Over Voltage Damage The Appliances

10/05/2011 8:17 AM

Gentlemen,

Please suggest for the possible overvoltage control for main supply line, the 10 kva power/voltage stablizer doesnot control the voltage,voltage reaches some time 270-280 volts which damage the lights and appliances. The tap changing request failed suggest the remedial and control at user end from over voltage.

Reply
Interested in this topic? By joining CR4 you can "subscribe" to
this discussion and receive notification when new comments are added.
Guru
United Kingdom - Member - Indeterminate Engineering Fields - Control Engineering - New Member

Join Date: Jan 2007
Location: In the bothy, 7 chains down the line from Dodman's Lane level crossing, in the nation formerly known as Great Britain. Kettle's on.
Posts: 32175
Good Answers: 839
#1

Re: over voltage damage the appliances

10/05/2011 8:20 AM

<...The tap changing request failed suggest the remedial and control at user end from over voltage....>

OK. Does this mean that the automatic tap changer is faulty? If so, then the remedy is to repair or replace it.

__________________
"Did you get my e-mail?" - "The biggest problem in communication is the illusion that it has taken place" - George Bernard Shaw, 1856
Reply
Guru
United Kingdom - Member - New Member Hobbies - Musician - New Member Engineering Fields - Mechanical Engineering - New Member Hobbies - Target Shooting - New Member Engineering Fields - Power Engineering - New Member Hobbies - Fishing - New Member

Join Date: Mar 2007
Location: South-east corner of Spain 50 48 49.24N 2 28 27.70W
Posts: 1508
Good Answers: 31
#2

Re: over voltage damage the appliances

10/05/2011 8:20 AM
__________________
“It's kind of fun to do the impossible.” Walt Disney
Reply
Guru
United States - Member - New Member Engineering Fields - Power Engineering - New Member

Join Date: Sep 2006
Location: California, USA, where the Godless live next door to God.
Posts: 4665
Good Answers: 804
#3

Re: over voltage damage the appliances

10/05/2011 12:03 PM

If you meant that you requested a tep changer from the utility, and they said no, then you can look at buying your own power conditioner.

In theory, that "power/voltage stabilizer" should have been the ticket. But some of those are complete scams and do nothing but releive you of some of your money, others are nothing more than capacitors that in this case may have made it WORSE!. You need to be careful and you need to learn to investigate these things before buying them, not just read their literature.

There are still old fashioned power conditioners available, essentially a transformer with a solid state tap switch arrangement, that would serve you better in this case. They are not cheap, but they are probably cheaper than replacing equipment and appliances.

If the over voltage is constant, you might be able to just buy an autotransformer that will "buck" (lower) the voltage permanently. They are less expensive but if you do that, realize that if the utility supply becomes "normal" then you will be low, which is another problem.

Surge arrestors will not take care of constant over voltages, they are for spikes. Different animal. But most power conditioners will have surge protection built-in as well.

Had you registered and indicated what part of the world you are located in, I might have been inclined to post a link for you. But without that little bit of offort on your part, I see no point.

__________________
** All I every really wanted to be, was... A LUMBERJACK!.**