Current Transformer

09/30/2011 10:08 PM

Sir,

What will happen if a CT is kept open in the circuit

eg.200/5A,160/5A

iI hope experts can give me the reply

Thanks

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#1

Re: current transformer

09/30/2011 10:13 PM

Please see this discussion, for example.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#7
In reply to #1

Re: current transformer

10/01/2011 9:09 AM

My sincere apologies. i rarely post before reading all other posts. This is what happens when i don't. GA to you.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#2

Re: current transformer

09/30/2011 10:14 PM

nothing will happen to it.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Reply Score 1 for Off Topic
Guru
United Kingdom - Member - New Member

Join Date: Aug 2010
Location: Resting under the Major Oak
Posts: 4347
Good Answers: 181
#3
In reply to #2

Re: current transformer

09/30/2011 11:43 PM

Bravo88 "nothing will happen to it."

Other than the minor problems of it burning out or catching fire. But otherwise no problem!

__________________
The reports of my death are greatly exaggerated.
Reply
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#4
In reply to #3

Re: current transformer

10/01/2011 1:50 AM

A CT left open circuit, will only have higher terminal voltage, perhaps the waveform will be distorted. It definitely will NOT burn out or catch fire, as there is no current flow ,no power dissipated.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Reply Score 1 for Off Topic
Guru
Technical Fields - Technical Writing - New Member Engineering Fields - Piping Design Engineering - New Member

Join Date: May 2009
Location: Richland, WA, USA
Posts: 21017
Good Answers: 795
#5
In reply to #4

Re: current transformer

10/01/2011 2:09 AM

Even though the voltage isn't "going anywhere," it can result in insulation breakdown, creating a short circuit. If/when that happens, the voltage does go somewhere. Please retract your statement.

__________________
In vino veritas; in cervisia carmen; in aqua E. coli.
Reply
Guru
India - Member - New Member

Join Date: Sep 2009
Location: Temporarily at Ashburn, VA
Posts: 2744
Good Answers: 164
#6
In reply to #4

Re: current transformer

10/01/2011 2:46 AM

Here is an excellent explanation : http://www.control.com/thread/1026220105

Posted by

Phil Corso on 15 March, 2006 - 11:47 pm

Responding to Curt's Mar12, 12:00pm and Meir's Mar 12, 12:02pm comments:

A) Turns-ratio is not responsible for overvoltage. Even CTs with lower ratios, like 5:1 or 1:1, have the cautionary notice (at least in the USA!) Furthermore primary voltage is a fraction of Volts. So, using turns-ratio as the primary to secondary multiplier, secondary volts would be in the order of volts to tens of volts.

B) Overvoltage occurs when the secondary open-circuits and the demagnetizing effect of the secondary emf is lost. Flux density quickly increases, limited only by core saturation.C) As core saturation progresses, waveshape changes. The usual sinewave changes to a peaked wave. Such a waveshape has an extremely high dV/dT characteristic. It is very likely that insulation flashover and/or fire results from dV/dT... not from a high amplitude sine wave!

Regards,

Phil Corso, PE {Boca Raton, FL, USA}

Thanks to this potentially lethal post by you bravo, i found this gem. i also used to think that the high voltage is naturally due to turns ratio.

i hope you will also be benefited by this one.

Thanks, Mr Corso.

__________________
Nothing worthwhile can ever be taught, it can only be learnt.
Reply
Guru

Join Date: Dec 2010
Location: 1° North Singapore
Posts: 568
Good Answers: 17
#8
In reply to #6

Re: current transformer

10/01/2011 7:36 PM

oop! I guess I was too fast to jump in. I admit my experience with CT was with small one, 10A type and with much higher turn ratio (500 to 1000) than that mentioned by the OP. The open cct terminal voltage of these small CT , although , much higher but it is not in kV range , perhaps in the 10 ~20 volts. I agree, for 200A/5A CT, the Open cct terminal would be much higher, as to whether it will reach kV range, only actual measurement can tell. If I can find a similar CT, I will check it out .

Due to core saturation , it will not be a full wave waveform , but spiky voltage at beginning of every half cycle of the AC current cycle.

__________________
Sharing knowledge is one thing that defies basic arithmetic logic --- the more you share, the more you get!
Reply
Power-User

Join Date: Jun 2009
Posts: 223
Good Answers: 15
#9

Re: Current Transformer

10/01/2011 10:25 PM

has any one ever actually seen a CT that has been left with an open circuited secondary? after it has got burned?

are any pics available as web resources?

Reply
Guru

Join Date: Oct 2009
Location: sometimes Wales,UK.. was Libya, now Oman!
Posts: 1715
Good Answers: 117
#10
In reply to #9

Re: Current Transformer

10/02/2011 1:08 AM

Yes.. Me!! Not a pretty sight.... and the smell.....

Sorry looked for photos.. can't find them, will keep looking

__________________
The square root of nothing is what you make it!
Reply
Associate

Join Date: May 2010
Posts: 46
Good Answers: 1
#11

Re: Current Transformer

10/02/2011 2:31 AM

I have seen this happen in 3 ph LV circuits generally due to a defective ammeter-selector switch. The switch fails to short circuit the two unselected CT secondaries and the CT gets damaged. This may happen over a period. I have noticed charred insulation but fortunately there was no fire.

Reply Score 1 for Good Answer
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#12

Re: Current Transformer

10/03/2011 6:04 AM

Fire, explosion, electric shock...

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#13

Re: Current Transformer

10/03/2011 7:47 AM

Is current flowing in the primary when the secondary is kept open circuited?

Reply
Reply to Forum Thread 13 comments

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Copy to Clipboard

Users who posted comments:

bravo88 (3); brich (1); electricalexpert65 (1); kvsridhar (2); Priyadarshan (1); PWSlack (1); soebfatehi (1); TonyS (1); Tornado (2)

Previous in Forum: Battery Charging on Gen Set   Next in Forum: Mechanical Engineer

Advertisement