Ratings of Transformer and Generator

08/28/2011 12:23 PM

Why transformer ratings in VA (i.e. apparent power) while generators can be rated in both VA as well as Watts ?

Is reactive power important for both? coz reactive power can never come into picture if load is pure resistive??

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Ratings of Transformer and Generator

08/29/2011 12:37 AM

For a genset, the VA rating pertains to the generator; whereas the KW (or HP) rating pertains to the engine. In other words, both an electrical and a mechanical rating; but the tranformer needs only an electrical rating.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Power-User

Join Date: Nov 2008
Location: India
Posts: 333
Good Answers: 6
#2
In reply to #1

Re: Ratings of Transformer and Generator

08/29/2011 6:06 AM

Yes, its true.

Transformer size is restricted by the temperature rise of the winding & insulation ( normally oil filled transformers , temp. rise limits are 45 deg. above Amb. of

40 deg.C) this is represented by VA rating.

__________________
Exploring the Science of Electricity
Register to Reply
Active Contributor

Join Date: Feb 2011
Posts: 15
#3
In reply to #2

Re: Ratings of Transformer and Generator

04/14/2012 4:25 AM

what about protection against overfluxing?

why protection is provided for it, as it can be controlled by just changing the material of core?

Register to Reply Off Topic (Score 6)