Dear all,

What is the difference between selecting a motor of 50 kW with Service factor of 1.5 or a motor of 75 kW with Service factor of 1.0?

Thanks in advance.

Register to Reply
Pathfinder Tags: Service Factor of Motor
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#1

Re: Service Factor of Induction Motor

09/05/2011 12:26 AM

we begin with the assumption that the rated voltage and frequency are maintained during operation.

you have not mentioned if the higher service factor consideration is because the motor will see only periodical overloads? or be continuously over loaded by 50%. your choice should be influenced by that information.

a 75kW motor running at full load has a defined life expectancy at service factor 1.0.

a 50kW motor running at full load has a defined life expectancy at service factor 1.0.

when a 50kW motor is used at service factor 1.5, it results in higher heat dissipation than a 50kW motor with service factor of 1.0.

therefore for this service factor the motor would have to be built in a larger size.

even after building the motor in a larger size it would still mean higher insulation stress and faster bearing wear.

Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#2
In reply to #1

Re: Service Factor of Induction Motor

09/05/2011 12:30 AM

more on subject . . . .

we generally select motors with higher service factors to run them "cooler than normal" and thereby improve insulation life expectancy.

we also apply higher service factors in cases where the motor runs in hostile environments.

if you wish to apply the stated conditions then you might do well to select a 75kW motor with a higher service factor than unity.

Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#3

Re: Service Factor of Induction Motor

09/05/2011 12:46 AM

"when a 50kW motor is used at service factor 1.5, it results in higher heat dissipation than a 50kW motor with service factor of 1.0."

In other words, it will work at 1.5 SF, but not far as long.

I'd order a 75 kW motor with a SF of 1.2.

Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#4

Re: Service Factor of Induction Motor

09/05/2011 4:01 AM

Answer given by Mr. soebfatehi very much explains your query. adding a further information, here is an extract from baldor.

Service Factor

Some motors carry a service factor other than 1.0. This means the motor can handle loads above the rated HP. A motor with a 1.15 service factor can handle a 15% overload, so a 10 HP motor with a 1.15 service factor can handle 11.5 HP of load. Standard open drip-proof motors have a 1.15 service factor. Standard TEFC motors have a 1.0 service factor, but most major motor manufacturers now provide TEFC motors with a 1.15 service factor.

The question often arises whether to use service factor in motor load calculations. In general, the best answer is that for good motor longevity, service factor should not be used for basic load calculations. By not loading the motor into the service factor, the motor can better withstand adverse conditions that occur. Adverse conditions include higher than normal ambient temperatures, low or high voltage, voltage imbalances, and occasional overload. These conditions are less likely to damage the motor or shorten its life if the motor is not loaded into its service factor in normal operation.

__________________
shamith gambhir, electrical engineer
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#5

Re: Service Factor of Induction Motor

09/05/2011 11:11 AM

If you know the meaning of service factor, you can decide which motor to select based on your need. See this link for motor service factor: http://cr4.globalspec.com/thread/54464/Service-Factor-of-Electrical-Motor

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru

Join Date: Nov 2006
Posts: 729
Good Answers: 2
#6

Re: Service Factor of Induction Motor

09/06/2011 9:27 AM

A study of loading conditions is required.If motor is likely to run at 50 kw most of the time but likely to get overloaded for 75 kw under some conditions then a 50KW motor with SF 1.5 is to be specified.Here the motor performance like EFF PF and temp rise over ambient will be designed for 50KW.If amotor is likely constantly operate at 75 kw then better to go in for a t 75 kw motor where all performance figs. will be designed considering 75 kw.When a motor is operating Service factor range the performance figures quoted for the rated conditions will not apply .In particular a higher temp. rise is permitted.SF 0f1.5 is normally not used.SF of 1.1,1.15or1.2 are normally used.You will find this mostly in varying load applications like reciprocating compressors where loads keep fluctuating.

__________________
To avoid crticism do nothing,say nothing,be nothing
Register to Reply Score 1 for Good Answer
Register to Reply 6 comments

"Almost" Good Answers: