Neutral Transformer Protection

09/12/2011 3:45 AM

Dear all,

I have three windings transformer 20/0.38 kV, Dyn5/Dd0, 2500 kVA, and the client want to get it protected from it's neutral sensing.

What is the advantage/disadvantage to get the neutral from the primary or the secondary side?

Thank you in advance.

Regards.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: Neutral Transformer Protection

09/12/2011 4:34 AM

Er, perhaps there is no neutral on the secondary?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#2
In reply to #1

Re: Neutral Transformer Protection

09/12/2011 4:54 AM

The primary transformer is Delta, and one of the secondary is also Delta.

That means I have to provide a ZCT either on primary or secondary for the 50N and 51N protection right?

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3
In reply to #2

Re: Neutral Transformer Protection

09/12/2011 5:05 AM

Why not ask the Client?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#4
In reply to #2

Re: Neutral Transformer Protection

09/12/2011 7:37 AM

I am afraid that your terminology is incorrect. In the Primary Delta as well as in the secondary delta, there cannot be any neutral and hence there cannot alos be neutral protection. I assume that you want protection against earth faults in the delta side. If so, this can be easily acheived by connecting a sensitive earth fault realy in a residual connection of the phase CTs or a CBCT or go for a relay which can provide earth fault protection with zero sequence sensing.

Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#6
In reply to #4

Re: Neutral Transformer Protection

09/13/2011 11:21 PM

@electricalexpert65:

You are right, that's what I meant for the protection. Then agan, what is the difference, for example, regarding the sensitivity etc, if I put the CT on the primary or on the secondary? Or I can just put it on the primary side, compare to providing 2 sets of CT on the secondary?

Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#7
In reply to #4

Re: Neutral Transformer Protection

09/14/2011 12:57 AM

Does earth fault current exist when both sides are Delta?

We may need two simultaneous earth faults to get fault currents !!!

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#5

Re: Neutral Transformer Protection

09/13/2011 12:03 AM

OP actually says 3 winding transformer. May be it is actually D/Yn/d with secondary Y.

In this case the star side can have neutral - 51N relays.

If both primary , secondary are D, no neutral current exist as there is no path for the same.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply
Commentator

Join Date: May 2011
Posts: 80
#8
In reply to #5

Re: Neutral Transformer Protection

09/14/2011 3:29 AM

@raghunath7

Actually its a 3 winding transformer to feed 12 pulse drive. So the vector group on the secondary are D and Y.

Register to Reply
Power-User

Join Date: Apr 2011
Location: Bengaluru, India
Posts: 128
Good Answers: 3
#9
In reply to #8

Re: Neutral Transformer Protection

09/14/2011 4:02 AM

Assuming your source end on primary side is grounded, you can measure the neutral current on the source side [Delta - Primary] for earth fault location from the source end CT's to Primary Delta winding location.

Again you can measure secondary Yn side neutral current using CT's for earth faults on Yn side for faults from the secondary Yn CT locations to the load supplied.

However, you cannot measure the earth fault current on the other secondary Delta side, unless you intentionally ground this second delta winding on secondary side.

__________________
Dr.Raghunatha Ramaswamy - We discover nothing new other than knowledge
Register to Reply