NEC Requirement for Motor Control Circuit

09/19/2011 5:20 PM

Hi,

I understand that NEC required a motor control station within sight of the motor. The question I have is, does the control station have to break the control circuit directly? Does the NEC allow the switch to send the signal to the DCS and the DCS will stops the motor? Thanks in advance.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#1

Re: NEC Requirement for Motor Control Circuit

09/19/2011 6:47 PM

The NEC says no such thing. Don't know wherre you got that from, but it was incorrect. If you want help, please describe your entire situation.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
2
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2

Re: NEC Requirement for Motor Control Circuit

09/19/2011 9:57 PM

NEC (2008) 430.102 (A) states "An individual disconnecting means shall be provided for each controller and shall disconnect the controller. The disconnecting means shall be located in sight from the controller location"

and 430.102 (B)(2) states "The controller disconnecting means required in accordance with 430.102(A) shall be permitted to serve as the disconnecting means for the motor if it is in sight from the motor location and the driven machinery location.

This means that the motor control station must be located within the sight of the motor. It doesn't matter the control station is directly disconnects the motor or disconnects it through the DCS or PLC system.

In the case of the motor is fully operated by automated system (no manual control station), there must have a disconnect switch in the motor power line within the sight of the motor per 430.102 (B)(1) "A disconnecting means for the motor shall be located in sight from the motor location and the driven machinery location".

Hope it helps.

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply Good Answer (Score 2)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#3
In reply to #2

Re: NEC Requirement for Motor Control Circuit

09/20/2011 1:01 AM

Good information. Makes sense. i think US customers and maybe NEC prefer devices like this one, with the blades visibly open when OFF ?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Anonymous Poster #1
#4
In reply to #3

Re

09/20/2011 1:54 AM

.

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#5
In reply to #4

Re: Re

09/20/2011 2:31 AM

?

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#27
In reply to #3

Re: NEC Requirement for Motor Control Circuit

09/21/2011 11:08 AM

US customers and maybe NEC prefer devices...

No. Because of OSHA requirements,such cabinets can never be open, and therefore only the handle can indicate the on/off status.

__________________
Think big. Drive small.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#6
In reply to #2

Re: NEC Requirement for Motor Control Circuit

09/20/2011 7:15 AM

No it means that the disconnect for the controller applies to the one necessary for the motor if it is with in site of both. If both the controller and the motor are not with in site of each other. Then a disconnect means have to be provided for both.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#11
In reply to #6

Re: NEC Requirement for Motor Control Circuit

09/20/2011 11:05 AM

Also the disconnect does not have to be in site of the motor or equipment. As long as the disconnect can be locked in the open position.

It's a good idea in practice though to set it with in site.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#7

Re: NEC Requirement for Motor Control Circuit

09/20/2011 9:29 AM

"I understand that NEC required a motor control station within sight of the motor. The question I have is, does the control station have to break the control circuit directly? Does the NEC allow the switch to send the signal to the DCS and the DCS will stops the motor? "

Control station and disconnect are NOT the same thing. He is referring to a control circuit issue, to which there is no NEC requirement. He may have been mixing up the issues in his mind, but that reference to the LOTO disconnect, however useful, does not actually answer the question he asked.

(msamad and kkvsridhar; no offense meant to your responses, I'm being pedantic because I get tired of people not knowing how to ask a question and then getting the wrong answer)

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#8
In reply to #7

Re: NEC Requirement for Motor Control Circuit

09/20/2011 9:50 AM

Oh, no offence taken of course

Such debates actually enrich a layman's (me ) knowledge even if the original post is inane (i am not saying this one is, OP). It is an academic thing for me since i live in an IEC country. i felt that US standards are oriented towards the user (since UL wants the safest stuff for people) while IEC's decision makers come from Industry. i have seen some small vested interest situations in the BIS meetings which i attended. The customer definitely took a second place.

