Transformer Connection

08/17/2011 6:26 AM

Dear friends

I am working in a small transmission system having 12nos 132/33 transformers. All of them are rated 125MVA. Vector group is Ynd5. 132kV side neutral of all our transformers are solidly earthed.

Now a new consumer is requesting a 132kV connection from our grid. They propose 132/11kV 40MVA transformer at their end. The vector group proposed by them is Dyn11

Is there any protection and operation related problem in using this this vector group transformer in our system.

Raju

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Engineering Fields - Power Engineering - New Member

Join Date: May 2007
Location: NYC metropolitan area.
Posts: 3230
Good Answers: 444
#1

Re: Transformer Connection

08/17/2011 9:42 AM

An interesting "on-your-feet" (homework, interview, water-cooler, etc.) question. Since it is short on details let's try something different. Why don't you provide your solution to this question and we will provide our comments on your answer. Fair enough? Looking forward to your reply.

__________________
“Tell me and I forget. Teach me and I remember. Involve me and I learn.” Ben Franklin.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Transformer Connection

08/17/2011 9:56 AM

I do not foresee any problem.

Register to Reply
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#3

Re: Transformer Connection

08/17/2011 4:00 PM

Quote " Now a new consumer is requesting a 132kV connection from our grid. They propose 132/11kV 40MVA transformer at their end. The vector group proposed by them is Dyn

It does not matter what the customer's vector group is. Your primary connection will likely be a delta. They will adjust their rotation as needed.

Register to Reply
Power-User

Join Date: Jun 2010
Location: Canada
Posts: 139
Good Answers: 6
#4

Re: Transformer Connection

08/17/2011 11:01 PM

Why do you care about the customer's Tx configuration? Be it "Y" or "D" . . .?

Your customer will soon find out that he can not purchase a transformer with a 132kV delta connected winding. I do not know of anyone offering - or using a Delta connection @ 132kV.

Register to Reply Score 1 for Good Answer
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#5
In reply to #4

Re: Transformer Connection

08/18/2011 4:19 AM

That's dealing with reality. In the mind anything is possible.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: May 2010
Location: Liverpool, NY
Posts: 961
Good Answers: 131
#6
In reply to #4

Re: Transformer Connection

08/19/2011 11:04 AM

You are incorrect that the customer cannot purchase a transformer with 132kV delta primary. Many (I would venture to say most) distribution station transformers fed from a transmission-level voltage (100kV and above) will be delta-wye. It's usually transmission station transformers (often auto-transformers) and generating station transformers (usually wye-delta) where we see a wye connection.

Just for grins, I just did a little searching of some vendors I know, and saw for sale on the used apparatus market several 40MVA, 161kV D - 13.8kV Y transformers, several 50MVA, 138kV D - 13.8kV Y, and others. There is no technical or physical reason that what the OP stated is impossible.

__________________
To get the right answers, first you need to ask the right questions.
Register to Reply
Register to Reply 6 comments

"Almost" Good Answers: