Generator Circuit Breaker: Can MV Cubicle Replace GCB's Function?

10/01/2011 5:18 AM

Hi all,

I've seen many power plant using generator circuit breaker between it's generator output terminal and generator transformer. But sometime ago i saw small generating power plant (less than 50MW) using only MV Cubicle as it's generator circuit breaker.

Do we absolutely have to use Generator Circuit Breaker? What's so special about GCB? Can we use MV Cubicle with the same equipment arrangement as GCB inside the MV Cubicle?

I've search in the forum and found this sentence, "Its the DC offset current that GCB should be capable to break. Thus is different than other breakers". Can anyone tell me what is the deeper meaning of that sentence.

thanks

Register to Reply
Pathfinder Tags: generator circuit breaker
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.

"Almost" Good Answers:

Check out these comments that don't yet have enough votes to be "official" good answers and, if you agree with them, vote them!
Guru

Join Date: Oct 2009
Posts: 2061
Good Answers: 169
#1

Re: Generator Circuit Breaker: Can MV Cubicle Replace GCB's Function?

10/03/2011 7:43 AM

Try googling and download the latest edition of the famous ABB Switchgear Manual. It has got a educative chapter on GCBs.

Register to Reply
Member

Join Date: Sep 2011
Posts: 6
#2

Re: Generator Circuit Breaker: Can MV Cubicle Replace GCB's Function?

10/05/2011 11:46 AM

The issue is the capability of the circuit breaker to break faults 'near' the generator and 'far' from the generator. The short circuit fault current is composed of several components: Initial symmetrical current, Peak current, Steady state current and dc offset current. Near the generator, at the inception of the fault and depending on where on the voltage curve you hit the fault, you could get a very substantial dc offset imposed on the fault current. The effect is to raise the peak curent and off set the sine wave above the zero line. The peak current is calculated by multiplying the initial symm current by a factor composed of the square root of 2 multiplied by 2 (if fault inception leads to full offset) and a factor which has a contant component added to the natural log with a negative exponent of system R/X. What this means is that near the generator or generator transformer R is small relative to X therefore you get the highest peak current. As you move away (get far from the generator) the peak drops. The dc component also decays at a rate governed by the negative exponent, comprising R/X multiplied by the time elapsed after the fault, of the natural log. So as R or t increases the short circuit current is not so much upwards modified by the dc offset and becomes essentially symmetrical. If you look at the breaker rating plate you will see a figure for symmetrical breaking current and assymetrical breaking current. The symmetrical current plus the dc offset gives you the assymetrical current, which is not symmetrical around the zero. So near a generator the breaker will be required to break mostly assymetrical sc currents while further away it will be breaking steady state sc currents which are symmetrical.

Register to Reply Score 1 for Good Answer