So it was refreshing to see things like a safety switch with visible isolation in sight of the motor one time when i was in the USA. When one is next to piece of machinery which is going nuts, one looks frantically for an emergency switch whose handle one can pull to shut off the darned thing.... NEC or not

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#9
In reply to #8

Re: NEC Requirement for Motor Control Circuit

09/20/2011 10:24 AM

fyi KVS - your live in a country where NEC2011 has been released by BIS . . .

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#12
In reply to #9

Re: NEC Requirement for Motor Control Circuit

09/20/2011 11:14 AM

So, is this US code based? i am afraid i don't own any Standards nor Codes.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#13
In reply to #12

Re: NEC Requirement for Motor Control Circuit

09/20/2011 11:20 AM

NEC 2011 is for India just like its predecessor NEC 1985 was . . . . all installations will align with NEC 2011 as it gets adopted and harmonized with local supply rules and building rules . . . difficulty is the high variance between building rules in different municipalities and states . . . we are trying through our trade organisations and professional institutions to bring down variance . . . hope to use support from all industry, trade and consumer quarters . . .

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#14
In reply to #13

Re: NEC Requirement for Motor Control Circuit

09/20/2011 11:36 AM

Ah, i see.

Anyway, the NEC of USA specified (as my American friends told me in 1982) that (a) Safety switches are to be used as emergency switch-off devices, and should have visible open gap between moving and fixed contacts, and (b) every moving machinery should have an emergency switch within sight.

i thought this was an excellent rule. i can't say whether what my American friends told me was true or not.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#17
In reply to #14

Re: NEC Requirement for Motor Control Circuit

09/20/2011 3:01 PM

There is a difference between a emergency shut off switch and a disconnect.

The device you describe is a disconnect it is there for service to the device. The emergency shut off switch which is usually on the control panel just stops the device. Not that the disconnect can't be used in an emergency. But the emergency stop switch should not be used for service.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#18
In reply to #17

Re: NEC Requirement for Motor Control Circuit

09/20/2011 11:01 PM

In IEC, the device is called a "Switch-disconnector". The "switch" means that the device can open a circuit at an overcurrent level higher than LRA. The "disconnector" means that it is also capable of providing safe isolation. In other words, such a device can be used as a "disconnect" when attending to maintenance on the downstream equipment. (Such maintenance is done when the motor starter is in the Off condition anyway), and is capable of switching off a substantial overcurrent in an emergency.

Such European devices are being used in USA nowadays, through ABB and Socomec who are branding their products for Cooper Bussmann and Ferraz Shawmut.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#25
In reply to #18

Re: NEC Requirement for Motor Control Circuit

09/21/2011 10:17 AM

Spent a few years installing those devices. Here they are referred to as a service disconnect. They can be with or without overload protection. Have been used for at least the last 40 years I know of nothing new. Maybe longer the gas station in worked in as a teenager had them on the wall for all the pumps. The station had been there before I was born.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Power-User

Join Date: Dec 2010
Posts: 166
Good Answers: 4
#30
In reply to #14

Re: NEC Requirement for Motor Control Circuit

09/21/2011 11:35 AM

Do not confuse an emergency switch with a disconnect switch. An emergency stop switch causes the control circuit to drop out, stopping all machinery in the process/line. A disconnect switch prevents power from getting to a specific motor regardless of what the control system wants it to do.

Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#29
In reply to #8

Re: NEC Requirement for Motor Control Circuit

09/21/2011 11:26 AM

When one is next to piece of machinery which is going nuts, one looks frantically for an emergency switch whose handle one can pull to shut off the darned thing.... NEC or not


An "E-stop" (emergency stop control rope or button) is what one should be looking for* to quickly stop machine motion. These are wired into the control circuits and not related to the disconnect switches. Often, the disconnect switch cannot be reached quickly enough if someone is being sucked into a machine. The disconnect switch is there for lockout-tagout purposes, not to stop a motor in an emergency.


Disconnect switches are typically not equipped with arc quenching provisions, so should not be operated with the motor under load.


* (and actually should already have looked -- if you are working near a machine, you should know the location of the e-stops, and as an operator should have tested them at the start of your shift.)

