Anonymous Poster #1

Transformer Protections

08/18/2011 7:30 AM

What are the Protections for Transformer?

Still now i know only relays:

27: Under Voltage Relay, 30: Announciation Relay,

50: IDMT O/C Relay, 50N: Instataneous O/C Relay

51: E/F relay, 51N: Instataneous E/F Relay

64: Restricted E/F relay

74: B/H relay, WTI, OTI Relay, (Relay No's: 86 , 94 and 95)

and OLTC and RTCC

I know only these relays any remaining protections also is there for protection of T/F.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Transformer Protections

08/18/2011 7:45 AM

Fuses?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Anonymous Poster #2
#2

Re: Transformer Protections

08/18/2011 8:50 AM

Surge protection my friend.

Reply
Power-User

Join Date: Jun 2007
Location: ether
Posts: 371
Good Answers: 1
#3

Re: Transformer Protections

08/18/2011 9:53 AM

theres also the Buchols relay... I am not sure if the name of this engineer is correct dough!

__________________
“For no man can forbid the spark nor tell whence it may come.” ? Francis Bacon
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4

Re: Transformer Protections

08/18/2011 10:56 AM

A few corrections:

27 is AC Undervoltage Relay

50 is Instantaneous Overcurrent Relay

50N is Instantaneous Neutral Overcurrent Relay

51 is AC Time Delayed Overcurrent Relay

51N is AC Time Delayed Neutral Overcurrent Relay

64 is Earthfault Relay (64R is Restricted Earthfault Relay)

74 is Alarm Relay

86 is Lock-out Relay

94 is Tripping or Trip-free Relay

95 is Assigned for devices where none of the Device Function Numbers 1 to 94 are suitable.

Buch-Holz Relay shall be numbered 63;

Oil Temperature Relay shall be numbered 26T & Winding Temperature Relay shall be numbered 49T

This is as per ANSI C 37.2-1970.

And, as regards the protection of transformers, it depends upon the size & criticality of the transformer.

Reply
Active Contributor

Join Date: Aug 2011
Location: Hyderabad
Posts: 14
#5
In reply to #4

Re: Transformer Protections

08/18/2011 11:54 PM

Dear Sir,

Thanks for your information it is very usefull to my bright career.

Thanks & regards,

Srinivas

Reply Off Topic (Score 5)
Power-User
Engineering Fields - Electrical Engineering - New Member

Join Date: Dec 2009
Posts: 247
#6
In reply to #4

Re: Transformer Protections

08/19/2011 2:21 AM

you forgot the most important one, percentage differential protection - which operates for internal fault, but will not operate for through fault. A simple differential protection does not take into account of CT's inaccuracy due to difference in magnetic saturation characteristic of field winding - which is more pronounsed during transient conditions.

sks

--------------------------------------

(serving humanity)

Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#7
In reply to #6

Re: Transformer Protections

08/19/2011 2:38 AM

Acting too smart! huh! So, you think that differential protection is 'most important' for transformers! Would you provide it for any size of transformer, say 100kVA? What I have done is to correct the ANSI Code explanations, which were wrongly mentioned by the OP. Moreover, the OP has not specified the size of the transformer. Haven't you read what I have mentioned at the end of my posting that the extent of transformer protection depends upon the size and criticality of the transformer?

And, since you are trying to teach me 'percentage differential protection' - by the by, it should be "percentage biased differential protection" - let me ask you a question:

Generally, in transformer differential protection, one uses Class PS CTs, whose knee point voltage or the saturation level, is calculated duly taking into account all the worst case scenario parameters. Then why should one use a percentage biased differential relay?

Reply
Power-User

Join Date: Jun 2010
Location: Kolkata, West Bengal, India
Posts: 172
Good Answers: 1
#8
In reply to #7

Re: Transformer Protections

08/19/2011 5:28 AM

To take care CTs mismatch during operation of protection.

__________________
Manindra
Reply