Cable Gland in IIC Area for Exn Motor

09/05/2011 12:44 AM

Can IIA/IIB cable gland for IIC area for Exn motor?

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#1

Re: Cable Gland in IIC area for Exn motor

09/05/2011 3:29 AM
__________________
shamith gambhir, electrical engineer
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#2

Re: Cable Gland in IIC area for Exn motor

09/05/2011 4:02 AM

All types of cable glands can be used with Ex n.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Participant

Join Date: Sep 2011
Posts: 2
#3
In reply to #2

Re: Cable Gland in IIC area for Exn motor

09/05/2011 4:37 AM

motor is Exn.

It falls in IIC area

Can IIA/IIB gland used for this motor if IIC gland is unavailable.

What is technical difference between IIA/IIB & IIC gland.

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#4
In reply to #3

Re: Cable Gland in IIC area for Exn motor

09/05/2011 5:00 AM

Check out the Wikipedia page on Hazardous Area electrics.

Repeating the question suggests that the device isn't actually Ex n. Please state full details of the Ex n equipment including manufacturer and part number.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Power-User
India - Member - design engineer Engineering Fields - Electrical Engineering - New Member United Arab Emirates - Member - New Member

Join Date: Feb 2010
Location: dubai,mangalore,bangalore.....
Posts: 145
Good Answers: 8
#5
In reply to #3

Re: Cable Gland in IIC area for Exn motor

09/05/2011 5:50 AM
__________________
shamith gambhir, electrical engineer
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#6

Re: Cable Gland in IIC area for Exn motor

09/05/2011 6:31 AM

The worrying thing about hazardous area electrical equipment queries, is that the query indicates that the originator is working beyond the horizons of his/her training to date.

If in doubt, stop, and request suitable training.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#7

Re: Cable Gland in IIC Area for Exn Motor

09/05/2011 11:27 AM

You cannot use it in IIC classified area. The cable gland of gas group IIA or IIB are not suitable for the gas group of IIC (such as for Acetylene or hydrogen), so this cable gland will not protect the explosion of Acetylene or hydrogen coming out from the enclosure, and hence it is not safe.

This seems weird to me. I have never seen the explosion proof cable gland suitable only for gas group IIA and IIB. Generally, cable glands are suitable for all IIA, IIB and IIC. Here is the Hawke cable gland for classified area: http://www.ehawke.com/cableglands/753.html

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#8
In reply to #7

Re: Cable Gland in IIC Area for Exn Motor

08/23/2024 7:20 AM

The motor is stated as being <...Exn...>, though, therefore it doesn't have the capability of producing an <...explosion...> (doesn't sound right, though that is what the Original Poster has stated).

One might expect the terminals' enclosure to be at least Ex 'e' or Ex 'd':

  • No special precautions needed with Ex 'e'.
  • Ex 'd' cable glands are needed with an Ex 'd' motor terminal enclosure.

And:

  • Operatives designing, specifying, fitting and testing the equipment need special training, so that this type of question doesn't get asked.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856