__________________
Think big. Drive small.
Register to Reply
Associate

Join Date: Sep 2011
Location: Ontario
Posts: 52
Good Answers: 2
#37
In reply to #8

Re: NEC Requirement for Motor Control Circuit

10/03/2011 2:43 PM

Hi kvsridhar

"When one is next to piece of machinery which is going nuts, one looks frantically for an emergency switch whose handle one can pull to shut off the darned thing.... NEC or not"

Opening a disconnect switch, like the one in your earlier picture, under load may or may not result in an explosion and injury to the operator depending upon how fast he pulls and the exact moment in the AC cycle.

The only safe way of shutting off heavy electrical loads is via the circuit breaker, operated either via the control station or by the stop button on its cubicle.

In powerstations and other places, where the operators are in the control room, there will also be a control switch on or nearby the equipment in the field, which can send a signal to the control circuit and open the circuit breaker - that is the one to use for emergency shut-off.

By the way, it is true a disconnect switch box can not be left open so the blades can be observed, but when isolating for work protection the procedure is to open the box to verify all the blades are open and the switch is otherwise in good condition before closing the box and locking and tagging the handle in the open position.

Hope this clarified your understanding.

__________________
Fools rush in where wise men fear to go...
Register to Reply Off Topic (Score 5)
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#38
In reply to #37

Re: NEC Requirement for Motor Control Circuit

10/03/2011 10:50 PM

Thank you (Fry and Far). As i have worked all my life on IEC-based products, the usual disclaimer about my ignorance of US practice.

However, some home truths about IEC disconnects :

1.The products are quick-make, quick-break. They do not depend on the speed with which the operator pulls the handle.

2. They have to be tested to make/break 10 times the rated current. The twilight zone between normal load and the high-short-circuit zone (which will be handled by the fuse.)

3. Circuit breakers are meant mainly for short-circuit sensing and tripping. A yellow/red emergency stop button opens a tiny aux contact and gives a trip command to the circuit breaker. In the rare event of that tiny piece of brass being welded shut, the CB does not get any trip command. The power-interrupting-manual-disconnect is analogous to the power limit switch on a crane which will force stop the crane if all else fails, by directly interrupting the motor current.

Anyway, as i said, i am learning about US practices here, and thank you for your inputs.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply Off Topic (Score 5)
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#10

Re: NEC Requirement for Motor Control Circuit

09/20/2011 10:59 AM

In the UK, any requirement for an isolator at or near the motor will break the control circuit first, then break the phases to the motor pending the fitting of a padlock. If fitted, an emergency-stop pushbutton will be wired in series in the control circuit.

There is no requirement on pushbutton stations' locations. Any number of installations simply don't have them.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#15

Re: NEC Requirement for Motor Control Circuit

09/20/2011 1:11 PM

As ozzb said, there are acceptable exceptions to the rule, but it is still considered a "best practice" to put a disconnect withion sight. Also, the rules originally came from OSHA, the Occupational Safety Hazards Association that was involved in "enforcement" of safety standards, but was rendered toothless under the Bush Administration. So in 2005, the NEC adopted the same rules to make it enforeceable at the local electrical inspector's level. Technically though, if an end user fails to have a LOTO (Lock-Out-Tag-Out) disconnect device within sight of the motor, and does not prove that one of the exceptions applies, then OSHA can fine them even if an electrical inspector allowed it. Thirdly, there is another code similar to the NEC (which is technically the NFPA 70), called the NFPA 79 which specifically covers machinery safety issues and can be enforced by the local fire marshals, who may or may not accept the exceptions allowed by the NEC or OSHA. So with the potential of getting dinged by 3 separate agencies, most people are loathe to take the chance just to avoid the slight increase in installed cost to put in a LOTO device. Hence the "best practice".

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Guru
Hobbies - Fishing - Old Salt Hobbies - CNC - New Member United States - US - Statue of Liberty - New Member

Join Date: Mar 2007
Location: Rosedale, Maryland USA
Posts: 5197
Good Answers: 266
#16
In reply to #15

Re: NEC Requirement for Motor Control Circuit

09/20/2011 1:35 PM

I'd like it better if it said with in site and throwing distance of the tools at hand.

