Short Circuit Calculations for 2500A LV Switchgear Panel

11/05/2010 10:54 AM

Hi every one, Can I get a formal/standard short circuit calculations for 2500A switchgear panel in word format,I need to send it one of my client...I will appreciate if any one send it to me.

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#1

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/05/2010 11:14 AM

If it is energised you can do it.Measure the current(say 200A) and voltage(400A).Switch off the load and read the voltmeter(402V) quickly before the AVR restore the voltage. Now calculate as under: For a drop of 2V current required is 200A Then for a drop of 400V(SC conditions) current required=200x400/2=40000A=40kA(SC)

__________________
pnaban
Register to Reply
2
Guru
United States - Member - New Member

Join Date: Jun 2008
Location: Alabama
Posts: 1604
Good Answers: 63
#2

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/05/2010 2:20 PM
Register to Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/05/2010 10:15 PM

Good links. GA.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#4
In reply to #2

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/06/2010 5:36 AM

My method given under item 1-is it not accurate?.

__________________
pnaban
Register to Reply
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#6
In reply to #2

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/06/2010 11:59 AM

Thanks,,It is useful.....

i have calculated as below

FLA = 1500(kva)X1000 / 1.732X415(volt)X0.9 =2086A

Z=5%..... 100/5 = 20

KA = 2086X20

41720 Amps

Is it ok? actually I was searching a good format to send it one of my client.

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Anonymous Poster
#5

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/06/2010 11:06 AM

Your switchgear panel is in word format???...

Why did client need it?...Normally consultants need it........short circuit calculation is not for a panel...it is for the system...in this case up to this panel....where are the other details such as cable, transformer, distance, ...etc

Poor employer!!...Poor Client....but you enjoy life

Register to Reply Score 1 for Off Topic
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#7
In reply to #5

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/06/2010 12:00 PM

no thanks i dont want any help from u....cheers

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#8

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/07/2010 1:03 AM

http://www.east-med.schneider-electric.com/documents/electrical-distribution/en/shared/AMTED300014EN.pdf

http://www.bussmann.com/library/docs/spd02/SPDSection07.pdf

check the above links for formulas n notes. search cr4 for more info...

here are some examples.

1)The Transformer which is feeding the Panel is source of Short Circuit Current. To be in safer side the fault level is calculated by following formulae

Fault MVA = Base MVA / per unit impedance

Base MVA = Rating of Transformer feeding the Panel

Per unit impedance = Impedance of the transformer in % / 100

Note: All the impedance down line are ignored thereby adding to more safety.

Example :

Suppose the Transformer rating is 33/0.415 kV, 2000 kVA with Z = 7%

Fault MVA = 2/0.07 = 28.57 MVA

Fault Current = 28.57 / (1.732*0.415) = 40 kA (approx)

2)Short Circuit current is calculated depending on the percentage Impedance and line voltage. Line voltage( V L ) is multiplied by 1.1 to take carte of the 10 % rise in voltage and Z .

As an example , In 3 phase 1000KVA Transformer ( single ), 22/ 0.415 kV,

the % Z = 5.25 and

Short Circuit Current

...... 1.1 x V L

I = -----------

......... √ 3 x Z

The Impedance Z should be calculated in ohms

........→ % Z x 10 x kV2

Z = ----------------- say in this case 0.009 (calculated)

............→ kVA

..................................→ 1.1 x 415

Short circuit current I = ----------------- = 29.3 kA

. ................................√3 x 0.009

The 0.8 given is a derating factor depending on the heat dispensing of the enclosure considering the panel is installed in indoor in well-ventilated room.

__________________
shamith gambhir, electrical engineer
Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#9
In reply to #8

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/07/2010 1:06 AM
__________________
shamith gambhir, electrical engineer
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/08/2010 9:29 AM

Only by paying for it.

There is no facility in CR4 to send Word files electronically.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#11
In reply to #10

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/08/2010 9:51 AM

then I know how to make it in word

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Anonymous Poster
#12
In reply to #11

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/09/2010 12:24 AM

Lot of waste of space in your office!!!!!!

Register to Reply Score 1 for Off Topic
Commentator

Join Date: Oct 2009
Location: Dubai,UAE
Posts: 62
Good Answers: 2
#13
In reply to #12

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/09/2010 1:03 PM

hello masseera...:P

__________________
There are no shortcuts on the road to a great experience.
Register to Reply
Anonymous Poster
#14
In reply to #13

Re: Short Circuit Calculations for 2500A LV Switchgear Panel

11/20/2010 2:41 AM

Masseera di jai ho...........

Register to Reply
Register to Reply 14 comments

Good Answers:

These comments received enough positive votes to make them "good answers".