Anonymous Poster #1

Instrument Earth Bar and Safety Earth Bar

09/06/2011 6:51 AM

Hi All,

I am working on a system cabinet of certain PLC.

It has istrument and earth bar mounted at the bottom as required for earthing.

The difference i noticed was, istrument earth bar has one rubber stand between its two bars and safety earth does not have this. I wanted to know the reason behind this.

Reply
Pathfinder Tags: instrument earth bar
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
4
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Instrument earth bar and safety earth bar

09/06/2011 7:00 AM

The safety earth is subject to eddy currents, leak currents and occasional fault currents. The instrument earth ideally needs to be immune to these, so it is generally isolated at the panel and connected to the main earthing point with a separate bonding cable to that place.

Safety earth is sometimes called "dirty" earth and instrument earth "clean" earth for that reason.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply Good Answer (Score 4)
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#4
In reply to #1

Re: Instrument earth bar and safety earth bar

09/06/2011 11:54 PM

@ PWSlack . . . don't the two (clean and dirty) then go to the same earth (even if through separate pits)?

since i often like your answers, i am tempted to ask many questions to you . . . to help demystify some "ground" realities on this subject . . . with assumed permission, i submit . . .

in case there is a direct lightning strike in the vicinity and the EARTH rises to a very high potential . . . then will not both the earths rise almost equally? in such a case what is the use of the isolation of the "clean" earth inside the panel?

why only lightning strike? even in the case of a direct flashover from line to earth at a near to source point of low impedance, may a similar risk be perceived?

if the two earth are indeed to be isolated then should the instrument earth have a resistance built in series? to limit the current?

if the instrument aux supply is derived from the same source as the panel power supply without any isolation transformer in between then does having a separate earth bus bring any advantage? or disadvantage?

Reply Score 1 for Good Answer
Guru

Join Date: Dec 2005
Posts: 1602
Good Answers: 19
#6
In reply to #4

Re: Instrument earth bar and safety earth bar

09/07/2011 8:47 AM

I give you a GA, not because you provide a good answer, but because of the good questions you raise!

I'm a graying mechanical engineer and have often seen "clean" ground and "dirty" grounds in communications shelters. I have not completely understood why and have just accepted the practice.

This post supplies several great replies that have given me a better background to understand why. But like sobefatehi, I am curious how the clean and dirty grounds are kept "separate", even though they both are ultimately have only 5 or 10 ohms resistance between them?

And to the poster who mentioned putting an impedance on the ground connection, what size and configuration is this coil? (Is it a coil?)

__________________
Eventually, one needs to realize that it is far less important to be the smartest person in the room than it is to sit next to that person and make friends.
Reply Score 1 for Good Answer
Guru

Join Date: May 2010
Location: Metro.Manila, Philippines.
Posts: 1271
Good Answers: 27
#7
In reply to #6

Re: Instrument earth bar and safety earth bar

09/07/2011 11:51 AM

IMO, there is always going to be a Finite amount of impedance differences in any form of grounding or earthing mechanism(s). This holds true for both of the so-called "clean" and "dirty" grounds /earths. Regardless of how well the bondings are made, different ground loops will always exist due to this finite amount of differences in ground impedances. Minimizing ground loops differences will help improve or minimized this ground noises up to a certain acceptable level..

__________________
vsar
Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Not a New Member Hobbies - Musician - New Member Hobbies - Fishing - New Member

Join Date: May 2006
Location: Reading, Berkshire, UK. Going under cover.
Posts: 9684
Good Answers: 468
#2

Re: Instrument Earth Bar and Safety Earth Bar

09/06/2011 7:53 AM

Further to #1, in some labs the instrument earth is connected to its own earth mat or pit or whatever to ensure that it's as "quiet" as possible.

__________________
"Love justice, you who rule the world" - Dante Alighieri
Reply
Power-User

Join Date: Jun 2008
Location: beverly hills
Posts: 116
#3

Re: Instrument Earth Bar and Safety Earth Bar

09/06/2011 8:25 AM

Hi All,

In our Petrochemical plant, Clean earth & Safety Earth install seperately.

Thanks

Reply Score 1 for Good Answer
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Nov 2009
Location: Abuja, Nigeria.
Posts: 126
#5

Re: Instrument Earth Bar and Safety Earth Bar

09/07/2011 4:30 AM

The answer is correct to an extent and the argument is also correct since the reason for providing separate earthing points in the panel is to allow for separate earthing; they can not be bonded together for any reason. They should be separately earthed. If for any reason they want to communicate or shake hands, it must be through a ground impedance.

__________________
There is peace in silence and achievement in plans.
Reply
Reply to Forum Thread 7 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

Dickson (1); JohnDG (1); PWSlack (1); Ried (1); ronron (1); soebfatehi (1); vsar (1)

Previous in Forum: Thermocouple Errors - What to Expect?   Next in Forum: Cable Tray and Pipe Radius

Advertisement