Earth Resistance

09/22/2011 2:08 AM

Hello All,

We just measured the earth resistance in plant and found 0.22 Ohm. Transformers atr 1.5 MVA. I would like to ask where this reading falls in the range? Too good or in mid?

And what if these transformers were replaced by 3 MVA, would same earthing 0.22 be suitable?

Thank You!!

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Earth resistance

09/22/2011 3:24 AM

WHAT VOLTAGE? (Sorry for shouting, but this is another electrical question lacking key data.)

[Is there such a thing as a "too good" (excessively low) earth resistance value?]

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply Score 1 for Good Answer
Member

Join Date: Nov 2010
Posts: 7
#2
In reply to #1

Re: Earth resistance

09/22/2011 3:31 AM

no need to shout !! yes it is essential data and missing just working inside one factory for 9 years made me think of the 11KV/ 380 to be only voltage level

sorry for that!!

Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#3

Re: Earth resistance

09/22/2011 4:01 AM

The earthing needs to be sufficient to operate the circuit protective device(s) without damage to the equipment or cabling.

Next!

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Register to Reply
Guru

Join Date: Oct 2008
Posts: 42355
Good Answers: 1693
#4

Re: Earth Resistance

09/22/2011 9:16 AM

Tell us, please, what do you think of this value? Surly you have some thoughts on the subject?

Your omission of critical information, and the question itself, lead me to believe that you are in the wrong line of work.

Register to Reply
Guru
New Zealand - Member - Kiwi Popular Science - Weaponology - New Member Engineering Fields - Power Engineering - New Member Engineering Fields - Electrical Engineering - New Member

Join Date: Sep 2006
Location: Auckland, New Zealand
Posts: 8777
Good Answers: 376
#5

Re: Earth Resistance

09/22/2011 3:54 PM

0.22 ohms seems a bit too high, perhaps you should run another plant in parallel to halve the value.

(Couldn't resist. Hey it's down Friday here).

On a serious note, what electrical standard are you working to? I would have thought the earth resistance limits for your particular application would be in there.

The value itself is a little misleading as you don't say where you measured the resistance (distance does play a factor generally, but it depends a bit on what standard your are working to) or what the resistance was previously (if the resistance has jumped since the previous reading it could indicate a potential problem with your earthing integrity, which is a problem).

Can you provide more information including plant location?

And what if these transformers were replaced by 3 MVA, would same earthing 0.22 be suitable?

This statement is worrying as the way I read it (in the context you have used it in) it seems you may not understand how transformers and protective earthing systems work.

Again, can you provide more information please.

__________________
jack of all trades
Register to Reply
Guru

Join Date: Jan 2008
Posts: 1753
Good Answers: 59
#6

Re: Earth Resistance

09/23/2011 12:39 AM

Earth resistance is not a fixed value, that you can measure with any precision. It varies with the seasons, with the moisture in the ground. The protection ought to work at any time. Getting thru certification is an entirely different matter, isn't it?

Register to Reply
Participant

Join Date: Sep 2011
Posts: 1
#7

Re: Earth Resistance

09/23/2011 6:44 AM

A 0.22 Ohm result is very very good irrespective of equipment. I refer to the xformer

Register to Reply Score 1 for Good Answer
Associate

Join Date: Jun 2011
Location: ROUEN (in NORMANDY), 120 km from Paris, France, Europe, Earth, Sun Sytem, Milky Way, Universe.
Posts: 39
Good Answers: 3
#8

Re: Earth Resistance

09/23/2011 1:11 PM

Yes to both questions. Your values are even good for an electronic earth. Congratulations, BRZK

__________________
That's all, Folks. Take some time to learn where you live...
Register to Reply Score 1 for Good Answer
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#10
In reply to #8

Re: Earth Resistance

09/25/2011 12:05 PM

What is this electronic earth? As per IEEE 1100, any seperate electronic earth is IMPROPER.

Register to Reply
Commentator

Join Date: Jun 2011
Location: New Zealand
Posts: 75
Good Answers: 5
#9

Re: Earth Resistance

09/23/2011 4:51 PM

Is this a ground mount transformer? Is the earth value you refer to from the earth ring that surrounds the transformer? If you are replacing a ground mount transformer with a physically bigger unit then a new earth ring will be needed to keep the touch voltages and step potential voltages in line. Check your local regulations. Also, as the potential fault current will rise with a larger kVA transformer then the cable diameter sizes used in the earth system may need to increase.

Register to Reply Score 1 for Good Answer
Register to Reply 10 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard