Bower Drive

09/25/2011 3:20 PM

Hello to all

I am installing a vfd for a blower of 1000cfm with 11kw motor of 415v 3ph

I am using eurotherm ercfw09 model drive.for this blower application is

v/f 50hz is good choice or v/f adjustable is good? In machine we use this blower for a application where its speed contineously need to vary little bit.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: Bower Drive

09/25/2011 4:53 PM

If the speed variation is slight, constant voltage might be okay; if significant, v/f should be constant instead.