__________________
Life is not a journey to the grave with the intention of arriving in a pretty, pristine body but rather to come sliding in sideways, all used up and exclaiming, "Wow, what a ride!"
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#19

Re: NEC Requirement for Motor Control Circuit

09/20/2011 11:15 PM

Generally an emergency stop button(big red top) to stop the machine should be near the machine operator. Also an isolating switch should be near the motor(in sight) after the starter, to isolate motor/machine for maintenance so that nobody can switch it on. Then a question arises- when the starter is under maintenance and if the electrician normally switch off the circuit from the switchboard if switchboard is not in sight from the starter can someone switch the breaker on?. Do we need another isolator before the starter?. Is a notice "danger,do not switch on" on the breaker sufficient if it is not lockable?. What does the regulations say?.

__________________
pnaban
Register to Reply
Commentator

Join Date: Jun 2011
Posts: 67
Good Answers: 2
#20
In reply to #19

Re: NEC Requirement for Motor Control Circuit

09/20/2011 11:43 PM

Can a lockable mushroom head emergency off push button located next to the motor be used in place of switch disconnector/ disconnector/LOTO placed in visible location to motor?

Register to Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#21
In reply to #20

Re: NEC Requirement for Motor Control Circuit

09/21/2011 12:02 AM

A big, yellow/red emergency pushbutton can still interrupt only the control circuit. Never the power circuit. If the contactor contacts have welded shut, nothing happens. Motor keeps on getting supply. A manual, visible blade safety switch is the best.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Register to Reply
Associate

Join Date: Sep 2011
Location: Ontario
Posts: 52
Good Answers: 2
#33
In reply to #21

Re: NEC Requirement for Motor Control Circuit

09/22/2011 1:35 AM

A manual disconnect switch with open blades and no arc quenching is dangerous to operate with the motor under load, it can blow the enclosure open and start a fire or electrocute the person pulling the handle.

__________________
Fools rush in where wise men fear to go...
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#32
In reply to #20

Re: NEC Requirement for Motor Control Circuit

09/21/2011 12:00 PM

No!

__________________
Think big. Drive small.
Register to Reply
Guru

Join Date: Feb 2009
Location: West Coxsackie, NY
Posts: 533
Good Answers: 10
#22

Re: NEC Requirement for Motor Control Circuit

09/21/2011 2:30 AM

MSAMAD hit this one very nice! 3 years ago we were given a task of adding an AC drive to a conveyor system in a cement plant on their feeder system to the barges.

We arrived, MCC bucket was locked out/tagged out. Machine was also locked out tagged out. (Or we thought.) We did the drive install, which also meant changing several items on the machine motors, adding encoders, changing limit switches, adding various sensors and coupling therm all to the drive and the DCS system.

Start up, machine did nothing... Spent days testing. Days later guys complaining a system in the middle of the line has been acting up and dumping product on the belt blocking it.

We finally realized the Lockout/tag-out was the wrong MCC bucket, the machine we were working on was Live 480 3Ph and could have been active at any time via the DCS system. Could have been much worse since most of their equipment was all 4160 3Ph. Luckily nothing happened electrically bad.

Also, the machine was on the 2nd floor, MCC was on first floor and maybe 300 feet away. No disconnects, no E-Stops to be seen. Actual machine controlled by New VFD, 1900 feet away from MCC Bucket.

Value of lesson: ALWAYS CHECK LO/TO! Never ever take anyone's word for granted especially if it comes from an engineer!

I still say, all engineers must work at least 3 years in the field before they sit behind that desk and dictate what takes place in the field with those CAD DWG's and what ever else they say! Got to have that hands on!!

__________________
"Real Bass Players" do not use picks
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#31
In reply to #22

Re: NEC Requirement for Motor Control Circuit

09/21/2011 11:58 AM

It is worth noting that even if you had "checked" the LOTO status, you would still not be in compliance. If you are working on a machine your locks must be on the disconnects.

