Earth Fault

09/08/2011 12:54 AM

what is the main reason behind putting the setting of E/F lower than all others fault? that is 10-40%

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Earth Fault

09/08/2011 3:53 AM

Er, because it doesn't need to be any higher, perhaps?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#2

Re: Earth Fault

09/08/2011 5:00 AM

If you've got an earth fault you want the quickest disconnection. Overload can be tolerated for short periods, hence the higher settings.

__________________
The reports of my death are greatly exaggerated.
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#3

Re: Earth Fault

09/08/2011 9:48 AM

Two Reasons:

i) First and foremost is human safety! Even a small earth fault current can create dangerous touch voltages to be developed on exposed and/or extraneous conductive parts, thereby endangering a human life. So, it is imperative that the earth fault protective setting is kept as low as possible. The 10 to 40% setting normally given is for giving due allowance for the system unbalance current - which can occur due to normal load operating conditions too (due to unequal distribution and/or utilisation of single phase loads spread across the three phases) - particularly, if the earth fault relay is wired in the residual path of the phase CTs.

ii) Second is economical! Any earthfault current is drained into the earth without doing any useful work. You wouldn't want to continue draining costly electricity! Would you?

Register to Reply
Associate

Join Date: Aug 2011
Location: India
Posts: 29
Good Answers: 2
#4

Re: Earth Fault

09/08/2011 1:38 PM

Just to add to above, a Ph-Ph fault current flows through conductors intended for actually carrying currents, while a Ph-E fault may also flow through those 'conductors !!!' which are not intended for actually carrying currents & thus Ph-E fault needs to be isolated at lower current values than other faults such as Ph-Ph fault.