Fault Current

09/03/2011 5:45 AM

Dear friends, i want to know that before designing a new feeder protection system how to calculate the feeder's fault current to provide protection relay a refrence fault current.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
3
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#1

Re: fault current

09/03/2011 8:04 AM

If you need to ask this question should you be designing feeder protection?

__________________
The reports of my death are greatly exaggerated.
Register to Reply Good Answer (Score 3)
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#2
In reply to #1

Re: fault current

09/03/2011 10:16 AM

Exactly

If the only life the OP was risking by learning the rules of power distribution, I could understand learning the hard way. Only authorized people should work on power distribution.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
2
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3

Re: Fault Current

09/03/2011 12:13 PM

Transformer rated full load current ÷ percent impedance = SC current that it can deliver....

Or, did you want something else?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Good Answer (Score 2)
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#5
In reply to #3

Re: Fault Current

09/04/2011 3:27 AM

this assumes infinite source.

The equation should have been Transformer rated voltage/Rated Impedance = SC

In actual practice we do not have infinite source. There will be a source impedance [or thevenin's impedance ] and source voltage [or thevenin's voltage]

The actual fault current is determined by Thevenin/s voltage divided by thevenin's impedance.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: Fault Current

09/04/2011 5:57 AM

i can see the logic of what you say. However, i have seen people just take the transformer power ÷ pu impedance...for example, 1 MVA tfr,5%impedance, so SC current = 28kA. (415V system)

How wrong is this figure in your opinion/experience ? Is it likely to be 1%, 5%, 10% ... higher than real SC current? Some ballpark figure will be appreciated.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#8
In reply to #6

Re: Fault Current

09/04/2011 6:21 AM

Well I prepared a table of typical values based on my experience with Indian grids.

The first part of the table shows thevenin's impedance on 100 MVA base for typical fault levels in MVA indicated for different kV level.

The second part of the table shows the transformer impedance on 100 MVA base for different MVA rating of the transformer.

The total impedance to be used is the sum of the value of the first part + corresponding value of the second part, depending on actual fault level and the transformer rating.

We will see that when the grid fault level reduces, the thevenin's impedance increases and will have more significant bearing on the accuracy of the calculations.

For example if we consider 11 kV 500 MVA fault level, with Thevenin's impedance of 0.2 per unit on 100 MVA base and 10 MVA transformer with 0.5 per unit impedance on 100 MVA base, we get a total impedance of [0.5+0.2 = 0.7 per unit] on 100 MVA base. Obviously this is significant change in this case , if we ignore thevenin's impedance.

kVFalut MVAFault MVA on 100 MVA baseThevenin's impedance in per unit on 100 MVA baseFault kA
400100001000.0114.43375673
2205000500.0213.12159703
1321500150.0666666676.560798514
661000100.18.747731351
331000100.117.4954627
1150050.226.24319405
0.4250.25436.08439182
Transformer Rating in MVA5% impedance on 100 MVA in pu
1000.05
100.5
51
15
__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Participant

Join Date: Sep 2011
Posts: 2
#19
In reply to #8

Re: Fault Current

09/07/2011 3:44 AM

thank a lot Dr. i am erecting a 33 kv / 66 kv substation in my 33 kv feeders how many kamps i have to consider as a fault current for 25 mva transformer . is 33 kv line's lenth , soil's type or resistivity and voltage level are also effecting the fault current ?

Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#20
In reply to #19

Re: Fault Current

09/07/2011 4:09 AM

If your concern is only relay setting and if this is a radial feeder, I will advise you to consider the minimum current at which the IDMT characteristic just reaches the definite minimum operating time. [for 51 type relay], For all currents above this current, the operating time will be same [definite minimum time]

For all currents below this value, the relay characteristics ensure grading with other similar relay characteristics which are either backup relays to this one or primary to this one, as consequence of the characteristics shape.

Earth fault current calculations will get affected by the zero sequence parameters and ground return impedances.

you cannot simply assume some fault current and may need to compute the fault currents, by constructing the network model and considering the impedances of the fault sources and the network. You can contact a consultant for the same.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply Off Topic (Score 5)
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#4

Re: Fault Current

09/03/2011 11:14 PM

redfred - i think it is only by working on anything can one acquire skills required to be authorized . . . i am sure you will ponder a while on this . . .

Register to Reply
Guru
Engineering Fields - Electrical Engineering - Been there, done that. Engineering Fields - Control Engineering - New Member

Join Date: Dec 2008
Location: Long Island NY
Posts: 15600
Good Answers: 981
#17
In reply to #4

Re: Fault Current

09/05/2011 11:28 AM

I've pondered your statement for a reasonable amount of time. I see only two scenarios that explain your statement.

First, you misunderstand the meanings of the phrases, authorized to work on a system and an authority of a system. Authorized to work on a system is synonymous to an individual or group has been granted permission to work on a complicated or dangerous system. Likely this permission will be granted with conditions of safety equipment and/or training to work on the system. This permission will also be granted only when proper coordination with other affected and effected groups get informed. The individual or group that grants permission has the position of authority for that specific system. With this authority comes the responsibility that only individuals with proper training will be permitted to work on the system. Similarly, this authority comes with the responsibility that coordination of all individuals working on this system are aware of their responsibilities and conditions during all phases of operation. Now I do agree that once an individual has been granted authority to work on a dangerous system, they must continue to learn from the experience and be open to others criticism of their work. I also agree that those granted the responsibility of being the system authority should first work somewhere as one seeking authority. But before their hands, tools, design gets installed on a dangerous system they must first get the authority to do this from the proper authority.

