Question on current sudden increase

09/02/2011 1:30 AM

why current increase when power source shift to normal supply from inverter while motor still turning????

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Question on current sudden increase

09/02/2011 1:35 AM

Is the motor at rated speed when the transfer occurs? If not, the situation resembles DOL starting, with increased current.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Anonymous Poster #1
#2

Re: Question on current sudden increase

09/02/2011 1:36 AM

is motor acting as load?

switching surges

voltage stored in coil etc. my be the reason.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Question on current sudden increase

09/02/2011 9:20 AM

Is there power factor correction in the inverter?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#4

Re: Question on current sudden increase

09/02/2011 12:41 PM

If the transition is open, for example with a transfer switch, ANY small amount of deceleration in the motor while there is no power on it during the transition will result in a current surge when reconnected.

If the transition is too fast, the magnetic field in the motor may not have collapsed yet and the motor may still be regenerating. If that happens, when you re-connect, you will be out of phase with the supply and extreme current and torque surges may actually damage the motor.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru

Join Date: Sep 2009
Posts: 1056
Good Answers: 88
#5

Re: Question on current sudden increase

09/02/2011 7:15 PM

A modern inverter gets feedback from motor's current vector and applies appropriate corrections depending on expected and actual load dependant slip, making it possible to apply less current for lighter loads, according to real conditions and programmed data. I assume you are referring to this current difference and not the expected surges when any disruption on normal power feed would cause, because of even momentary phase sequence loss and resulting de-synchronization. So generally some current variation is to be expected. S.M.

__________________
Life is complex. It has a real part and an imaginary part.
Register to Reply
Power-User
Popular Science - Weaponology - New Member

Join Date: Jun 2011
Location: Berkeley, CA USA
Posts: 128
Good Answers: 4
#6

Re: Question on current sudden increase

09/03/2011 1:34 AM

How long does the increase last for?

If your inverter puts out a square wave the effective voltage coming out of the inverter may be higher. If you are connecting to a lower voltage supply but providing constant power the load will draw more current. Also if your inverter is supplying a square wave and you are not using a true RMS meeter the reading will be off when looking at the inverter output.

__________________
Working to end the use of carbon for energy
Register to Reply
Participant

Join Date: Jun 2011
Posts: 2
#8
In reply to #6

Re: Question on current sudden increase

09/04/2011 6:53 PM

I'd also be making sure you are using a true RMS meter, as indeed some inverters do produce square wave instead of the reasonably clean sine wave from the mains.

The current increase may be measurement error due to this

Register to Reply
Power-User

Join Date: Jul 2008
Location: UK
Posts: 205
Good Answers: 50
#7

Re: Question on current sudden increase

09/04/2011 7:05 AM

because there is a speed and / or frequency mismatch from before to after.

Some inverter control can be less 'stiff' if the applied voltage is lower than the mains supply or rating (aka energy saving mode for example) so the reconnection accelerates the motor to its load rated speed from the lower speed of the VFD. Maybe this could be your unexpected increase in current at what you may think is the same speed?

__________________
Something new every day!
Register to Reply