Mechanical Shaft Power to Electrical Motor Power

09/26/2011 2:29 AM

Dear All,

While we are calculating mechanical shaft power, what is necessary to consider efficiency of the motor?

The example is below:

Shaft power = 2.2KW.

Safety margin = 1.2*2.2 = 2.64.

2.64 is not standard motor. so we are going to select 3.7KW.

In this case motor is loaded only 50%. Even though we are investing energy efficient motor, we are losing efficiency.

My question is: How can we eliminate above issue? Second question is: While converting shaft power to electrical motor power, do we consider efficiency of motor or not? If efficiency of motor is considered, what is the use of that one? Because efficiency relates to input power. 5 KW motor shall deliver 5 KW, even low efficiency also. But the think is higher input power.

Whether my doubt is correct or not, kindly suggest.

__________________
Knowledge Sharing
Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: mechanical shaft power to electrical motor power

09/26/2011 2:45 AM

2.2/3.7 ≈ 59% rather than 50% loaded.

If the 2.2 shaft hp already includes a safety factor (?), you might be able to omit the (additional) 1.2 factor. In that case, a standard 2.2kw motor might suffice, especially if it also includes its own service factor. (In the U.S. 1.15 is common, but I don't know about your locale.)

Motors are supposed to be rated by output, with the input power being somewhat higher according to the efficiency of the motor.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator
India - Member - New Member

Join Date: Jun 2008
Location: Tamilnadu,india
Posts: 64
#2
In reply to #1

Re: mechanical shaft power to electrical motor power

09/26/2011 2:55 AM

thanks for your reply.

location is india. shaft HP is without Safety factor. i think in india Service factor shall not be used.( i am not sure).

__________________
Knowledge Sharing
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#3
In reply to #2

Re: mechanical shaft power to electrical motor power

09/26/2011 3:08 AM

We have on CR4 several friends from Tamil Nadu and other areas of India. With luck, some further information may arise that fits your location. There are European motors between 2.2kw (3hp) and 3.7kw (5hp); maybe you can find an intermediate selection that meets IS.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Commentator
India - Member - New Member

Join Date: Jun 2008
Location: Tamilnadu,india
Posts: 64
#4
In reply to #3

Re: mechanical shaft power to electrical motor power

09/26/2011 3:17 AM

i shall do .

this is the example for choosing motor KW.

like that we are using so many motors in our industry. how we can aviod this problem. once we can select the exact motor with less safety margin.it will create future loads.(unavoidable).

__________________
Knowledge Sharing
Register to Reply
Guru

Join Date: Feb 2011
Posts: 1119
Good Answers: 11
#5

Re: Mechanical Shaft Power to Electrical Motor Power

09/26/2011 8:59 AM

It's ok to use the 3.7 KW motor if that's the next size available on the market, anyway, the load dictates the power consumption and inputs of your motor. If you might select lower rated motor for the use, it heats up more often than the 3.7 KW and when there is heat, it shortens the life of the coils ending to lossing resistance in a short period of time, so you might not be able to serve the capacity its intended.

Try to evaluate with the price, see the difference between 3.7KW and 2.2 KW, it aint that big amount I believe.

It's worth to consider other than buying another 2.2KW at a quarter life span of 3.7KW motor.

__________________
" To infinity and beyond" - Buzz Lightyear
Register to Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#6

Re: Mechanical Shaft Power to Electrical Motor Power

09/26/2011 4:36 PM

Just to clear up one issue though, the motor rated "power" IS the shaft power, not the electrical power (called the "absorbed" power in your part of the world). So a 2.2kW motor will put out 2.2kW of shaft power, but may draw (absorb) 2.75kW of electrical power from the line if it is only 80% eff..

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**
Register to Reply
Commentator
India - Member - New Member

Join Date: Jun 2008
Location: Tamilnadu,india
Posts: 64
#7
In reply to #6

Re: Mechanical Shaft Power to Electrical Motor Power

09/27/2011 12:20 AM

thanks for your information.

the design people keep 15% over margin due to future loads.because if Bucket elevator is design for 100TPH. but client may run 120TPH.in this case motor may not deliver that power.so design people keep some safety margin. so 2.2KW shaft power for 100TPH.if want to run 120TPH. you keep 2.2*1.15.so motor margin is increased.then if critical motor electrical engneer keep some margin that is one size higher frame size.finall motor is over sizied. 100 & 75 % loading motor efficiency is 90.2%.if motor is loading for 50%.the efficiency shall be 89.2only. kindly suggest me

__________________
Knowledge Sharing
Register to Reply
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#8
In reply to #7

Re: Mechanical Shaft Power to Electrical Motor Power

09/27/2011 12:36 AM

120TPH versus 100TPH is a 20% increase, not 15%. Then 2.2KW x 1.20 = 2.64KW. From the usual local motor sizes, you can select 3.7KW. (Unless, as mentioned before, you can find a European ~3.0KW motor that meet IS.) For these larger motors, you may need to reevaluate the shaft design and increase it.

(There are too many fingers in this pie, by the way.)

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Register to Reply
Guru

Join Date: Jun 2011
Location: Phnom Penh
Posts: 4019
Good Answers: 102
#9

Re: Mechanical Shaft Power to Electrical Motor Power

09/27/2011 5:03 AM

You really seem to be concerned that having a motor that is "over-sized" will introduce inefficiencies. Motor ratings define the maximum (nominal) output capacity. An unloaded motor only has to contend with bearing friction and copper losses. Bigger motors have bigger windings and therefore less copper losses compared to equivalent loading onto smaller motors. Bearing friction and cooling fan drag are much the same for either. So having a bigger motor would be more efficient as they run cooler due to lower copper loss. That will let you do your 120TPH easily and not worry about any waste at lower loads. Electric motors have almost no parasitic input energy characteristics unlike internal combustion engines which chew juice even when unloaded. If you think too much you will just confuse yourself.

__________________
Difficulty is not an obstacle it is merely an attribute.
Register to Reply
Guru

Join Date: Feb 2011
Location: Atlanta, GA
Posts: 1053
Good Answers: 110
#10

Re: Mechanical Shaft Power to Electrical Motor Power

09/27/2011 5:35 PM

I'd look at the actual efficiency curves of each motor. You may find that the larger motor and smaller motor have nearly identical consumption at the design load.

__________________
Think big. Drive small.
Register to Reply
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#11

Re: Mechanical Shaft Power to Electrical Motor Power

01/23/2024 2:57 AM

It is quite in order to open discussion with (a) motor supplier(s). Telephone?

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856