My second option that explains your statement should be considered offensive. It is meant to be offensive because lives are at stake. You don't give a damn about the life of anybody foolish enough to ask about a dangerous system that is not asking their questions to the authority in charge of the system. You have no problem giving enough of a plausible answer that they feel empowered enough to circumvent the safety of a well controlled system. If the system is sufficiently robustly maintained that before a fatal incident happens the erroneous intrusion or design gets caught and a fool has been found. What greatly bothers me of this attitude and approach is that the fatality may not be the eager fool but somebody who happens to be at the wrong place at the wrong time.

Before you make an indignant reply, I do not think that you are so callous as my second scenario. I believe that your thoughts were closer to my first scenario. But I hope you appreciate the potential gravity of the second scenario and why I had to bring it up.

So I repeat my earlier comment. Only authorized people should work on power distribution.

__________________
"Don't disturb my circles." translation of Archimedes last words
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#18
In reply to #17

Re: Fault Current

09/05/2011 12:04 PM

of course i understand and appreciate where you are coming from . . . maybe my statement came from a third premise and was intended to elicit responses quite like yours . . . after all there can be 11 types of people in the world . . . thanks for writing in to expand our knowledge and understanding of serious and important concerns . . .

Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#7

Re: Fault Current

09/04/2011 6:20 AM
__________________
shamith gambhir, electrical engineer
Register to Reply
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#9

Re: Fault Current

09/04/2011 11:48 AM

Formula in post # 3 (KVS post) can be utilized (together with 'parallel' combination of source MVA) to arrive at the fault current with 'finite source' as well. As per KVS post # 3/6, for 1.0 MVA, Z= 5% trafo, S.C. for a through fault is 28 kA @ 415V sec. (or 20 MVA). This is assuming infinite source at the trafo prim.

Let us now consider 'finite source' with below assumed S.C. MVA values:

1. 50 MVA

2. 25 MVA

3. Infinite MVA source (also included for comparison purpose)

For a fault on sec. side of trafo, S.C. MVA will be:

For 1: = (50x20)/70 = 14.28 MVA (down to about 71.4%)

For 2: = (25x20/)/45 = 11.11 MVA (down to about 55.5%)

For 3: = 20 MVA (100%)

Thus it can be seen that there is a significant change in fault current based on "strength/weakness of source" as rightly mentioned by previous post # 5/8 of Raghunath.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#10
In reply to #9

Re: Fault Current

09/04/2011 12:06 PM

My thinking is

....is it not safer to use the 'infinite source' value since any 'finite source' can only deliver a lower fault? If one does an actual case study, one may be surprised that while the arguments are interesting in the abstract, reality is quite different, and that when you want a 36 kA CB, you will actually find a 50kA CB is not more expensive. So, rather than have an uneasy feeling that the CB may be somewhat underrated if the Thevenin calculations are awry, better to be safer with a higher capacity CB.....

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#11
In reply to #10

Re: Fault Current

09/04/2011 12:12 PM

when you use a 50kA CB for a system with a fault current of only 35kA - instead of using a 36kA CB - you have to be cautious while setting the same . . . else you will compromise protection . . . this in the field is often overlooked even by experienced engineers . . .

Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#12
In reply to #11

Re: Fault Current

09/04/2011 12:26 PM

Higher kA rating is safer but expensive.

Normally fault level in the grid continuously increases with addition of new transmission lines, and power generators as in India [India is supposed to have robust growth plans over next decade] and the higher rating chosen now may become insufficient in about 10 to 20 years time.

I have come across situations, where we had to put reactors in series to limit the calculated fault levels.

Higher kA rating of the breakers will not affect the protective relay settings. Relay settings are primarily dependent on [for overcurrent relays]

a. normal operational currents for which they should not trip

b. Fault currents [above normal operational currents] for which they should trip. This is independent of kA rating of the breaker and depends on system impedance. Also thermal withstand limits before which they should trip.

Typical industrial systems will have few levels of transformers and voltage levels and fault levels at lowest voltage level usually remain constant. The concern is only at the voltage level that is directly connected to the grid, where variation of fault level may influence the choice of ratings.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#13
In reply to #11

Re: Fault Current

09/04/2011 12:26 PM

I agree.

As far as "equipment selection/sizing" is concerned, it may be fair to a certain extent, to use conservative values. However, for "relay setting", as reqd. by OP, the co-ordination should satisfy for both 'Max'. as well as 'Min.' fault conditions.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#14
In reply to #13

Re: Fault Current

09/04/2011 1:00 PM

Referring to LV CBs only, 36 or 50 kA doesn't make any difference ... please step back and think .... this is CURRENT-LIMITING zone. A LVCB, seeing a 36kA(~70kA peak) or 50kA(105kA peak) fault, will start opening very, very rapidly.....long before any peak is reached.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#15
In reply to #14

Re: Fault Current

09/04/2011 1:43 PM

Again going back to #9, if the O/C relay is set to operate at 20 MVA (28 kA) 'conservative' fault current, it may not 'coordinate' properly for the 'actual' fault current of say 11.11 MVA (15 kA).

This is why, for relay setting, it is reqd. to do the setting at the actual fault current.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#16
In reply to #15

Re: Fault Current

09/05/2011 12:40 AM

We are not talking about the same thing obviously, so here is my final post on the subject of LV current-limiting circuit breakers, and their coordination....

Above 2400A in this case, the CB goes into "Reflex trip" mode, and operates irrespective of any setting on the relay.

Granted that i am only talking about one small part of the overall distribution system. Perhaps the OP is asking about 400kV systems, in which case, all my posts are not applicable.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Register to Reply 20 comments