Aluminum Busbar Support Distances - LV Switchboards

09/12/2011 3:59 AM

I would like some assistance/direction in locating a set of tables/calculations that relate to aluminium busbar design in LV (415-1000V 50Hz AC) switchboards. This arrangement is a rare occurrence (all copper busbars) in Australia hence the lack of local knowledge. I have already located information relating to temperature rise, however busbar support distances are my present concern. This is not a specific application enquiry but more of a attempt at an impartial comparison between copper and aluminium in these applications.

Register to Reply
Pathfinder Tags: aluminium busbar Busbar Support
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#1

Re: Aluminium Busbar Support Distances - LV Switchboards

09/12/2011 4:48 AM

for copper busbars - read COPPER FOR BUSBARS - download from ICA website . . .

Register to Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#2

Re: Aluminium Busbar Support Distances - LV Switchboards

09/12/2011 7:34 AM

The distance between bus bar supports is calculated on the basis of the total stress acting on the bus bar conductors during a short circuit. If the bus bar has more 0.2% Proof Strength, like that of Coppoer bus bar, the insulator support span can be more. Whereas in case of Aluminium, the support span shall be reduced, as the 0.2 % proof strength of Aluminium is much lesser.

Firts of all you have to calculate the total stress acting on the bus bar conductors (both main conductor stress & the sub-conductor stress), then check if this is less than the 0.2% proof strength of the bus bar material chosen. If not, either change the bus bar material grade or reduce the stress by many menas, one of which is reducing the support span.

Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#3

Re: Aluminum Busbar Support Distances - LV Switchboards

09/13/2011 12:24 AM

Did you check the IEC standard for LV switchboards, form 1,2 etc?. If not mentioned there send the SC level,size of busbar etc to manufacturer of busbar and ask for their recommendations.

__________________
pnaban
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#4

Re: Aluminum Busbar Support Distances - LV Switchboards

09/13/2011 12:27 AM

You might have studied these already, if not ....

Schneider Electric's ECT 162,145,186 and 156 may give you some help. PDFs available from Schneider website.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Participant

Join Date: Sep 2011
Posts: 4
#5

Re: Aluminum Busbar Support Distances - LV Switchboards

09/13/2011 1:03 AM

Sir,

Deciding support distance/phase to phase center to center distance depends on the Short circuit current that the switch board has to cater.Based on this the calculation is to be made.It shall be same for aluminium or copper bus.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #5

Re: Aluminum Busbar Support Distances - LV Switchboards

09/13/2011 1:35 AM

Are you sure? Aluminium being somewhat weaker than copper, so would need more supports (that is, space between supports should be smaller than for copper)?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#7
In reply to #6

Re: Aluminum Busbar Support Distances - LV Switchboards

09/13/2011 3:00 AM

Can you quote from the relevant IEC standard?.

__________________
pnaban
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#9
In reply to #7

Re: Aluminum Busbar Support Distances - LV Switchboards

09/13/2011 3:59 AM

IEC 61439 and all its parts are under revision. i have no access to them.

However, support spacing depends on design and will vary from one manufacturer to another. So, i doubt if IEC can lay down any detailed specs. The proof of the pudding is in the eating it is said, so the Icw test is the final proof.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#8
In reply to #5

Re: Aluminum Busbar Support Distances - LV Switchboards

09/13/2011 3:06 AM

For the same current rating, aluminium and copper busbar sizes cannot be the same. As the mechanical strength of copper and aluminium are also different, support distances and phase to phase/Earth clearance also should be different. To support your view can you quote some standard or code?.

__________________
pnaban
Register to Reply