of Starters For Motors

08/14/2011 12:09 AM

All depend on what you need.

You need lowest cost, DOL is the choice, but High start current is consideration.

You need good deal between cost and performance Star-Delta is the choice, but high current start is still consideration.

You have little more budget, Soft starter or transformer start system is the choice.

You have more budget, VSD is the best choice, Low current start, high performance(depend on VSD type), low electricity use.

Register to Reply
Commentator

Join Date: Sep 2008
Location: India
Posts: 91
Good Answers: 6
#5

Re: Selection of Starters For Motors

08/14/2011 1:10 AM

One more advantage of DOL starter is,

A Star-delta starter can only be used if in the motor name plate it is stated as delta connected for the rated line voltage. For example, if in name plate it is stated as Star connected, and if you use star/delta starter, you will burn the motor.

Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#6

Re: Selection of Starters For Motors

08/14/2011 7:04 AM

If your supply system is strong then go for DOL otherwsie Star/Delta

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#8

Re: Selection of Starters For Motors

08/16/2011 11:21 AM

for 10HP, DOL would suffice.

Register to Reply
Active Contributor

Join Date: May 2011
Posts: 14
#9
In reply to #8

Re: Selection of Starters For Motors

08/17/2011 12:19 AM

for more than 10HP wheathere to use star delta or vfd

Register to Reply