Sanyo Air Conditioners 36,000 BTU - Not Restarting
09/05/2011 1:55 AM
Dear all,
We have installed three pieces of 36,000 BTU each in our server room, but sometimes they do not start automatically after electrical power return. Has any one expeperienced a similar problem?
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
If the conditions were already down to setpoint temperature and humidity upon restoration of power, there would be no need for them to restart at that time.
There might be a power-on delay timer as part of the control system.
__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
I vote for the delay timer. Most self-contained A/C units now employ a hermetically sealed cooling circuit and use a capillary tube instead of a metering valve. After the unit has shut down it should not be restarted until pressure on the high side (the condenser side) of the circuit drops enough to allow the compressor motor to start without stalling. This can take several minutes.
A motor stall in a hermetic unit can cause severe (and expensive) damage to the compressor. That start-delay timer may have saved you a big-ticket service call.
Re: Sanyo Air Conditioners 36,000 BTU - Not Restarting
09/18/2011 6:26 PM
The Air-conditioning Unit working and power goes, it will
not start immediately and there will be a delay time set to restart due to the
following reasons:
1.
Once Electrical Power Utility power goes.
Sometimes, Utility power comes and goes immediately till it stabilizes. It
takes some time. That may affect the compressor winding. So to stabilize
Electrical Power & to re-start AC unit compressor motor, the manufacturer
keeps the delay Time around 5minutes.
2.
Once power is witched on and compressor motor
develops the full torque high enough to push the piston in compressor to
develop high pressure at high pressure section of Air-condition Refrigeration cycle. If power goes or failure, motor will stop. After a few seconds power comes
back, Motor will not start due to low starting torque of the compressor motor
against high pressure of high pressure section of the Air-condition Refrigeration cycle or
as if compressor motor rotor were locked. Then motor would be in the state of Locked rotor condition and
motor would draw 6 times the full load current till motor would develop its full
torque. Prolong locked rotor current may burn or affect the motor winding.
Owing to this,
manufacturer keeps the delay time to re-start once power goes. During this
delay time (5minutes) High Pressure in the High
pressure section of the refrigeration cycle become very low pressure at
that time, motor re-stars with its starting torque that will be sufficient to
rotate the compressor motor shaft and pushes the pistons without going into Locked Rotor Current State that makes
the motor winding not being subjected to high current and winding life will be long.
Time delay to restart will be provided for Air-conditioning Unit
having BTU/hr around 36,000(3Ton) or above. But delay time will not be provided
to window AC Unit of 18,000Btu/hr (1.5Ton) or less.