If working under group LOTO rules, then the keys for the various disconnect locks must be locked in a cabinet that is locked with all the individual locks of the workers, so that access to the keys cannot be obtained without each worker removing his lock.

Part of the LOTO process is to test* that the machine (or part of it you are working on) is in fact dead. In many companies, failure to do so gets you fired... if not killed.

* Unfortunately, in many companies and in many contracting outfits, the workers are clueless re how to test. Too many assume that because the motor does not start when the start button is pressed, that they have turned off the correct disconnect. Perhaps they have only turned off the control circuit.

__________________
Think big. Drive small.
Register to Reply Score 1 for Good Answer
Power-User

Join Date: Sep 2011
Location: Near the New Madrid Fault. USA
Posts: 269
Good Answers: 1
#23

Re: NEC Requirement for Motor Control Circuit

09/21/2011 8:17 AM

No, just a disconnect that opens the power circuit so it can be safely locked out.

__________________
It's not Rocket Science
Register to Reply
Guru

Join Date: Jun 2010
Location: srilanka
Posts: 2725
Good Answers: 5
#26
In reply to #23

Re: NEC Requirement for Motor Control Circuit

09/21/2011 11:00 AM

In addition an emergency pushbutton with mushroom head near the machine operator is essential.

__________________
pnaban
Register to Reply
Associate

Join Date: Sep 2011
Location: Ontario
Posts: 52
Good Answers: 2
#34
In reply to #26

Re: NEC Requirement for Motor Control Circuit

09/22/2011 1:45 AM

The purpose of the emergency stop pushbutton is only to save the machinery from self destruct. Workers should be protected by physical and procedural bariers.

__________________
Fools rush in where wise men fear to go...
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#36
In reply to #34

Re: NEC Requirement for Motor Control Circuit

09/22/2011 12:50 PM

In most jurisdictions, this is not true. Many machines are equipped with emergency stop buttons (and ropes, belly bars, etc) that perform a safety function. The regulations come from many sources and for many reasons, but there are many machines that cannot be so thoroughly guarded as to eliminate the possibility of operator injury (or injury of bystanders). Many lives have been saved (and injuries avoided or lessened) by rapid use of e-stop buttons.

__________________
Think big. Drive small.
Register to Reply
Anonymous Poster #2
#24

Re: NEC Requirement for Motor Control Circuit

09/21/2011 9:16 AM

You are getting so many different answers from many people. Some are close. Some are right, and some are just dead wrong. I think you should consult a locally licensed electrical Professional Engineer to get the straight story. He can inspect your situation and advise you best.

Register to Reply
Power-User

Join Date: Dec 2010
Posts: 166
Good Answers: 4
#28

Re: NEC Requirement for Motor Control Circuit

09/21/2011 11:25 AM

The NEC requires a Disconnect switch within sight of the machine. This is so that someone working on the machine will not be injured by an unanticipated start-up. If not within sight of the apparatus the disconnect must also accept a padlock to prevent some well-meaning idiot from starting it and removing your (insert appropriate body part here).

Register to Reply
Commentator

Join Date: Jun 2011
Posts: 67
Good Answers: 2
#39
In reply to #28

Re: NEC Requirement for Motor Control Circuit

10/04/2011 12:25 AM

To sum up, a good practice will be to have a lockable disconnect switch with visible blades in sight of the machine. In addition an auxiliary switch from this disconnect feeding back to MCC thereby interlocking the starter. Further a mushroom head emergency stop button near the machine for fast action if the machine has to be switched off in a hurry.

Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#35

Re: NEC Requirement for Motor Control Circuit

09/22/2011 12:49 PM

The OP is long absent and the rest of us are like the fabled group of blind men arguing over the description of an elephant by examining only the one part we can touch...

This subject has way too many variations to be determined from afar in a general way, there is no grand unifying rule.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply Score 1 for Good Answer
Register to Reply 39 comments

Good Answers:

These comments received enough positive votes to make them "good answers".

"Almost" Good Answers: