NGR Vs NGT

09/27/2011 2:56 PM

What is the differance for using of Neutral Grounding Resistor Vs. Neutral Grounding Transformer? What is the disign criteria? for this.

Register to Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Feb 2009
Location: Houston, USA
Posts: 946
Good Answers: 244
#2

Re: NGR Vs NGT

09/27/2011 9:49 PM

The Neutral Grounding Resistor (NGR) and Neutral Grounding Transformer (NGT) are two different things and are used for different purposes. One is not the comparable to or substitute of other. See these threads for the detail about NGR and NGT:

For NGR, see

http://cr4.globalspec.com/thread/56612/Neutral-Grounding-Resistor

http://cr4.globalspec.com/thread/51653/Neutral-Ground-Resistor-NGR

For NGT, see

http://cr4.globalspec.com/thread/36828/What-is-Earthing-Transformer

- MS

__________________
"All my technical advices in this forum must be consulted with and approved by a local registered professional engineer before implementation" - Mohammed Samad (Linkedin Profile: http://www.linkedin.com/in/msamad)
Register to Reply
Anonymous Poster #1
#3

Re: NGR Vs NGT

09/29/2011 3:21 AM

I have some comparison for NGR vs. Earthing Transformer (connected to HV switchboard, not generator or transformer neutral)

Consider if you have a plant that powered from several parallel generators on HV network, by using NGT, you will fix the resistance for your HV system to a certain fix value.

If you use NGR connected to generator star-point, everytime you add a new generator for plant expansion, the total effective resistance value will be modified, to which you may need to re-work on the protection setting on entire HV system. (unless you can ensure only one NGR is connected to the system at one time)

Register to Reply Score 1 for Good Answer
Power-User
Engineering Fields - Power Engineering - New Member

Join Date: Aug 2010
Posts: 111
Good Answers: 2
#4

Re: NGR Vs NGT

09/29/2011 11:04 PM

your NGR is an impedance inserted between your neutral and the ground..this is to minimize the amount of current entering the neutrals of your grounded source eg. generators, transformers...

a grounding transformer is applied to a floating ground system...the ussual approach is to connect the primary into a wye bank in order to create a neutral which is then grounded to earth and leaving the secondary open...

__________________
take care of your seconds and the minute will take care of itself..
Register to Reply
Register to Reply 4 comments