Anonymous Poster #1

What Should Be Recommended

09/01/2011 12:35 PM

i have machine which is controlled by a microprocessor, the problem is during every after power interruption it hang and needed resetting before starts working again. Motor rating at 11kw. Voltage drop about 0.5 second switching from genset to local power provider. What could you recommend to eliminate resetting?

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Hobbies - Musician - Engineering Fields - Chemical Engineering - New Member Engineering Fields - Control Engineering - New Member Engineering Fields - Instrumentation Engineering - New Member

Join Date: Jan 2007
Location: Moses Lake, WA, USA, Thulcandra - The Silent Planet (C.S. Lewis)
Posts: 4216
Good Answers: 194
#1

Re: WHAT SHOULD BE RECOMMENDED

09/01/2011 12:48 PM

An uninterruptable power supply:

(not an endorsement)

__________________
"Reason is not automatic. Those who deny it cannot be conquered by it. Do not count on them. Leave them alone." - Ayn Rand
Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#2

Re: WHAT SHOULD BE RECOMMENDED

09/01/2011 12:51 PM

What are you asking for?

Are you looking for a way to fix an OEM product's behavior? Or is this your own microprocessor design and you have a problem?

For the first issue I would just buy a simple UPS power backup unit for the micro. Then power interruption will have no effect. I do this for my milling machines so the electronics do not reset.

If this is your own design, then I would suggest a power supply monitoring chip that has a built in reset function when the power supply level falls to a set level, thus insuring the system will not get into a locked state and restart in a controlled way.

I would also revisit the power supply design to make sure that there is sufficient drive for the circuit and enough reserve capacitance to serve your needs.

Reply
Power-User

Join Date: Aug 2007
Location: Lahore
Posts: 369
#3
In reply to #2

Re: WHAT SHOULD BE RECOMMENDED

09/01/2011 11:47 PM

The best solution is UPS. I installed UPSs with all PLCs.

__________________
Don't assume any thing, always check/ask and clear yourself
Reply
Anonymous Poster #1
#5
In reply to #2

Re: WHAT SHOULD BE RECOMMENDED

09/03/2011 12:25 PM

This actually an OEM product behavior. Installing UPS to micro seem to be a good idea, but i have a drive too intergrated to the system, does it supposed to be included scheduled for UPS?

Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#6
In reply to #5

Re: WHAT SHOULD BE RECOMMENDED

09/03/2011 12:35 PM

to run a ac drive from power derived from a ups requires too much thinking and after all the thinking the answer may be a NO . . .

Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#7
In reply to #5

Re: WHAT SHOULD BE RECOMMENDED

09/03/2011 1:15 PM

You should power the whole microcomputer and drive and any peripherals for the machine off of the same UPS.

Reply
Anonymous Poster #1
#8
In reply to #7

Re: WHAT SHOULD BE RECOMMENDED

09/04/2011 1:52 AM

any advice then for a 15KW UPS, how big is this? Is there available on the market?

Is there any other means to counter measure the power interruption? How about an AVR would that do given change in voltage would be about a split second?

Reply
Guru
Popular Science - Evolution - New Member Popular Science - Weaponology - New Member

Join Date: May 2006
Location: The 'Space Coast', USA
Posts: 11119
Good Answers: 918
#9
In reply to #8

Re: WHAT SHOULD BE RECOMMENDED

09/04/2011 8:28 AM

Your best answer would come from the manufacture of the equipment you are trying to protect. I would recommend calling them and speaking to a technical representative or engineer.

The UPS should be sized to fit the power requirements of the electronics. I am not sure that you need to run the mechanical machine from a UPS, but I am not clear on the full nature of your needs. It is hard to understand the complete story by simply writing "emails" back and forth.

That is why I recommend either calling an expert on the phone or a face-to-face discussion with a field engineer to make sure you have all your bases covered.

Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#4

Re: What Should Be Recommended

09/02/2011 12:44 AM

do you need to restart your process from where you left it when power dropped?

or does your process need to restart from the last finished stage?

or does your process need to restart from zero state?

all of the above need to be attended by your system designer and software writer together.

-

-

-

now for the hardware issue and need to restart electrically . . .

if your process does not require a full restart from cold state then - go for a ups that has a communication interface so that your program has time to shut down and your drives have time to park and all is well before you disconnect power from your control systems . . . in addition to communication, your ups must also have enough battery capacity to last till all the shut down takes place . . . some processes may require some cycle to complete before shutting down too . . .

Reply Score 1 for Good Answer
Reply to Forum Thread 9 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Anonymous Hero (3); Anonymous Poster (2); Mikerho (1); Signode (1); soebfatehi (2)

Previous in Forum: EMTP Model   Next in Forum: Question on current sudden increase

Advertisement